Posted by: @craig1980
- @derek-m I didn't set them back to 21 straight away and left them for a day. At night it was longer between but by the next day it was back to the same.Â
Had the indoor temperature changed? A further test would be to watch closely the operation of the wireless receivers for the thermostats when the system performs its short off - on cycle.
Also check that all the plug and socket connections on the circuit board are making good contact.
Â
Posted by: @craig1980@derek-m no change in the indoor temperature. The lights on the receivers do not change when it cycles on and off.
Did you close the airing cupboard door overnight? The reason I ask is that sometimes equipment, and circuit boards, can suffer intermittent faults due to thermal expansion.
What water law settings are applied at the moment?
Â
@derek-m the airing cupboard door is always shut. It doesn't get that warm in there.Â
Pics of the screen set up of water law.Â
Not sure if the set up with "floor" is correct. Whether it should be FCU instead?
Also running -2 on the home screen which I'm led to believe is a short cut to adjusting a water law setting. Assuming the 31?Â
Â
Posted by: @derek-mYes, I've seen all the different diagrams in the manuals, but it doesn't tell one which is correct. Also I don't see the point in having two pumps to do the job that one pump should be able to do.
I’d go with the one from the Jule installation manual, as it’s a Jule cylinder/heatpump package. Now that we’ve seen some more photo’s you can clearly see that the hydraulics match what is shown I their manual exactly.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @derek-mHi Hugh,
Do you know if the Samsung controller will still use WC when operating with the indoor temperature located within the controller?
I have a lot of time for Glyn Hudson over on YouTube who has just DIYd his 5kW Samsung install and has documented it with a decent video. From the comments I’ve been having with his, he says that the Samsung will still use WC when the wired controller is used as for measuring room temperature. I’ve asked him if the controller will also support load compensation and reduce the flow temperature when the room is approaching the target temp. Inversely, increasing the flow temp to recover quickly from a nighttime or away/holiday mode setback temperature.
He uses a single pump (with PWM control) on his setup but his primary pipe work is short.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Let me have a read through the manual and decipher what some of the descriptions mean. I'll get back to you tomorrow.
Glyn has his 5kW Samsung wired/plumbed up with full monitoring, the data can be viewed at:
https://emoncms.org/samsung5kw
Single grundfos PWM pump, a heatpump cylinder with a 1m2 coil (the same cylinder I’ve got - they were cheap on eBay back in the summer), and radiators throughout.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 24 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Damage on install - useable or dealbreaker?
They have already been dishonest by not telling you abo...
By GrahamF , 4 hours ago
-
Testing new controls/monitoring for Midea Clone ASHP
Hi all, I thought it might be of interest to others i...
By benson , 4 hours ago
-
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 6 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 7 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 8 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 8 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 11 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 12 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 13 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 13 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago