12kW Samsung gen 6 short cycling
Good evening. Welcome to my life staring at my ASHP and scratching my head.
I've had a Samsung gen 6 12kw ASHP fitted with all new pipework and rads on an eco4 grant so you can guess that I was just handed the room stats for each of the two zones and told to adjust with the stat.The system was set at 55 and no WC. No legionella either (although I've turned this off and will run manually as and when).Â
The house is a medium 5 bed, cavity bead insulation, loft insulation and double glazing. It's a 60s house but modernised and well insulated for its age. It is in West Wales so fairly mild climate.
I like to run the house at 18 degrees max so I've set the WC pretty low at 20 and -3, 20 and 31.Â
I'm getting a good COP at around 3.7 although that has dropped to 3.4 today. Using around 16kw including water heating for up to an hour.
Temp today is 8-9 degrees and the pump runs for around 7-8 mins, turns off for 18 seconds then runs again for 7-8 mins. It starts at 100w and peaks at 800w. House is sitting at around 19 degrees.Â
Water law is set up on Floor, should it not be set on Fcu and rad? What diffeference would that make?
External thermostat #1 and #2 and remote controller room temp are all set on "room temp on/off or WL interlink on/off (water pump 3)". Is that correct?
My question is how can I stop the short cycling and how can I improve efficiency?Â
Sorry for all the questions but I've driven myself mad staring at that screen. 🙈🤣
12kW eh….. seems large. What did the heat loss calcs show your heating load to be?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Hi. Unfortunately it was an eco4 grant installation so I doubt they even bothered with heat loss calcs. Likely just a guess and slap it in. 🤣
12kw does seem about right when speaking to others and what size they have.Â
The house is 164sq/m detached in an exposed spot near the coast in Pembrokeshire.Â
Some pictures of the plumbing in/around the area of the UVC if you could sir... We'll see if we can figure out how this is plumbed up and address the short cycling.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@craig1980 Yes, UVC is plumber slang for Unvented Cylinder.
OK, so we've got a standard Samsung setup with two external pumps (Why they can't put the pump in the monobloc is beyond me). The pump that is directly below the port marked 'Heat Pump return' - does that have one or two cables connected to it?
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @craig1980it was an eco4 grant installation so I doubt they even bothered with heat loss calcs.
Then they've left themselves in a tricky position as regards Part-L Section-7 of the Building Regulations:
and Sections 3 & 4 of the same Part-L
You could contact your Local Planning Authority's Building Control Dept and ask if they have been properly notified about the installation at your site. They have the power of enforcement if the terms of the Building Act have not been complied with.
You should have a schematic of your installation and notes on how to operate/maintain it. It isn't sufficient to give you a pile of manufacturers' manuals for the individual component parts of the system! 🤔Â
Within the documentation which you do have, there should also be a response from National Grid Electricity Distribution (formerly Western Power). Your installer will have filed an application under the regulations for Low Carbon Technology (LCT). You would need that response if you ever wanted to sell the property because it's the only evidence you have of compliance.
Â
Posted by: @craig1980My question is how can I stop the short cycling and how can I improve efficiency?Â
Firstly I'd be pretty pleased to have a COP between 3.4 - 3.7 on a new ASHP installation that's still suffering from cycling 😊Â
But there are others here with more knowledge than I about how to attempt a remedy.
Â
Posted by: @craig1980The house is 164sq/m detached in an exposed spot near the coast in Pembrokeshire.
That sounds like a great location for a wind-turbine and storage battery to run the ASHP at low cost over winter.
Have your visits to this forum yet enabled you to find the live topic about Wind Turbines and Planning?
Save energy... recycle electrons!
- 22 Forums
- 2,036 Topics
- 44.4 K Posts
- 22 Online
- 3,239 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@dwynwen welcome back… and glad to hear you made it thr...
By Mars , 9 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@ad3628 I’ve seen loads of heat pumps successfully inst...
By Mars , 9 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 12 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@jamespa they didn't provide any contract, or design pr...
By benson , 14 hours ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 17 hours ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 22 hours ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 22 hours ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 1 day ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 1 day ago
-
Thanks both Some useful tips I’ll keep you informed ...
By Fingers , 2 days ago
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 3 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 3 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 3 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 3 days ago