Thanks Derek and Kev super impressed by your response.
In answer Derek we have 5 rads upstairs with Trv's 2 towel heaters without Trvs. All controlled by a wireless thermostat provided with the system. This is classed as zone 2. Down stairs the 7 thermostats in each room just call for heat for ufh, this is classed as zone 1.
Im going to increase by 1 deg, on each thermostat on zone 1 now to see how that goes.
Yes Kev M its counter intuitive to what we have known regards gas but more than willing to give it a try.
Posted by: @sandThanks Derek and Kev super impressed by your response.
In answer Derek we have 5 rads upstairs with Trv's 2 towel heaters without Trvs. All controlled by a wireless thermostat provided with the system. This is classed as zone 2. Down stairs the 7 thermostats in each room just call for heat for ufh, this is classed as zone 1.
Im going to increase by 1 deg, on each thermostat on zone 1 now to see how that goes.
Yes Kev M its counter intuitive to what we have known regards gas but more than willing to give it a try.
From you own personal experience I would recommend that in order to use the weather compensation correctly you should turn all your thermostats up to say 25ºC so they are calling for heat all the time.
And have all TVRs fully open.
Let the ASHP run using the curve for say 12 hours. After this time, if the downstairs temp is too low, notch the FTC controller display up, or if too high, notch it down and repeat the 12 hour test.
I have a similar setup as you, UFH downstairs which has 3 thermostats (but all on ASHP zone 1) and several rads upstairs with TRVs (on ASHP zone 2).
My thermostats are now purely there to tell me what the temp is, they do not control the ASHP.
Downstairs: office is usually 21ºC, hallway is usually 19ºC and living area/kitchen is usually 22ºC. The difference in temp is relative to the area of UFH piping in each area.
Upstairs is always around 20ºC.
It does sound scary I know, especially with the current cost of energy, but I too am a thrifty Yorkshireman and after almost a year of testing, experimenting with different heating regimes and settings, if someone is at home most of the time, this seems to be the most efficient way to run these systems.
But if you all go out to work, perhaps other settings/schedules might work better for you.
Great info Mark C, we are here most of the time. As we have only lived here 6 weeks its hard to get our heads around this. I just want it to be comfy not overly warm but i had visions of sitting in hat and coat all day if it was too expensive for hubby🙄 so trying to understand it get the best out of the system.
Hi @sand
Actually I had forgotten that Mark also has a 2 zone system, so following his advice would probably be the easiest option for the present. My concern was how well balanced your system is and if all the thermostats and valves are actually connected to the controller.
The fundamental idea behind weather compensation, is that to maintain a reasonably constant temperature within your home, the heat energy supplied should closely match the total heat loss, and vary with changes in outside air temperature. Obviously, the heat loss compared to heat energy supply will vary from room to room, so you may find differences in temperature that possibly will need to be balanced, if they are found to be outside acceptable limits.
If like Mark, you can operate your system with no intervention from the thermostats and TRV's, but solely on weather compensation control then that would be much better.
Mark a question for you. Have you noticed how the FTC controller manages the opening and closing of the zone valves?
Posted by: @derek-mMark a question for you. Have you noticed how the FTC controller manages the opening and closing of the zone valves?
In a word, no!. Although on the FTC zone 1 is for UFH and zone 2 is for rads, I don't understand the relationship to the actual zoning throughout the property.
i.e. our UFH has 3 zones/thermostats which link to 6 manifold actuators. There is 1 synchron valve that controls flow to the manifold.
We then have 2 zones for radiators, each of which has it's own synchron valve.
This image shows ecodans kwh usage over last 4 wks. On 27th Dec changed settings to compensation curve, I know weather has been very mild, but very happy with results.
Followed Dereks advice re comp curve figs. the settings are currently -2 on the ftc. Upstairs a steady 19 and rooms downstairs 21 22 most of the time. On 24/7. I'm warm, husbands happy, thanks again for great advice.
Happy New Year.
So far so good then, it'll be intersting to see how the next couple of (colder) days go. I've done the complete opposite as you and switched from weather compensation to constant flow on Christmas day as an experiment. I'll post the results after the next couple of days but weather compensation is definitely winning so far.
@sand and others.
How do you get these figures and graphs/diagrams etc? I too have Ecodan 11.2KW ASHP.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
I have the app, which i find clunky. I would've thought that a big brand name like Mitsubishi could come up with something a bit more advanced.
Posted by: @markcHave you got meters installed that monitor usage and delivery?
Known as MMSP Metering and Monitoring Service Package. Or access to the MelCloud app?
Hi Mark. I don't have MMSP but I do have access to MELCloud. Although that tells me I need a firmware update but won't update for some obscure reason. Also I understand the data from MELCloud isn't at all accurate. For example the shown set temp' is 24C which is correct but it shows the actual room temp' as that or very close also which is inaccurate. The temp is set at 24C to keep the setting for weather comp' curve but the room temp is a comfortable 21/22C. It makes me wonder if the other readings are accurate.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 41 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
@jamespa thanks, it's way off of the MCS performance es...
By big_si , 11 minutes ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 3 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 4 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 4 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 6 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 8 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 22 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 10 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 11 hours ago
-
SolarPV tables / online calculator
By MichelleC 18 hours ago
-
By Toodles 2 days ago