which of those two links do you suggest I donât need?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @sandSorrry forgot to ask re rads would aluminium or cast iron rads work with ashp low flow as long as they were K3. Do they even do K3 cast iron.Â
Aluminium has a thermal conductivity about 5 times better than cast iron or steel I think, there are reasons that itâs used for heatsinking electronics. You can get aluminium rads, but I would expect that they would be hugely expensive. I assume that you are thinking about those designer cast iron column radiators, from what Iâve seen, these tend to come in 1, 2, 3 or more vertical columns stacked to different lengths. Again, you can compare the heat output for different physical sizes. One thing I noticed when looking at designer radiators recently, was that the heat output was considerably lower than a similar size standard radiator. This is probably because they are designed to look good at the expense of efficiency. Itâs about the surface area in contact with the air flow for convection, the standard rads have the corrugated fins between the panels, increasing surface area.
Posted by: @morganwhich of those two links do you suggest I donât need?
You don't need either.Â
To use weather compensation you just need to set the FTC to curve mode and set your initial curve settings.
This will manage the flow temp in relation to the outside ambient temp.
If you are wanting the heating on 24/7 you need to set your Neo thermostat to something high, like 25ÂșC so it is always calling for heat.
Or if you want the heating off overnight, set a low temp for that period on the Neo.
@Derek-m was very helpful in going through the setup over Skype. Perhaps he would do the same for you if required.
Posted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
That isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
It is becoming apparent that weather compensation being a slope and not a curve does have its issues.Â
e.g. with my current slope I get 30ÂșC flow when the outside temp is 5ÂșC. This gives me a constant 22ÂșC room temp downstairs.
When the outside temp is 10ÂșC the same slope generates 25ÂșC flow which only gives a 21ÂșC room temp.
It is possible to tweak the curve settings to cater for these 2 outside temps, but I imagine as the weather gets colder the settings will need to be adjusted manually.
Posted by: @morganThat isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Yes but if you are only using weather compensation you don't need any internal thermostats or thermistors. (apart from using them to tell you what the room temp currently is).
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
I think that you are perfectly correct Rusty, Auto Adaptation is indeed closed loop control, whereas weather compensation is open loop control, though it does appear to work reasonably well, particularly in homes that have a large thermal mass.
Posted by: @morganThat isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Hi Morgan,
Your question was 'which of the two items that you are purchasing, will you not need to be able to use weather compensation control', and the answer is (as MarkC pointed out) that you don't need either of those devices. You can set weather compensation on your FTC controller whether it is in your room, your airing cupboard, or even your garage, the location does not matter, because it is measuring the outdoor air temperature using a sensor that is already installed in the outdoor unit.
I fully agree with Brendon, that thermostats should be avoided whenever possible.
Hi Derek and Mark.
I get that but I might not always run via weather compensation so when running via other means my preference is to dispose of the neostat altogether and have all in house Mitsubishi controls and remove the thermostat out of the equation.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 45 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 3 hours ago
-
RE: Heat Pump Servicing & Maintenance â Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 17 hours ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 21 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 2 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 2 days ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone boxâŠ.
By Majordennisbloodnok , 3 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 3 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 4 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 5 days ago
-
RE: How much am I âsavingâ?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 5 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 7 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 7 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 1 week ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 1 week ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 2 weeks ago