Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @sandSorrry forgot to ask re rads would aluminium or cast iron rads work with ashp low flow as long as they were K3. Do they even do K3 cast iron.Â
Aluminium has a thermal conductivity about 5 times better than cast iron or steel I think, there are reasons that itâs used for heatsinking electronics. You can get aluminium rads, but I would expect that they would be hugely expensive. I assume that you are thinking about those designer cast iron column radiators, from what Iâve seen, these tend to come in 1, 2, 3 or more vertical columns stacked to different lengths. Again, you can compare the heat output for different physical sizes. One thing I noticed when looking at designer radiators recently, was that the heat output was considerably lower than a similar size standard radiator. This is probably because they are designed to look good at the expense of efficiency. Itâs about the surface area in contact with the air flow for convection, the standard rads have the corrugated fins between the panels, increasing surface area.
Posted by: @morganwhich of those two links do you suggest I donât need?
You don't need either.Â
To use weather compensation you just need to set the FTC to curve mode and set your initial curve settings.
This will manage the flow temp in relation to the outside ambient temp.
If you are wanting the heating on 24/7 you need to set your Neo thermostat to something high, like 25ÂșC so it is always calling for heat.
Or if you want the heating off overnight, set a low temp for that period on the Neo.
@Derek-m was very helpful in going through the setup over Skype. Perhaps he would do the same for you if required.
Posted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
That isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
It is becoming apparent that weather compensation being a slope and not a curve does have its issues.Â
e.g. with my current slope I get 30ÂșC flow when the outside temp is 5ÂșC. This gives me a constant 22ÂșC room temp downstairs.
When the outside temp is 10ÂșC the same slope generates 25ÂșC flow which only gives a 21ÂșC room temp.
It is possible to tweak the curve settings to cater for these 2 outside temps, but I imagine as the weather gets colder the settings will need to be adjusted manually.
Posted by: @morganThat isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Yes but if you are only using weather compensation you don't need any internal thermostats or thermistors. (apart from using them to tell you what the room temp currently is).
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, Iâll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as itâs all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
Â
I think that you are perfectly correct Rusty, Auto Adaptation is indeed closed loop control, whereas weather compensation is open loop control, though it does appear to work reasonably well, particularly in homes that have a large thermal mass.
Posted by: @morganThat isnât what Brendon reckons. Â If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as itâs a tempâ sensor as opposed to an âon/off switchâ. Â Hence my desire to switch. Â He is scathing of âthermostatsâ.
Hi Morgan,
Your question was 'which of the two items that you are purchasing, will you not need to be able to use weather compensation control', and the answer is (as MarkC pointed out) that you don't need either of those devices. You can set weather compensation on your FTC controller whether it is in your room, your airing cupboard, or even your garage, the location does not matter, because it is measuring the outdoor air temperature using a sensor that is already installed in the outdoor unit.
I fully agree with Brendon, that thermostats should be avoided whenever possible.
Hi Derek and Mark.
I get that but I might not always run via weather compensation so when running via other means my preference is to dispose of the neostat altogether and have all in house Mitsubishi controls and remove the thermostat out of the equation.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 255 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 5 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 16 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 2 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 2 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson â as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 â as @jamespa says, it's for filling and re-...
By cathodeRay , 7 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 18 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 23 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 24 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty âcan of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call â what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP â how to set weather compensation
@mk4 â good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago