which of those two links do you suggest I don’t need?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @sandSorrry forgot to ask re rads would aluminium or cast iron rads work with ashp low flow as long as they were K3. Do they even do K3 cast iron.
Aluminium has a thermal conductivity about 5 times better than cast iron or steel I think, there are reasons that it’s used for heatsinking electronics. You can get aluminium rads, but I would expect that they would be hugely expensive. I assume that you are thinking about those designer cast iron column radiators, from what I’ve seen, these tend to come in 1, 2, 3 or more vertical columns stacked to different lengths. Again, you can compare the heat output for different physical sizes. One thing I noticed when looking at designer radiators recently, was that the heat output was considerably lower than a similar size standard radiator. This is probably because they are designed to look good at the expense of efficiency. It’s about the surface area in contact with the air flow for convection, the standard rads have the corrugated fins between the panels, increasing surface area.
Posted by: @morganwhich of those two links do you suggest I don’t need?
You don't need either.
To use weather compensation you just need to set the FTC to curve mode and set your initial curve settings.
This will manage the flow temp in relation to the outside ambient temp.
If you are wanting the heating on 24/7 you need to set your Neo thermostat to something high, like 25ºC so it is always calling for heat.
Or if you want the heating off overnight, set a low temp for that period on the Neo.
@Derek-m was very helpful in going through the setup over Skype. Perhaps he would do the same for you if required.
Posted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controller
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, I’ll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as it’s all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
That isn’t what Brendon reckons. If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as it’s a temp’ sensor as opposed to an “on/off switch”. Hence my desire to switch. He is scathing of ‘thermostats’.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controller
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, I’ll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as it’s all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
It is becoming apparent that weather compensation being a slope and not a curve does have its issues.
e.g. with my current slope I get 30ºC flow when the outside temp is 5ºC. This gives me a constant 22ºC room temp downstairs.
When the outside temp is 10ºC the same slope generates 25ºC flow which only gives a 21ºC room temp.
It is possible to tweak the curve settings to cater for these 2 outside temps, but I imagine as the weather gets colder the settings will need to be adjusted manually.
Posted by: @morganThat isn’t what Brendon reckons. If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as it’s a temp’ sensor as opposed to an “on/off switch”. Hence my desire to switch. He is scathing of ‘thermostats’.
Yes but if you are only using weather compensation you don't need any internal thermostats or thermistors. (apart from using them to tell you what the room temp currently is).
Posted by: @rustyPosted by: @markcPosted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controller
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
Not familiar with the FTC6, just trying to learn about the control systems, I’ll have to read the data sheet and more about weather compensation and auto adaptation.
From a control systems point of view, I would have expected auto adaptation to be a better solution as it’s all closed loop with more information available. Given my current understanding, weather compensation looks more open loop, with lots of tweaking to get a reasonable profile, which might make it suboptimal under certain conditions. Derek M will probably now put me straight.
I think that you are perfectly correct Rusty, Auto Adaptation is indeed closed loop control, whereas weather compensation is open loop control, though it does appear to work reasonably well, particularly in homes that have a large thermal mass.
Posted by: @morganThat isn’t what Brendon reckons. If you remember he would remove the Heatmiser thermostat and replace with the Mitsubishi units as it’s a temp’ sensor as opposed to an “on/off switch”. Hence my desire to switch. He is scathing of ‘thermostats’.
Hi Morgan,
Your question was 'which of the two items that you are purchasing, will you not need to be able to use weather compensation control', and the answer is (as MarkC pointed out) that you don't need either of those devices. You can set weather compensation on your FTC controller whether it is in your room, your airing cupboard, or even your garage, the location does not matter, because it is measuring the outdoor air temperature using a sensor that is already installed in the outdoor unit.
I fully agree with Brendon, that thermostats should be avoided whenever possible.
Hi Derek and Mark.
I get that but I might not always run via weather compensation so when running via other means my preference is to dispose of the neostat altogether and have all in house Mitsubishi controls and remove the thermostat out of the equation.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 49 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 4 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 16 minutes ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 39 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 3 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 3 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 4 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 6 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 6 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 7 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 9 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 11 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 17 minutes ago
-
Heat Pump Sizing & Installation Costs
By Mars 13 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 14 hours ago
-
SolarPV tables / online calculator
By MichelleC 21 hours ago