Hi @sand
Your pipework and setup seem very similar to mine.
Red pump in 4th pic is the pump that pushes hot water around all your heating system.
Red balloon like expansion tank is to handle excess pressure for the heating system.
White expansion tank is to handle excess pressure for DHW.
The flow to heating/DHW is controlled using Synchron valves, not a 3 way diverter valve as Derek said might be the case.
The DHW tank is self insulated so no, you don't need to add extra insulation.
Your FTC controller (what you use to change the ASHP settings) is located in the garage. With it located there you can use weather compensation but cannot use auto adaptation.
Hope that helps.
Thanks so much MarkC brilliant information. Good to know that tank does not need to be insulated.
Youâre welcome, I never know whether to reply on things like this, as itâs not easy to know how much people already know, donât want to âteach grandma to suck eggsâ.
If you are contemplating swapping out the rads, just be aware that, assuming Stelrad, the K3 will be around 50% deeper than the K2, but with around 40% more heat output for the same size panel. You can estimate the output power of the existing panels by simply measuring them and looking up the K2 range data on the web (sorry, that may be obvious), though beware that this may be at a delta-t of 50C (i.e. traditional 70C flow temp for a 20C room temp), at 45C flow temp the power output will obviously be lower and would need estimating. You can then see if the rad size is adequate for the room if you know the room heat loss estimate. On the Stelrad website there is a useful heat loss calculator that can be used to estimate this, based on flow temp, room size, desired temp, etc. Not promoting Stelrad, itâs just a useful example, there are others!
Can you expand on why auto adaptation cannot be used, but weather compensation can? Is it simply that the location means that the room temperatures arenât available while the external temperature is available. That seems odd, as from the brief description that I found, auto adaptation seems ideal and itâs just a communications issue with the room thermostats.
Thanks Rusty I know absolutely nothing about heating and never thought I would need to ! Then bought this house (with a ashp so had to quickly learn. Info re rads is great.
Sorrry forgot to ask re rads would aluminium or cast iron rads work with ashp low flow as long as they were K3. Do they even do K3 cast iron.Â
Posted by: @rustyCan you expand on why auto adaptation cannot be used, but weather compensation can? Is it simply that the location means that the room temperatures arenât available while the external temperature is available. That seems odd, as from the brief description that I found, auto adaptation seems ideal and itâs just a communications issue with the room thermostats.
That's exactly it. Weather compensation uses the external thermistor whereas auto adaptation uses both the external thermistor and the internal thermistor located in the FTC control panel to read internal room temp and adjust the flow temp as required.
For auto adaptation to work the FTC needs to be located in a room/hallway. A location where a typical central heating system would have its single thermostat.
So for example imagine outside temp is 5ÂșC on a cloudy day, so the compensation curve sets the flow temp to 30ÂșC. This generates an internal temp of 22ÂșC.
The next day is also 5ÂșC outside but is a sunny day. The curve would also set the flow temp to 30ÂșC, but the solar gain on the windows and building fabric make the internal room temp 25ÂșC.
The FTC located the room knows it's 25ÂșC inside, so reduces the flow temp accordingly.
If on the other hand the FTC is located in the garage, this feels no solar gains doesn't adjust the flow temp.
Is it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @morganIs it safe to assume that if the FTC is in the same cupboard as the cylinder etc (common instal procedure) that, like the garage scenario, auto adaptation is not an option?
It appears to be the common practice yes.
For Mitsubishi ASHPs, if you want to use auto adaptation the options are:
1. Move the FTC controllerÂ
2. Wire in an additional thermistor and locate that in the room/hallway.
3. Add an additional, wireless FTC controller and local that in the room/hallway.
I think the current opinion is that using auto adaptation instead of weather compensation only won't give massive economic savings, but it will help to maintain a more comfortable internal temperature.
At the moment my FTC6 is in the airing cupboard with the cylinder etc and it will remain there.
The thermostat at present is a Heatmiser Neo which I didnât want and donât like but my installer is unable to get stock from Mitsubishi so had to go this route to complete the instal prior to winter.
Iâm now in possession of a Mitsubishi remote controller ( https://les.mitsubishielectric.co.uk/products/controls/remote-controllers/par-wt50r-e-remote-controller ) and await the delivery toward the end of January! Â of the wifi receiver ( https://les.mitsubishielectric.co.uk/products/controls/remote-controllers/par-wr51r-e-remote-controller-receiver )
When I have possession of both the installer will return and swap out the Neostat. Â I should then be able to run a âproperâ weather compensation set up and access Melcloud applications. Â Not too bothered with auto adaptation.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 49 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
Hmm Before doing that I would want to be certain that...
By JamesPa , 4 hours ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 4 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
Sorry Bravo. I have no installer contacts outside the U...
By Mars , 15 hours ago
-
Have your say in the Renewable Heating Hub Awards
Itâs time to celebrate the best (and call out the worst...
By Mars , 15 hours ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 23 hours ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 1 day ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 3 days ago
-
RE: Solar Power Output â Letâs Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 3 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 4 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 5 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 5 days ago