Givenergy batteries not in sync - any ideas? appears not calibration.
I have a Givenergy Gen1 5kw Hybrid inverter with
3 x 8.2kw batteries
Installed 2020
I have not monitored closely in the past but believe the batteries kept reasonably in sync with similar SOC (state of charge levels) at all times.
For the last few months I have had an issue with the batteries being out of sync and divergence between SOC batteries divergence getting worse.
Despite raising with Givenergy we don't seem to be making progress to resolution. e.g. Recalibration has been tried several times which has only resolved matters for a single charge/discharge cycle at best. They also did a firmware update
e.g. recently with Reserve set as 4%
Overnight:
aggregate 4% and idle
Primary 29%
Batt1 0%
Batt2 0%
evening:
aggregate 39% and
Primary 66%
Batt1 32%
Batt2 25%
morning:
aggregate 4% and therefore discharge stopped & idle
Primary 23%
Batt1 3%
Batt2 1%
previous day limited solar included
aggregate 16%
Primary 32%
Batt1 15%
Batt2 13%
aggregate 23%
Primary 40%
Batt1 21%
Batt2 19%
aggregate 25%
Primary 42%
Batt1 23%
Batt2 20%
divergence obviously means the capacity of the batteries is not used properly for charge or discharge and is not available for EPS etc.
Have asked Givenergy to investigate & escalate - so far they have tried recalibration and a firmware update without success. Not getting feedback on further actions.
Situation getting worse:
Overnight:
aggregate 4% and idle
Primary 29%
Batt1 0%
Batt2 0%
Yesterday evening:
aggregate SOC 51%
Primary 79%
Batt1 40%
Batt2 35%
I have raised in a Givenergy forum but thought I would add here in case anyone has other suggestions and to highlight the issue.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
even when my aggregate charge has been "full" on SOC the underlying has been nowhere near - and stopped charging.
Primary 99%
Batt1 83%
Batt2 81%
There is no consistency. At times Primary has had the highest charge but at times Primary has been the lowest!
It seems to me there is definitely an issue - as its being raised by a few people. Other people may have the problem but simply be unaware if they are not monitoring.
The lack of responses from @Givenergy is disappointing - indeed worrying.
As Octopus Tracker is cheap today (19.56p) I will kick off a full charge. lets see where it gets to
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441, I'll contact GivEnergy and see if they can assist you.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@tim441, just heard back from GivEnergy. They've suggested that you call their call centre and they'll walk you through everything: 01377 252874.
Let us know what the outcome is.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor thank you very much for taking the trouble. Apologies for slow response as I've been travelling today. I will follow up tomorrow & let you know what they say.
From other discussions it seems this problem has been ongoing for some time & with quite a few people. I suspect some people with 2 or more batteries may not be aware of the problem as it does not trigger any alert. It's seen only by drilling down in app or data etc.
The hope seems to be with a firmware update that's being tested... to solve this and other problems. No release date known.
But I'll try to get a fuller update tomorrow.
Thanks again.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@editor Givenergy have agreed to send an engineer. Not clear if that's to run tests/checks or what has been diagnosed. But will be glad to see them and hopefully get matters resolved so we can maximise usage of the batteries going forward. Thanks for your help. Will update with news.
I'm keen to see a solution as I have recommended Givenergy to quite a few people and hope that they live up to general good impression of good value for decent quality. I have an additional solar project later this year - planning to add battery (or 2 ) and EPS ..... and so far think that will be Givenergy.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Hi
I install these batteries as well as having a system with two 9.5kWh packs.
there is an ongoing issue with SOC drop off and I expect this is causing imbalance in your stack.
if one of the BMS modules reports incorrectly, it will not charge or discharge depending on which way it’s wrong.
there is an update being tested and is a couple of versions in, one of my clients is a test system.
it’s very frustrating as there seems to be no real prioritisation from GivEnergy on this point
whilst I certainly don’t have inside information, the feeling is their focus is on the new EV Charger and All In One product releases as well as the European market expansion.
Hopefully once the new products are released we will see some focus on resourcing this existing problem.
Internationally recognised award winning installer of heat pumps and stuff
Knowledgeable & helpful Givenergy engineer visit today as arranged. From the log data he was sent as they thought there might be a faulty cell in one battery. Partly based on the voltage data that he said gave more reliable information than SOC. Sounded feasible?
However when stripping down offending battery discovered several connections were not tight by 2 or 3 full turns. Obviously not good! Cleaned up and remade connections. Checked other batteries (which were fine). Started a calibration.
I will monitor in coming days. His view was that the firmware update may not make a difference but will apply it once released.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
In passing worth noting that the Givenergy "All in one" inverter & battery is likely to be released around end May - similar to Tesla Powerwall
13.5kwh battery
6kw nominal AC output
7.2kw peak power
with additional Gateway to provide whole house backup and 18.4kw nominal AC power
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Firmware updated yesterday and calibration completed. Early results look encouraging.
small observation this morning:
SOC 72% 52.5v 23c
Primary 68% 52.8v 25.1c
Batt1 72% 53.2v 24.1c
Batt2 72% 52.7v 23.5c
perhaps this differential between the 3 packs is normal. I will keep an eye on it over coming days to see how it looks at various levels of charge/discharge. But overall looks better than before anyway
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Reliable, easy to use home battery options
1 month ago
-
ROI on ASHP, Solar PV & Batteries
1 year ago
-
8.2kW GivEnergy
1 year ago
-
Givenergy All-in-one launched & price. Competition for Tesla Powerwall?
2 years ago
-
Givenergy "All in one" vs Tesla Powerwall
3 years ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 462 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 31 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
We suffered a water leak last year in two rooms and had...
By MartinHook_UK , 42 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 50 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 8 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 14 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 18 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 19 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 21 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago