@transparent Well they sound promising, SOC isnt crucial to me, but its nice to have. Im hoping to get a timber frame shell up early next year and there would be nothing stopping me from installing a new battery system then inside it. if the inverter isnt reusable then I could get the whole thing fully functional before switching the panels over. 🙂
Good luck with the floor 🙂 Im having a day off DIY!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@irmartini Ive looked into this further and I think that the minimum 5kWh solar production is in fact the battery charge as it is DC coupled and the sensor wont distinguish between that and solar production. This then explains why my back of a fag packet calculation differs so much from the later one using the Octopus data! Thanks for solving the mystery for me. 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody - I've read through several specifications and manuals for your Huawei inverter.
The installation instructions are in English, but it's not the finest piece of draughtsmanship I've seen.
The two pairs of solar panel inputs and the battery connections are all referred to as "DC power inputs"
They all use the same MC4 connectors, and are placed next to each other!!
Worse still, the adjacent DC-switch isolates the two solar inputs, but not the battery.
Your attention to this important safety feature is carefully tucked away as Footnote B, which I've underlined in red.
In a nutshell, the inverter is nothing special.
Huawei have concentrated their efforts on delivering a snazzy App, which is what you'd expect from a Smartphone company.
You can use non-Huawei batteries with different capacity.
It is generally frowned upon to mix batteries with very different overall capacity ratings.
Yes it will work, but the currents will be quite different and the BMS units are unlikely to provide any useful SoC data.
You can (optionally) buy a Peacefair Coulometer PZEM-015 unit and try it with your existing battery.
It would be an interesting cheap test to see if it's any different to the Huawei SoC calculations.
Save energy... recycle electrons!
@transparent Thanks for looking at all this, hope the floor went well. I neglected to mention that my battery is DC coupled, I hope that doesnt change anything.
I confess Im a bit nervous about disassembling the battery, where would the coulometer go? (I really want to put a 'b' in there)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Perhaps the bee ran out of charge 😉
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @bontwoodyI neglected to mention that my battery is DC coupled
That can be interpreted several ways, depending where that coupling goes.
Are you saying that your PV panels are connected to the battery, rather than the inverter?
... because that's not what it looks like in the photo you posted.
There should be a pair of wires going between the battery and the inverter.
They will have about 52v across them.
That's where a coulometer goes.
It's unnecessary to open the battery.
As for progress on my floor....
... it's still missing a few bits:
Apparently, the room requires joists, and a floor - or so my wife tells me.
I've explained that it's not that straightforward... and that I have indeed created a flaw.
Save energy... recycle electrons!
@transparent Im not clear of the actual connections, I just know that the DNO would allow the batteries connected like this and not AC coupled as usual. My feeling is that the battery sits between the panels and inverter although how the charging is managed I have no idea.
Re floor: emphasise the advantages of the increased headroom you have created 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
It sounds like your installer was the one who actually communicated with your DNO,
and has then given you a partial explanation.
On the left is an AC-coupled battery, next to a solar inverter.
That battery unit from PowerVault has its own integral inverter.
If both the green inverter and the battery were to export to the grid, then the combined current could exceed 16A (3.68kW),
and the DNO would need to grant G99 approval.
Approval would most likely be granted with the condition that export current was limited to 16A by the use of an approved current-measuring system.
Your Huawei battery has no possible AC output,
nor can it accept direct connection of solar panels.
It's DC coupled to the inverter.
Output to the grid is limited purely by the inverter only being able to output 16A at 240v.
And it's that last factor which might cause you to consider selling on both your Huawei battery and the inverter.
An inverter which can only output 3.68kW is short of what you might require for the house.
One major advantage of having a sub-floor void is that it's a good environment in which to place a further 500kWh of storage battery 🙂
Save energy... recycle electrons!
@transparent OK, thats clear. I didnt pay a lot of attention to the details but I knew it was to prevent export from both the panels and the battery at the same time.
Something perhaps I should have mentioned is that I have a separate 2.66 kV PV array which came with the house and has a good FIT payment. It has its own Fronius inverter. The two systems are totally separate as you would expect.
The solar array connected to the battery system is about 4.3 kV.
You could perhaps get enough batteries under there to have an electric house vehicle 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
There are no post-installation checks on installations which have already been accepted for FIT payments.
For example, if your Fronius inverter were to fail, then you'd be able to replace it with a different/newer unit without needing to have your site re-approved.
There's nothing to prevent you re-directing that original 2.66kW PV array to supply an inverter which connects with a storage battery.
It still fulfills the overall aim of the FIT scheme, in that it:
- reduces demand on the grid during peak periods
- reduces losses due to phase-imbalance at the local substation
So you could consider the following arrangement for example:
In effect the house runs off storage batteries most of the time.
You can have as many inverters as required to supply the load presented by the house.
You can have as many storage batteries as you wish, to increase the amount of time between charging.
With enough storage, you can avoid recharging from the grid until the next sunny day arrives.
Having more than one inverter and battery provides greater resilience against a fault.
This isn't a direct proposal for your home.
I'm merely putting this forward to let you have a vision of what's possible.
Finally, you will note that I've adjusted your specification of the solar panels operating at 2.66 and 4.3 kilovolts respectively.
Such a high voltage would likely exceed the specification for the insulation on wires and connectors!
Shall we stick to kilowatts (kW) in future? 😉
Save energy... recycle electrons!
LOL kV...Sorry Im reverting back to radiography mode! I do know the difference ...honest 🙂
No one has ever suggested that possibility to me and the idea of charging the battery from both solar arrays is attractive. Had the installer suggested it, I might well have found some additional funds at the time.
Im not really worried about having DC feeds or an off grid capability really (unless it was stupidly cheap to add on).
Im guessing the inverters would have to be the same power as currently fitted to keep the DNO happy?
Thanks for this.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@transparent So doing a bit of further research, Ive come up with these options:
1. Add extra module to Huawei system, cost £2200, result 10 kWh
2. Build battery in Seplos enclosure, cost £2000 - resale of luna module, result 14 kWh
3. Buy Fogstar battery, cost £2500 - resale of luna module, result 15.5.kWh
options 2&3 may require me to change the Huawei inverter too.
Are all three options capable of having the second solar array wired into the battery with another inverter?
Cheers Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 24 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 13 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 16 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 21 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor @sandy I tried contacting them via Whatsapp b...
By brad , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 3 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 3 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 3 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 5 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 5 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 5 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 6 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 7 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago