When I was selecting my new solar array and house battery, I had to cut my cloth according to my budget, and in the end settled for a 5 kWh Huawei Luna battery module. I wasn’t sure if this was large enough at the time, but figured that I could add additional 5 kWh modules at a later date if not.

There is something intrinsically appealing about having enough battery capacity to see you through a whole day and it certainly gives you flexibility about when to charge and if to sell some electricity to the grid.

Now that I have a whole year of data, I am in a position to determine whether increasing my battery capacity would make sense financially. I am currently on the Octopus Intelligent Go Tariff, which gives a tariff of about 7p per unit overnight and 27p during the day.

The first graph below shows my heat pump usage throughout the year. Obviously the house uses more electrical energy that just that, but during the day this is my biggest use during the colder months. Domestic Hot Water heating and EV charging are done overnight on a cheap tariff as is washing dishes and clothes (mostly).

For large parts of the year, charging my 5 kWh battery at night is sufficient so that I don’t need to draw any significant power from the grid during the peak rate period. It is clear from the graph that all days when I use less than 5 kWh hours fall into this bracket.

The second graph shows my solar output for the same period. Even in the depths of January to February, it is rare not to produce at least around 5 kWh, so in fact I am probably not importing from the grid when I use less than 10 kWh of electricity with my heat pump.

Looking at the first graph again, there are very few days (less than 30, I would estimate) when this happens. If any of these days coincide with a good solar output day then this will be reduced again.

If we assume I was to purchase a second battery module then this could hold another 5 kWh. The difference in unit price between peak rate and off-peak rate is about 20 pence a unit, so let us assume I could save about £1 for every day when I import 5 of more kWh’s of electricity.

From the previous estimate, let’s be generous and say 30 days. So I could save £30 per year. Given the cost of an additional battery module is about £2000, the payback period would be about 67 years (ignoring future price changes).

Now I know that this is a bit of a “back of a fag packet” calculation and that there may be opportunities to make money by selling back to the grid. Also no one knows what will happen to electricity pricing in the future and other makes of battery may be cheaper.

However even given all these variables, I would suggest that the financial argument doesn’t look good for me to upgrade. Also I would suggest that with a little thought and planning, a heat pump user like myself can get most of the advantages of a home battery without purchasing a large battery pack.

I’m anticipating a healthy debate on this conclusion. 🙂

HPUsage
SolarOutput

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
Quote
(@irmartini)
Estimable Member Member
1268 kWhs
Joined: 11 months ago
Posts: 66
 

Your solar array must be positioned perfectly.

 

Between Dec23 and Jan24 I had 30 days with production below 5kWh (worst day was 0.4kWh) and that's with an 11.4kW array.

“Anything worth doing, is worth doing right.”


   
ReplyQuote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

We have 6kW of PV but our neighbours have large trees that the sun can’t get over in winter, and a 9.5kWh battery. I assumed we would get another battery when the heat pump went in. But some simple sums show it would never pay back it its lifetime. 
Nevertheless we just might buy another 9.5kWh battery just for the pure satisfaction of being independent of the grid and only ever buying the cheapest electricity.

But there is another limit for us which is getting to fully charged within the cheap periods (we’re on COSY) since our AC3 inverter can only charge at 3kW so it takes just more than the 3hours to fill it (if empty) so that means a further AC3, not just an extra battery. Right now the GivEnergy software can’t reliably control parallel inverters, which they call a plant.

Your Huawei battery will have similar charge limits and do you know what they are? No manufacture supports mixed supply  of different makes indeed some are mutually compatible in their own product range

 

This post was modified 5 months ago by Judith

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote



bontwoody
(@bontwoody)
Noble Member Contributor
5011 kWhs
Joined: 3 years ago
Posts: 740
Topic starter  

@irmartini Ive spread my bets with and additional East and West orientation in addition to the original South facing one 🙂

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5011 kWhs
Joined: 3 years ago
Posts: 740
Topic starter  

@judith Ive just had a quick look and I think its its saying 1.5 kW per 5 kWh module

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5011 kWhs
Joined: 3 years ago
Posts: 740
Topic starter  

So not being one to rest on my laurels, it occured to me that I should be able to get a more accurate prediction of my energy usage from Octopus using their csv download.

I have to say the results surprised me a bit. I excluded the electricity usage during the cheap go periods but found some quite high usage when I wasnt expecting it. After a bit of investigation I noticed this was Go using slots outside its normal range and also some free electricity slots during days when the grid was green.

After a bit more cleaning of the data, I finally got to the following graph which indicated my daytime import over the year was 1225 kWh (much more than I had estimated initially using my other data).

Calculating the impact of a second 5 kWh battery module came in with a saving of £214 over the year, giving a payback period of about 10 years. While still being borderline it is a lot more promising than I initially thought.

One thing that might have affected the outcome is that for the initial part of the year, I was using Octopus Cozy, not Go, so its possible charging the battery in the afternoon slot might have exagerated the benefit. I will do the analysis again when I have a full year of Go data. 🙂

ImportedEnergy

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
👍
1
ReplyQuote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

Posted by: @judith

 No manufacture supports mixed supply  of different makes indeed some are mutually compatible in their own product range

 

if course what I should have written was INcompatible within their own range!

 

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @bontwoody

in the end settled for a 5 kWh Huawei Luna battery module

Can you expand on that choice please?
I'm particularly interested in security of supply.

Having visited the Luna product page, it appears that the extended guarantee is linked to a requirement to use their cloud-based software for monitoring and system diagnosis.

Do you have App preferences to prevent Huawei taking your battery off-line, for example to install an over-the-air upgrade?

 

Posted by: @bontwoody

If we assume I was to purchase a second battery module then this could hold another 5 kWh. [....]

Given the cost of an additional battery module is about £2000, the payback period would be about 67 years

[bigger snip]

Calculating the impact of a second 5 kWh battery module came in with a saving of £214 over the year, giving a payback period of about 10 years.

The price of battery-grade lithium carbonate has fallen to 20% of what it was 2 years ago.
That's primarily due to Western Countries putting back the date by which they will no longer allow ICE vehicles to be sold.

That has an immediate effect on the price of importing LiFePO4 cells from agents in China.
I'm being offered 16x 280Ah cells for around £1500.
Some agents have stocks already in Poland, Germany or Turkey to avoid the 7-weeks marine shipping delay around South Africa.

Add to that a Seplos Mason steel enclosure, incl BMS and cabling, for around £500.

The DIY route gives you 14kWh for the same £2000 price as another 5kWh from Huawei.

 

This post was modified 5 months ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5011 kWhs
Joined: 3 years ago
Posts: 740
Topic starter  

@transparent At the time, it was very difficult to get a solar installer and the one who did reply only fitted either Solar Edge or Huawei. The 10kWh SE quote was out of my range so I settled on the modular Huawei. Annoyingly you can buy a Luna module in Germany for £1400.

I do use the online monitoring platform and apart from the fact I havent been able to combine its data with any of my other monitoring systems, Im reasonably happy with it. Im not too worried about the security of supply (barring war with China!) and the system as a whole works well. I havent investigated the app preferences in that regard.

With respect to the DIY route, I am open to doing most things DIY but I do admit to being a little scared of the home battery scenario. The thought of totaling the battery through a mistake is haunting!

If I could use a DIY battery with the Huawei inverter with a confidence of success, I would certainly consider it, I could then sell on the original Luna module and perhaps knock another £1000 off the price. At present my inverter and battery are outside but I hope to install them in an extension next year.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @bontwoody

If I could use a DIY battery with the Huawei inverter with a confidence of success, I would certainly consider it

You have a high expectation of success with the assistance you'll get on this forum!

Tell us the model number of the inverter and I'll look at the specification.

It's likely that the Huawei App is picking up data from both the inverter and the Luna battery simultaneously.
But I doubt you're spending any time looking at the cell-voltages obtained from the CAN-bus link between the two units.

Once a battery has been configured to work with a particular inverter, most end-users are only interested in what data comes from the inverter.

If you really want to know what's happening within a battery, most BMS units generally their own App which allows you to check.

The one piece of data which is invariably incorrect is the State-of-Charge.
That's notoriously difficult to calculate unless you regularly calibrate the monitoring software by completely discharging the battery and then re-charging to 100%

Most home-battery users wouldn't consider doing that.
We tend to use batteries in the middle of their capacity range.

 

This post was modified 5 months ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5011 kWhs
Joined: 3 years ago
Posts: 740
Topic starter  

@transparent It was really the SOC I was interested in 🙂 but with a bigger battery that wouldnt be so critical.

I suppose it wouldnt be the end of the world if I had to replace the inverter too, and I could sell than on with the battery 🙂

Photos attached

IMG 0714
IMG 0713

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Let me quickly address the State-of-Charge (SoC) issue,
and I'll come back to the inverter once I've read the specs.
[aside] today's plan is to replace the floor joists on one my rooms, and it's not progressing fast!

A BMS unit would normally be expected to undertake four roles:

  1. protect the cells against over-charge by continuously checking for the one with the highest voltage
  2. ditto for too much dis-charge
  3. balance the cells to attain an even voltage across them whilst in charge-mode
  4. calculate the SoC

 

It's pretty good at the first three, but you can't measure the SoC properly whilst there's current flowing.

 

The best method is to deploy a separate coulometer which measures current and voltage on the main connection cables.

The market leaders in this technology are Victron in Holland and Batrium in Australia.
Each of them has developed a finely engineered coulometer which costs several hundred pounds.
The price tells you a lot about how difficult this is!

However, there's a third alternative from a Chinese manufacturer called Peacefair.

I've been using their stand-alone Coulometer PZEM-015 for over a year, measuring current via a shunt rated at 300A.
It costs about £18 incl a shunt, and beats the socks off the three different BMS units I have here on test.

image

I spoke to Peacefair about 8 months ago because I would've liked to have a data-out port from their unit, rather than just the inbuilt LCD.
At that time they couldn't offer such a device.

Last month they emailed me a newsletter which offers an alternative with a data-out

The PZEM-017 is a dedicated coulometer which provides data using Modbus across an RS485 connection.
The downside is that it doesn't have any LCD.
You can only extract the data, which you then take to whatever computer system you want.

 

There's also a dedicated coulometer from another Chinese company called JuncTek, costing around £60-ish.

I've used one of their KH140F units for about a month.
But tests were curtailed because one of the front-panel buttons wouldn't work, which limited what we were trying to do with Modbus.

 

Save energy... recycle electrons!


   
ReplyQuote
Page 1 / 5



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security