Would I be unkind to the Grid?
At present, I have 2 Powerwall 2’s and am thinking about adding a third (Yes, I appreciate ROI is unlikely in my lifetime!) When the battery is charging from the grid, it is drawing some ~42 amps. Adding a third powerwall would take this to ~63. On top of this might be a further 13 amps for my DHW immersion element and in winter - a further ~8-10 amps for the ASHP plus perhaps another ~2 amps for fridge freezer etc. This suggests to me that at a certain time of the night, my drain on the grid could then reach approx 85-90 amps for perhaps 2 to 3 hours!
I do not know the size of main fuse but I do remember my DNO did replace it after the previous one expired 30 years or more ago. (Actually, they were fitting a new meter and changed the fuse at the same time but no way can I see what the current rating is). I think the Powerwall can be configured to charge at various rates but I have not investigated this as yet. I would rather not find out that if my supply has an 80 amp fuse, it would blow under the above mentioned load. However, my point is… Am I being irresponsible in demanding this amount of current on a domestic circuit? I have G99 approved as I have solar panels and a battery which can both export to the grid and at present, I do export up to ~ 50 amps or so. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
It’s more like it will be unkind to you!
In a damp Welsh holiday cottage in December with -2C outside we put on electric heaters to warm and dry rooms and the electric cooker was on. We blew the main fuse!
it took many hours with no power before the man arrived to reconnect us and we were cold and hungry.
Since you control your battery charging to match Agile’s lower rates you can also stagger them for a penny or two more to keep below 80% of max, and you need to know what that is. It might be 60A or it might be 100A. Main fuses are not slow-blow so a switch on transient (mainly motors) could take you over the limit.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith Oh Judith! I feel for you, during Covid Lockdown, we had SSEN working in the road on a cold winter’s day and they needed to turn off the supply for about 12 hours to carry out repairs to a section of cabling. As a consequence, we had no heating (gas c/h with electronic control and pump), no cooking (gas hob with electronic safety cut off control), no hot food as hob and microwave cookers not useable. My wife has special dietary requirements and no-one would deliver such food to us at home (no buses on our route due to Covid restrictions.) Were we glad when we had power back after dark! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 112 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
By Grantmethestrength , 17 hours ago
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 1 day ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 3 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 4 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 4 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 6 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago