The installation of a Smart Meter provides a good opportunity to have an additional 2-pole isolation switch between the meter and the consumer unit.
This is effectively just a 100A AC breaker, identical to the Mains Switch already in the Consumer Unit (aka Distribution Board).
It's held within its own DIN-rail enclosure, which must have sufficient physical space to allow easy connection of the 25sq.mm 'meter tails'
A separate isolation switch such as this allows an electrician to work within the consumer unit at a later date without having to ask the DNO to 'pull the Service Fuse".
Some Energy Suppliers will offer to have their meter engineer install an isolation switch then they fit the meter.
They will bill you separately for this work.
Alternatively you can employ a local electrician to install the isolation switch in advance of the Smart Meter being installed.
It is then ready to receive the new meter tails (double-insulated cables).
An isolation switch may not be mounted onto the same back-board as the Smart Meter and Service Fuse, although this is commonly done!
That back-board is reserved for equipment which is owned by statutory 3rd party organisations such as your DNO, Energy Supplier and DCC.
Save energy... recycle electrons!
The Smart Meter installation process has been developed to double-up as a safety-check.
The trained installation engineer operates under the Meter Operation Code of Practice Agreement (MOCOPA) between Energy Suppliers and the Electrical Networks Association.
Before the meter installation commences, the mains supply to the property is subjected to a visual inspection.
There are a number of possible deficiencies, divided into three Asset Condition Codes
These are more fully described within Annex 1.7 of the MOCOPA Guide, version 3.5, which contains excellent colour photographs to illustrate each possible fault.
You don't need to be a qualified electrician or a MOCOPA-trained engineer to report faults listed in the Guide.
Anyone who finds a mains-incomer which appears to fail one of these visual checks can report the situation to the regional DNO.
Ideally, send them a photo. That enables them to prioritise their response.
The MOCOPA Guide is within a large tranche of documents which have been allocated to the Retail Energy Code Company (RECC).
They are busy rewriting all such documents into a common format.
The 'new' Smart Meter Installation Schedule reads like a set of legal definitions, allocating responsibilities.
It is functionally useless as it omits all the tables and graphics!
I strongly recommend that you download a copy of the earlier v3.5 of the MOCOPA Guide for future reference.
You never know when it will be 'found' by RECC and deleted from the site which I've linked to!
Save energy... recycle electrons!
Ok - I've got a quite an experience, now being investigated by the Energy Ombudsman. I switched to Octopus to benefit from their Outgoing Octopus tariffs for exports. They installed a new import/export Smart Meter in November and, suddenly, our import readings went way up. We brought it to their attention and they agreed that the readings were not in accordance with our historical data, and said that they would investigate the possible 'meter discrepancy'. That was in early December.
Since that time, Octopus failed to communicate about this even with me making dozens of phone calls and sending dozens of emails, always receiving the promise that someone would get back to me 'in a day or two'. When I finally told them I'd complain to the Energy Ombudsman, they sent out an engineer to check the meter - but the engineer was not qualified to deal with 3-phase meters, which is what Octopus installed.
When I heard nothing more from Octopus and complained about the fact that they failed to send another engineer, they responded by saying that now they don't think there is a meter discrepancy (they sent me some calculations that they made more or less on the back of an envelope), but they would send another engineer who can handle 3-phrase. In the SAME email they also suggested that I hire an electrician to figure out if the meter discrepancy exists - if it does, they would reimburse the cost (yeah, I really trust that one! BTW, I asked my electrician whether he could do this, and he said that he couldn't as it requires specialised equipment). So, I filed my complaint with the Energy Ombudsman - it's been more than a month since I've heard from Octopus at all, and the Ombudsman reviewed the complaint and is now investigating it with Octopus.
So, whatever the experience with Smart Meter installation, know this: if anything goes wrong in the process you can expect that Octopus won't help you.
A footnote: we have installed electricity meters to measure the electricity use of the Ground Source Heat Pump and our borehole pump so that we can get a better idea about what percent of our imports comes from our heating system. We also have 100 solar panels and check the exports versus generation each day so, finally, we are getting a handle on total generation versus total consumption. We measure this against daily minimum temperatures. It still doesn't tell us whether the Smart Meter is working properly, but at least we can see whether the fluctuations in imports correspond to the energy use of our heating/hot water system.
That's a sorry tale @phowardstutterheim
It should not have been the case that Octopus failed to treat as a complaint your statement in December that there was a "meter discrepancy".
Nor should you have communicated so often by phone and email.
1: There are only two stages in Octopus Complaints Procedure before the issue can be taken to the Office of the Energy Ombudsman as Stage-3.
If you report the matter by email on each of those two initial stages, then you have a date/time-stamped document.
Those emails on their own are sufficient for the Ombudsman to accept the case after 8-weeks has elapsed.
2: Several of us here this Forum could advise you a number of methods by which you could check the accuracy of the Smart Meter.
Requesting an electrician to do so isn't the best option.
You really want a monitoring device which remains in the house over several days (or even weeks).
An electrician would really only be able to check your usage over a relatively short period of time whilst he's on site. That approach is prone to measurement errors.
3: All electricity meter readings are logged with ECOES, the central meter database.
That's one way in which meter fraud can be detected.
The usage can be compared over many months of use, both before and after a new meter has been installed.
ECOES data isn't available to us as consumers, but it's certainly a source of evidence which can be checked by an Energy Supplier, such as Octopus.
That it hasn't been consulted, is indicative that your case was being handled by an ordinary member of the Customer Services Dept, rather than a specialist complaints-handling officer, as stated in their Complaints Procedure.
4: As Smart Meter issues are uncommon, it's unlikely that consumers understand what they can do.
You need rapid access to those of us who understand the background technical issues (& the complaints process!).
Please advise anyone else in a similar situation to use a forum like this.
Finally, as 3-phase domestic Smart Meters are so rare, can we have a photo please! 🙂
Save energy... recycle electrons!
Thanks for your very informative missive! I'm curious as to the monitoring device that you mention - but I presume it is not available to consumers? We had an interesting situation, aside from the increase in imports - which is that, for more than two weeks, our heating system (GSHP) was completely down, but energy usage remained about the same. This may have been (party) due to the fact that a) our hot water had to be produced 100% electrically, and b) we were using a few small space heaters to try to keep warm. Otherwise, we were rather agast at this. We followed the Ombudsman procedure in full, providing all the documentation that you mention.
I'm posting photos of the 3-phase Smart Meter, as requested.
You could hire and attach a power analyser similar to the one below, or maybe you could encourage Octopus to install one for a period of time to check your present 3 phase meter.
If you have to do so yourself then one could be hired from the company detailed below.
@phowardstutterheim, did you lodge the complaint with UtilitiesADR? I’ll be curious to see how they rule, because they were our ombudsman for a solar PV complaint and they ruled in the installer’s favour (E.ON) stating that we needed to prove that E.ON hadn’t overcharged us for equipment we never received - failing to hack E.ON’s accounting system, I’m not sure how we could prove it.
I hope that your complaint goes smoothly though.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks for the photo @phowardstutterheim and let me add some labels to assist others reading this in future:
The Comms Hub is exactly the same as would be used for a single-phase site.
The row of five LED indicators tells us that the site is in the Southern or Central GB territories, for which the Smart Meter Network licence is held by Telefonica.
In the Northern territory, which includes Scotland, the Comms Hub has just two LEDs which can flash either red or green.
However, the Electricity Smart Meter Equipment (ESME) shown above is physically larger than the usual single-phase device.
The internal electronics circuity is little different, but the enclosure has to accommodate three 100A relays and eight large brass terminals at the base.
A Poly-phase ESME can operate with a 3-phase supply (as in this case), and also 2-phase, split-phase or two separate supplies that are phase independent.
It uses Vector-Sum metering which handles import and export separately across the phases.
If the site has solar-panels, with a single-phase inverter connected to just one of the phases, the customer is only billed for the difference in consumption across those phases.
Ie you don't receive export credits for what goes out on one-phase, whilst simultaneously buying back in at a much higher price on the other phases.
Unlike commercial sites, a domestic property won't be using the three phases evenly.
Most appliances are still running on 240vAC (single-phase).
It usually just a heat-pump and/or EV charger which operate as a 3-phase device.
For this reason, the Neutral won't 'rest' at zero-volts.
It will inevitably be carrying some current which must also be accounted for.
Save energy... recycle electrons!
Posted by: @editorour current metre is in the back of a kitchen cupboard and access to it is not great.
Do you mean that you built the kitchen around it?
Assuming that it's not too cramped in the cupboard you should be OK. In my daughter's case they had to organise a repositioning of the DNO fuse to make space (it was in a small cupboard in the entrance hall along with the consumer unit). Consequently, several visits by several people.
Posted by: @derek-mYou could hire and attach a power analyser similar to the one below
And there are also options to assemble one yourself using an Arduino micro-controller.
If would make a great technology project for a student at A-level or 1st-degree standard 😀
There are other alternatives using energy meters and split current-transformers bought directly from suppliers in China.
An energy-meter certified as 'MID' is regarded as being suitably accurate for billing purposes.
A split-core current transformer can be clipped around a wire without cutting into it.
It's called a non-invasive measuring device.
Save energy... recycle electrons!
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 73 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa cannot find loss calculation. When they get i...
By BAMi , 11 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 53 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 17 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 21 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 24 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 6 hours ago
-
SolarPV tables / online calculator
By MichelleC 13 hours ago
-
By Toodles 2 days ago