Do we really need a mass upgrade of electricity infrastructure at the level we have been told, or even home batteries?
This is probably a question that @transparent can answer...but here goes anyway...
Over on 'the other place' a group of us were talking about batteries and load balancing. We then got onto demand limiting even if you don't have a battery
To summarise the thought process:
- the need for the mass infrastructure upgrade that we are told is an inevitable consequence of electrification (and therefore a direct result of 'net stupid zero' as some would style it) is, at least in the domestic case, driven by heat pumps and BEV charging (and to a presumably lesser extent induction hobs replacing gas hobs)
- neither home heating nor BEV charging is time critical
- the current infrastructure is (presumably) designed to deal with peaks caused eg by everyone switching the kettle on at half time, whilst they roast a chicken in the oven (or something similar)
- so what if we simply, at the house level, switch off BEV charging and heat pumps when these relatively short duration things are happening
- this could be a relatively simple automation (based on sensing house load) and taking advantage of the supply company shut out features that (at least some) heat pumps have and the load limiting features BEV chargers have.
- The sort of thing that can be productized for diddly squat. There is an install cost of course, but with a bit of thought that could be fairly modest or simply done when the BEV/Heat pump is fitted.
- and we can easily enforce it by limiting the main breaker to (say) 60A
- ... and if you want the luxury of running everything at once, then pay a BIG premium for a 100A breaker, so that the rest of us don't have to pay for infrastructure upgrades that are required only for those who want everything (and, in many cases, don't want to pay for anything)
- or alternatively...apparently Belgium already implements tarrifs based on your average usage over 15min, so do something like that
This approach is certainly less resource intensive than distributed batteries, and very likely cheaper than the mass infrastructure upgrade we are told is necessary.
Am I smoking the wrong dope?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I recall ages ago reading a report/analysis that worked out how much upgrade we needed based on working exactly as gas. So huge morning and evening peaks adding house heating to 60C with low COP to normal cooking use in the evening/ midday. At the time I didn’t question it, other than reflecting it was not very efficient use of resources of all kinds. (This was before I knew that ashps need long and low).
I haven’t read a recent analysis and it all, obviously, depends on what the authors assume about scope for peak shifting/smoothing by any method.
A recent gov consultation was on remote control of high loads such as heat pumps so that they can be restrained from use during peak demand. The question arises of who does the controlling?
Personally I prefer to do the control myself motivated by time of use (TOU) prices, but that is probably not a mass-market option. The providers of TOU tariffs such as octopus know a lot more than anyone else on this. What percentage of the population change their use profile etc.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithPersonally I prefer to do the control myself
I agree.
I believe the take up of ToU is quite low, so there will probably have to be both stick and carrot. To date thought processes seem to have been focussed on decentralised carrot (ToU pricing) and centralised stick (forced shut down).
I guess the way the thought process I set out above was going is that there are options to apply stick without centralised control (other than over the breaker capacity). These feel much more acceptable to me than either centralised control or paying for unnecessary upgrades. Combined with some carrot I would have thought it might be possible to make a material difference. Easily linked to the installation of heat pump or BEV chargers too, so not particularly difficult to administer (although necessary to avoid this becoming a blocker to adoption).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Another topic on which @transparent will be well able to wax lyrical is that of the local situation.
I seem to remember reading a while ago that the national infrastructure was sized to take into account many huge commercial consumers that no longer exist, meaning a theoretical greater ability to deal with peak loads than might first be thought. Since reading that, it has become obvious those big hitters of old have simply been replaced by different modern ones - data centres, for instance - so I'd guess all bets are off once again with regard to consumption peaks and troughs. Either way, the consumers that completely overshadow even the hungriest of domestic needs are not uniformly placed around the country any more than the power generation facilities. As a result, and I'm sure @transparent has mentioned this more than once before, some parts of the infrastructure are under much greater strain than others, whether because of overly high demands, particularly high or seasonal generation or imbalances of one sort or another.
If there is to be some application of carrot and stick - and I certainly believe there should be - I think it is hugely important to identify which types of strain are prevalent in any given area and therefore what remedy is best to apply. I know this is encroaching on the area of localised pricing (which I know is controversial and on which I haven't formed an opinion either way yet), but it'd seem to me wasteful of resources to, for example, incentivise someone to use less power during peak times if the local problem is excessive generation. I wonder, therefore, how easy it might be to provide a simplified local message for people to say in effect "the overriding issue in your local area is X and the best way for you to help is Y." Carrots and sticks could then be juggled by area more effectively, one would hope.
To quote @jamespa, "am I smoking the wrong dope?"
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokI wonder, therefore, how easy it might be to provide a simplified local message for people to say in effect "the overriding issue in your local area is X and the best way for you to help is Y." Carrots and sticks could then be juggled by area more effectively, one would hope.
My personal assumption, which I consider to be 'safe' is that everyone acts either purely selfishly or not at all, with the latter forming the majority. Perhaps this is unduly pessimistic but I can't see a system based on people voluntarily doing something altruistic working!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
You’re not smoking the wrong dope... in fact, you’re puffing on the stuff more people probably should be inhaling when it comes to realistic grid planning.
I think you’ve hit on something really important: a lot of our assumed need for huge infrastructure upgrades is based on unmanaged electrification (everyone charging their EV, blasting the induction hob and firing up the heat pump at exactly the same time). But as you rightly point out, many of these loads are time-flexible, and with even basic demand-side management, the picture changes drastically.
EV charging in particular is low-hanging fruit. Most drivers only need to top up a few kWh per night... that’s a short charge session, easily delayed or scheduled. And heat pumps, when paired with well-insulated homes and thermal mass, don’t need to run full title minute-by-minute. They can pre-heat or coast through short demand peaks.
We already have the tools: EV chargers with built-in load balancing (Zappi etc.), heat pumps with SG-ready inputs or APIs for external control and smart meters with half-hourly data logging. All that’s missing is a joined-up strategy to use them smartly before we dig up roads.
So no, you’re not mad. The real madness is that we’re still acting like the only path forward is gold-plating every cable, instead of investing a fraction of that cost in clever, consumer-friendly demand response.
The big question: will government and DNOs push this kind of solution or keep kicking the infrastructure can down the road?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @jamespaPosted by: @majordennisbloodnokI wonder, therefore, how easy it might be to provide a simplified local message for people to say in effect "the overriding issue in your local area is X and the best way for you to help is Y." Carrots and sticks could then be juggled by area more effectively, one would hope.
My personal assumption, which I consider to be 'safe' is that everyone acts either purely selfishly or not at all, with the latter forming the majority. Perhaps this is unduly pessimistic but I can't see a system based on people voluntarily doing something altruistic working!
That wasn't quite what I was trying to suggest.
My point is that I have no idea whether my local area is being put under greater strain by me either importing loads or exporting loads. At any given time, am I exacerbating a problem or smoothing it out? If I follow your "safe" assumption and act selfishly, it'd be good for me to know what people in my area are being incentivised to do and what actions might carry penalties. Clearly, it seems to me, with parts of the country that are power generating deserts and others that are conspicuous consumers the carrots and sticks could do well to be customised to fit local needs; one size doesn't fit all.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokClearly, it seems to me, with parts of the country that are power generating deserts and others that are conspicuous consumers the carrots and sticks could do well to be customised to fit local needs; one size doesn't fit all.
I agee with that.
I suspect however that the structure of the electricity industry and the political nightmare a postcode lottery electricity supply would represent means that, while doubtless technically sensible, it's not going to fly. Hence the suggestion that every house simply limits its own peak, being either incentivised to do so through carrots, or compelled through sticks.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
You may well be right, @jamespa.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
OK... I'm here. But the amount of my time needed to address this is issue is greater than what I have available!
Posted by: @editorThe real madness is that we’re still acting like the only path forward is gold-plating every cable, instead of investing a fraction of that cost in clever, consumer-friendly demand response.
Precisely!
I attended last month's Briefing for those forming the Transitionary Regional Energy Strategic Plan (RESP) body for my area.
The staff based at NESO want us to create the RIIO-ED3 Agreements which are the 'Contracts' between DNOs and Ofgem from April'27 onwards.
However the emphasis is on "ensuring that we're building enough infrastructure" to cope with Demand, and to connect all the generation & storage sites which NESO is busy reassessing at the moment.
There doesn't appear to be space for an alternative to building a massive grid.
That's not good...
... nor particularly Smart.
But anyone can contribute to these tRESP discussions.
You start by sending an email to box.resp@neso.energy
and please say which RESP area you're in.
The detailed maps are at the end of this Decision Notice (PDF) issued by Ofgem.
Posted by: @majordennisbloodnokthe national infrastructure was sized to take into account many huge commercial consumers that no longer exist, meaning a theoretical greater ability to deal with peak loads than might first be thought. [...] As a result [...] some parts of the infrastructure are under much greater strain than others, whether because of overly high demands, particularly high or seasonal generation or imbalances of one sort or another.
Yes. The electricity network topology was designed and built 100-years ago, based on the need for a main Transmission Grid (400kV) with relatively few large power stations.
Big industry users were placed close to that Transmission Grid, whilst the rest of the country was supplied by four layers of voltages on the regional Distribution Grid.
The situation is now very different.
Most of our generation is now connected at the Distribution Grid level.
That's the solar-farms, wind-farms and hydro-electric stations which are required to meet Net Zero.
But
1: the commercial energy sector would still like to invest in a large Transmission Grid because it gives them access to sell 'our' electricity via the marine interconnectors
2: DESNZ has been told by No.10 that they shouldn't move towards Nodal Tariffs (geographically based pricing) because it would favour some constituencies over others.
Posted by: @jamespa
- what if we simply, at the house level, switch off BEV charging and heat pumps when these relatively short duration things are happening
- this could be a relatively simple automation (based on sensing house load) and taking advantage of the supply company shut out features that (at least some) heat pumps have and the load limiting features BEV chargers have
This is roughly what DESNZ is working on under its Demand Side Response project.
However, they intend this to operate using centralised control and a database which amalgamates those commands with our metered energy accounts.
That's not the same as the concept of Demand Side Response which was approved by Parliament in Nov'14 when Smart Meter legislation was being put into law.
Here's a Government public information leaflet about Smart Metering, published two years later
Save energy... recycle electrons!
There are some projects looking at how smart meters and the smart meter network can be used in demand management.
Here is one for example
Whether the network is ever utilised at scale in the real world in the UK I have my doubts, just like I thought zonal pricing was a non starter for a variety of reasons not just politics around constituency voters. Getting investment into the UK generally right now is just a bigger problem as votes.
If you focus too much on the HAN etc to control demand you may end up frustrated I fear. But obviously up to you. So much money has already been invested elsewhere already it may already be a done deal.
The transition to renewables is messy generally right now. It looks like the 600k annual heat pump target may be scrapped as it is unaffordable. EV sales are struggling, hence the upcoming EV grants. Behind the positive headlines there are lots of issues.
Circa a third of energy consumption in the UK is from residential currently even with the loss of industry in the UK so there is a lot to consider as well as residential demand management.
It is certainly going to be interesting to see how things evolve over the next few years.
It's unclear to me how the Smart Control project work by Salford University and Hildebrand would be used.
At this stage it appears to be raw research, rather than yielding any particular product.
Unlike the Demand Side Response initiative led by DESNZ, the Salford Smart Monitor offers proportional control over home energy appliances.
It also uses the messaging system within our Smart Meters to send information about household temperature.
That could theoretically be combined with electricity consumption data to identify houses with poor energy efficiency.
Who might wish to pay DCC to receive such data isn't clear, nor what they would then do about it.
Posted by: @jeffCirca a third of energy consumption in the UK is from residential
The Digest of UK Energy Statistics Chapter-5 published last week shows 2024 domestic electricity consumption at 30%.
Note that Energy Industry Losses are stated at 9%.
However, those losses are dominated by the effects of phase imbalance and harmonics induced by domestic consumption.
That's because a high proportion of commercial/industrial electricity demand is 3-phase.
Smart Control of domestic use could significantly reduce those losses at the local sub-station.
But the approach being made by Salford/Hildebrand doesn't address this issue, nor the constraints on the area Distribution Grid.
Save energy... recycle electrons!
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 33 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
Could someone remind me of any interaction between any ...
By DavidAlgarve , 9 minutes ago
-
-
RE: Does anyone have experience of a smart water meter?
Thanks, @technogeek; yet more colour to the picture and...
By Majordennisbloodnok , 2 hours ago
-
@drei Hi, Its unfortunate you are not in Kent otherwise...
By ASHP-BOBBA , 13 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 2 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 3 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 3 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 4 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 6 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 6 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 7 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 7 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 week ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago