@derek-m Correct but the best way to control flow is automatically with equipment that can do it for you. If your system does not have Delta T contro...
@soniks Firstly, the engineers at Grant need to buy a new calculator or go back to school. 50 L/min will transmit 28Kw. You only need to transmit abou...
@soniks As I said, 28 mm will be fine, a 28 mm pipe has an internal diameter of 26.2 mm, the Grant 17 Kw will produce about 14 Kw at -2 at 50 odd degr...
@soniks change 28 mm primaries--- wrong, I have 30Kw heat pumps on 28 mm primaries very successfully Buffer tank--- Wrong in any circumstance unless...
@kev-m I understand where you are coming from, but it is wishful thinking. The industry did try to do exactly what you are asking and came up with the...
@derek-m Oh I wish. Unfortunately, we follow behind a myriad of idiots that blow your assumptions out the water.
@kev-m Unfortunately you are Oh- So-Wrong. If the builders had followed the building regulations over the last 30 years, you may be right, but they ha...
Yes, there will be a website, branding and end to end support for both the installer and the homeowner.
That is not going to happen. The housing stock is so different that there is no option but a bespoke approach. Train the installers properly in the te...
@alec-morrow I could not agree more and that is exactly what we are doing. Our main problem is the horrendous design of the majority of systems requir...
@editor I do not expect there to be any improvement in the current training or regulatory regime. There are too many people making lots of money out ...
- 22 Forums
- 2,096 Topics
- 46.2 K Posts
- 122 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 I asked Wattson: What is ‘intell...
By Toodles , 3 hours ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 7 hours ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 9 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 1 day ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 1 day ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 2 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 3 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 4 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 4 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 4 days ago