@derek-m Correct but the best way to control flow is automatically with equipment that can do it for you. If your system does not have Delta T contro...
@soniks Firstly, the engineers at Grant need to buy a new calculator or go back to school. 50 L/min will transmit 28Kw. You only need to transmit abou...
@soniks As I said, 28 mm will be fine, a 28 mm pipe has an internal diameter of 26.2 mm, the Grant 17 Kw will produce about 14 Kw at -2 at 50 odd degr...
@soniks change 28 mm primaries--- wrong, I have 30Kw heat pumps on 28 mm primaries very successfully Buffer tank--- Wrong in any circumstance unless...
@kev-m I understand where you are coming from, but it is wishful thinking. The industry did try to do exactly what you are asking and came up with the...
@derek-m Oh I wish. Unfortunately, we follow behind a myriad of idiots that blow your assumptions out the water.
@kev-m Unfortunately you are Oh- So-Wrong. If the builders had followed the building regulations over the last 30 years, you may be right, but they ha...
Yes, there will be a website, branding and end to end support for both the installer and the homeowner.
That is not going to happen. The housing stock is so different that there is no option but a bespoke approach. Train the installers properly in the te...
@alec-morrow I could not agree more and that is exactly what we are doing. Our main problem is the horrendous design of the majority of systems requir...
@editor I do not expect there to be any improvement in the current training or regulatory regime. There are too many people making lots of money out ...
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 57 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 57 minutes ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer pleased you found it!
By JamesPa , 2 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 4 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 7 hours ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 7 hours ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 20 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 20 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 1 day ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 1 day ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 2 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago