Its the flow temperature for the heating circuit, it means its running a fixed flow temp and is not on weather compensation, get that changed come the...
@m1kegibson Apologies if I'm teaching grandma to suck eggs but have you confirmed the max temp drop in the controller is set to 10C? To do that you h...
Hi it’s 6 years old first issue it’s ever had.The sensor is cheap £33 it’s the HVAC engineer cost £305 plus VAT
£400 later and it’s fixed it was the T3 sensor that measures the condensed refrigerant temp it should read single figures was reading 65C and occasion...
@editor thanks Mars that’s the same table I found in the service manual it’s does feel like it’s the sensor that’s at fault. When it stopped it was r...
@editor I found some info in the service manual it could be a bad condensing temperature or pressure sensor. It shuts down the heat pump if condensi...
@editor thanks Mars just waiting for support to open at 8am
Thanks it doesn’t provide anymore info just says UD-0
Where is the heat pump controller going that will be the thermostat it just needs to be in a sensible location. If you are running weather comp the ...
@robs Thanks that's what I suspected mine definitely doesn't have it.
@carpenterstation because heat pumps are built by engineers and have not been historically developed for the average human to be able to operate, henc...
- 26 Forums
- 2,177 Topics
- 47.9 K Posts
- 57 Online
- 5,748 Members
Podcast Picks
Latest Posts
-
RE: Say hello and introduce yourself
Welcome in, @pirate-rich. Glad to have you on board and...
By Majordennisbloodnok , 15 minutes ago
-
RE: Powerwall 3 or Myenergi or something else?
Let's also bear in mind that Fogstar supply more than o...
By Majordennisbloodnok , 2 hours ago
-
RE: Repiping and Reconfiguring our Heat Pump System Including Removing the Buffer Tank
@grantmethestrength, if you pull the trigger on the FRV...
By Mars , 6 hours ago
-
RE: How to choose Towel Rails for an ASHP
@judith Yes I agree. They are extremely expensive. ...
By GrahamF , 6 hours ago
-
RE: Which temperature sensor for a Steibel buffer and Ecodan?
@downfield I have never added a buffer sensor as we nev...
By ASHP-BOBBA , 6 hours ago
-
Riello NXHM Monobloc Air Source Heat Pump
Hi, does anyone have any feedback on Riello NXHM Monobl...
By dgarvey , 14 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
This is actually based on the same chipset as the Svena...
By Grantmethestrength , 18 hours ago
-
-
RE: How to Zone with a Single Room with UFH
We have exactly what you describe, one utility room wit...
By Judith , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Come the Ist of October, the Cosy cheapest...
By Toodles , 1 day ago
-
RE: Boxt Heat Pump Installation Experience
@ashfp Mine does have a buffer tank. That was my experi...
By Andrew J H , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
I'm sure you are right, I was just trying to understand...
By JamesPa , 2 days ago
-
RE: Preparing for 2nd winter in new build house.
Yuch! So that's basically just an on/off control. I...
By Transparent , 3 days ago
-
Good day everyone. I'm new here and have a few question...
By Edin67 , 3 days ago
-
RE: MCS certificate SCOP vs real-world performance
That may be contributing to lower than expected SCOP. ...
By JamesPa , 4 days ago
-
-
RE: Mitsu PAR-WT60R Wireless Controller - options
How it does it's job is something of a mystery although...
By Abernyte , 4 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 6 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 6 days ago