RE: Ecodan with FTC7 controller DHW schedule

@davidalgarve There are 2 heating modes for DHW Eco and Std, Eco as it suggests uses less input power but takes longer, so if you aren't on that alrea...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

@clockworks under reports there is an hourly temp plot that you can then choose by hour, its starts with the current hour but if you click on the time...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

@clockworks if you could post the hourly temp plots rather than the last 24 hour ones they will have all the detail that should match your other plots

5 months ago
Reply
RE: Ecodan flow rate tweak

I would give the Mitsubishi customer help line a call, the manual does say if you want to get max flow you will need to install an additional pump, se...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

If you post Melcloud graphs its worth clicking off all the other series you don't need, like set tank temp, this allows the plots to rescale to the da...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

If you want to use auto adapt then you will either need to get the main controller sited somewhere where it can get a good temperature reading or as ...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

With your increased curve and increased OAT (outside ambient temp) it was still trying to run around 38C. Between 1.40 and 3.40 you have the same cy...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

@sunandair Clockwork means DT25 of the rads at design flow of 45C vs a room temp of 20C or thereabouts

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

@clockworks Higher flow temps will get less cycling but at the cost of efficiency and you will find then it will run for a couple of hours and then re...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

@clockworks I wouldn't change the flow temp yet, try and see if its any better at 38C if you drop the flow temp cycling is only going to get worse any...

5 months ago
Reply
RE: Ecodan 6kW - is it "cycling", or normal operation?

The flow wasn't massively out, I'm no heating engineer but a heat pump needs constant flow, so the differential flow setting doesn't seem right and th...

5 months ago