Water pump operation choices on my Harnitek heat pump
Hi Chaps
I am looking at the water pump operation choices on my Harnitek heat pump .
i have three choices in the software options ,these are..
1) interval working mode
2) on constantly
3) off with compressor .
choice 1 is programmable, so it switchs off with the compressor, but then switches on for a set amount of time , and then off again for a set amunt of time , at the factory setting, its off for 6 mins then on for 1 min etc .repeating .
as far i i can tell with my data logging , this does not work at all , and it simply goes on and of with the compressor .
so i wonder , how do other ASHP's control their water pumps ?
O-er @ivanhoew
You are going to get a mixture of replies to that.
Let me start by suggesting how your heat-pump should've been commissioned....
1: An ASHP should operate continuously, rather than cycle on/off in response to external control (from a thermostat).
That being so, the compressor won't ever be off.
2: Most water circulation pumps have their speed adjusted according to the required flow-rate.
There are pumps which incorporate their own speed modulation...
... but the pump is generally controlled by a (digital) signal supplied from the heat-pump.
So your question implies that your system has been fitted with a circulation pump without modulation 😥
Can I suggest you give us the model numbers for the ASHP and the circulation pump.
If you can photograph the latter, that would be better still.
Building Regulations, Part-L, section-9 requires you to have been provided with site specific information on what has actually been installed in your home.
Do have the system diagram which you could post here?
Save energy... recycle electrons!
its a harnitek 12V1TBA-250L ashp , PUMPis intgral to the harnitek indoor 250 litre tank cabinet , controlled by the harnitek ecu .
pump model is WILO PARA 25-130 /987/1PWM1.
i think this is an ac pwm unit . i can datalog a varying pwm signal , but , when it does this it's also showing as pump status status 0, as opposed to pump 1 which i asumed means its on .
the system runs weather comp ,set v low ,27-31c and cycles between every 20 minutes and greater depending on the FT and ambient .
Re:
"1: An ASHP should operate continuously, rather than cycle on/off in response to external control (from a thermostat).
That being so, the compressor won't ever be off."
I would love to see an example of a heat pump installation that operates continuously ,with the compressor never being off ,with no cycling , in all weathers and times of year ?
from what i have read on here , especially clockworks thread on cycling , it seeems a lot of heat pumps switch on and off ,gaps anywhere from 20 m to an hour . .
what i want to know is what happens to thier circulation pumps when that cycling is happening .
i can log and show graphs if it helps to understand what i mean . 🙂
regards
robert
So you have this model with an integrated 250-litre DHW cylinder.
Posted by: @ivanhoewpump model is WILO PARA 25-130 /987/1PWM1.
i think this is an ac pwm unit . i can datalog a varying pwm signal , but , when it does this it's also showing as pump status status 0, as opposed to pump 1 which i asumed means its on .
The Harnitek data sheet suggests that there are (at least) two pumps
- inside the internal unit, supplying water to the 4-port buffer tank
- after the buffer, in the flow pipe to your radiators, alongside a motorised mixer valve
That requires some detailed expertise/knowledge to commission.
The two circulation pumps could be fighting each other, with the buffer-tank standing between them.
At this stage I don't know which pump you're referring to, let alone how the Harnitek firmware is adjusting the pump speeds in response to the flow/temperature sensors.
Their literature suggests this is a 'black box' which can be quickly installed and that it sorts itself out 🤔
How are you "datalogging a varying pwm signal"?
How does that correspond to what the Harnitek App/Display states?
Posted by: @ivanhoewit seeems a lot of heat pumps switch on and off ,gaps anywhere from 20 m to an hour . .
what i want to know is what happens to thier circulation pumps when that cycling is happening .
I think that question is going to tax the combined efforts of @jamespa @cathoderay and @majordennisbloodnok
because what happens with other ASHPs may not reflect what Harnitek's algorithms do.
What buffer-tank do you have and what sensors are connected to it for flow and temperature readings?
Do you have:
- the commissioning checklist sheet?
- the site-specific system schematic for your particular installation?
- the energy survey report with its system design parameters?
Save energy... recycle electrons!
ThanksTP , no, no buffer tank, one pump .
i log the pwm on my inbuilt harnitek logging SW .
RE:
"Do you have:
- the commissioning checklist sheet?
- the site-specific system schematic for your particular installation?
- the energy survey report with its system design parameters?"
nope none of the above , just the user manual , and the wi fi dongle to connect the pump ecu to my laptop .
dont get me started on eco4 install support !!
i recognise other makes may have different methods , thats what i wanted to know , what those methods are .
with my system i can change all the parameters , but am curious to know what other makes deem the best more efficient way to run the water pump , on all the time , on only with the compressor , or on and off at times intervals independant of whether the ashp is running .
heres an example of compressor and water pump speed changes as logged ...
if yuo look at the legend above you can see what colour means what , and that when the ashp tuns off , so does the water pump , at least its status goes to zero , which i assume meansx its off ...even when its pwm is showing an adjustment ! very odd .
regards
robert
- 21 Forums
- 1,961 Topics
- 42.5 K Posts
- 60 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
I hope there is a good view through the large window, I...
By JamesPa , 3 minutes ago
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 6 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 56 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 12 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 13 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 15 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 21 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 24 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 56 minutes ago
-
SolarPV tables / online calculator
By MichelleC 8 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 20 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago