Hi all,
new to the forum and looking for some help please as I’m a bit at loss with my heating system.
In short, I run a 35KW Viessmann boiler that’s operates by a Vitotronic 200-H. The system has a LLH and 3 heating circuit pumps with mixer valves (one for underfloor heating, one for downstairs rads and one for upstairs rads), plus another pump for the hot water tank. Everything is weather compensated.
My issue is essentially that not enough heat is being drawn from the low loss header. The hot water tank takes around 2-3hrs (!!) to get to it’s desired 50c temp, and on the heating circuits, the flow temp never really gets above 40, even if the boiler is producing 75c+.
As an experiment we removed the LLH, which seemed to improve things, however the boiler was then constantly running at 75c (rather than running at reduced temps of ~50-60 due it’s weather compensation), whilst the radiators were still only getting up to ~40.
We’ve since re-installed the LLH which makes the boiler operate like it should (running at Lower temps), but now the mixer valves seem to be stuck on cold (it’s 8c outside) and having a flow temp. of no more than ~25. I’ve tried increasing the heating slope and curve and whilst this makes the boiler temps increase, the mixers refuse to move and flow temps are low. The LLH is boiling hot but no heat seems to be leaving this.
Any ideas? Could the LLH have failed (there was a lot of rust in it when we cleaned it out)? Could there be sludge/build up in the system causing this?
Any ideas/suggestions would be very welcome!
thanks in advance!
It rather sounds as though you have a build up of sludge from what you say about the LLH. Has the system ever been power flushed? Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles we had it done last year (the magnet one, rather than a power flush) but there does seem to be sludge around as there is still lots of bits and fillings in the small magnaclean filter.
At the moment, we have a huge loss of heat between the LLH and the DHW and virtually a 100% loss between the LLH and the heating circuits. When the LLH was removed, it was better (got ~40c into the heating circuits) but the boiler wasn’t modulating then.
@hubb84 The Magnaclean filter is for everyday removal of particles of any ferrous material circulating in your pipework; I doubt that even if you cleaned out the filter daily, you would ever be likely to achieve a fraction of the muck removal that a power flush would. I’m not trying to suggest that this is your ONLY problem but the fact that you found a lot of sludge in the LLH and the Magnaclean also picked up some particles seems to suggest their is muck in your system and it isn’t Yorkshire Brass!
Your pump would appear to be able to deliver the heat you want but as it is not flowing into the radiators properly (or the DHW tank) it rather suggests a very restricted flow. This may be muck, it may be valves that aren’t opening fully - both aspects are worth checking I think. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles ok thank you. I’ve booked a power flush for next week and see where it goes from there. I agree that there seems to be some sort of restriction, so it’s just trying to find what and where.
will update next week!
ok so update from today: they tried to hook up a Magnaclean (the big one) on the return but we weren’t getting any, or very little, flow. This would explain why things take so long to warm up, or don’t get warm at all.
We checked all pumps and one (on the downstairs radiator circuit) has failed. Whilst this makes sense for not having any flow on that circuit, I don’t understand why we had the same issue when turning this off and running the other circuits separately.
Took two radiators off and both were quite full of stuff, but when we tried to flush the system just with the mains pressure, it was clear.
They’re hesitant to do a power flush as we have a lot of plastic piping too…anyone have experience with this?
At a bit of a loss now as to what to try/do next.
@hubb84 No experience here I’m afraid, but I think your work has confirmed that you have sediment build up. If plastic piping isn’t up to a power flush, might there be a chemical approach? I have in mind using a solvent or sludge softening agent of some sort (if there is such a thing???) I would imagine the likes of Fernox would be the people to ask about such a solution.
Perhaps the pump that failed died of congestion? Are there any power flushing schemes that use suction rather than pressure? Sorry no solution but lots of questions from someone with very little knowledge of such a problem. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@hubb84 Try looking at powerflushassociation.com. They may have a solution to your need to flush out plastic pipes. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 43 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 19 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 45 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 1 hour ago
-
What is the best strategy for operating a very oversized heat pump?
As the title really. There are at least three live thr...
By JamesPa , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 13 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 16 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 18 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 20 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 21 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 22 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 9 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 21 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 24 hours ago
-
By Toodles 2 days ago