Skirting board radiators
Has anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Posted by: @neilhHas anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Hi Neil,
An interesting concept.
I noticed from their performance data that they are only showing figures for water flow temperatures of 45C, 50C and 55C, which is the inefficient range for operating an ASHP.
Based on their data you would require the following lengths of ThermaSkirt to replace a 1200mm x 600mm radiator, to achieve the same heat output.
Deco BM2 15.4m for type 22 (double panel) and 22.6m for type 33 (triple panel)
Deco BM3 10.4m for type 22 (double panel) and 15.2m for type 33 (triple panel)
It would be interesting to see how they perform at lower water flow temperatures.
Since ASHP's operate at their best efficiency at the lowest water flow temperature that meets the heat demand, it is important to have heat emitters with the greatest output at a given water flow temperature. The larger the area of the heat emitters, the lower the water flow temperature would need to be.
How do ThermaSkirt compare in price to a standard radiator or UFH?
Â
Â
@derek-m  Ah yes. Though in princple the lengths are probably not a problem. I'm just in exploratory ideas phase at the moment so no prices sought. I still like in-wall idea, especially the 3Thermo design (if I can get some decent technical details). Perhaps different solutions for different rooms, given good zone control system.
Hi Neil,
One of the things I enjoy about the forum, is that there are people like yourself who just don't accept the norm, but look for alternatives that may or may not be an improvement. For much of my career I have been expanding the envelope to find solutions to long standing problems, just because something has been done a certain way for many years does not mean that it cannot be improved.
Posted by: @neilhPosted by: @derek-mjust because something has been down a certain way for many years does not mean that it cannot be improved.
Else we'd be sitting round a fire in a cave !
Don't knock caves, I'm in my 'man cave' right now.
I have just had a look at the 3Thermo system that you highlighted, it also looks very interesting. They specify an energy output of 250W/m2, but don't state what the water temperature would need to be to provide that output. I wonder if it could be installed over existing plaster or whether the plaster would need to be removed and then the wall re-plastered after installation.
I suppose in an ideal world we would have a system that has underfloor heating, wall heating and skirting heating, all supplied by a heat pump that is running at 25C with an outside air temperature of -10C.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 119 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer great you located the source of the issue a...
By Mars , 4 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 13 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 19 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 21 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 1 day ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 1 day ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 2 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 2 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 3 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 3 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 4 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 5 days ago