help with new bathroom and towel radiator
having a big renovation of the house so getting a heat pump in at the same time, but ive got a problem room. weve created a new bath/util room with a dedicated plant room within it for the HW tank etc. the ceiling is insulated the floor is insulated the walls on both sides are insulated. the other 2 walls are thermal type blocks. whole room is dot and dabbed. tiny double glazed window 400x800. heat loss for the whole area is 593W for just the actual area that is the bath/util its about 492W. im struggling to find a stainless steel towel rad that will fit in the 550Wx2300H wall that can manage much more than 250W at the 40c design flow. dont want to use underfloor and floors tiled now anyway. dont want to use normal rads if possible as they tend to rust. the main flow and return 28mm's to the house are running in the ceiling void so might help with some heat into the room?
ideas?
Can you include the heat loss from the plant in the calculations, as these may help you meet the heat loss for the room? A DHW tank can lose (emit) 100W per hour, and a volumiser 50W, not to mention uninsulated pipework.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @adamkhaving a big renovation of the house so getting a heat pump in at the same time, but ive got a problem room. weve created a new bath/util room with a dedicated plant room within it for the HW tank etc. the ceiling is insulated the floor is insulated the walls on both sides are insulated. the other 2 walls are thermal type blocks. whole room is dot and dabbed. tiny double glazed window 400x800. heat loss for the whole area is 593W for just the actual area that is the bath/util its about 492W. im struggling to find a stainless steel towel rad that will fit in the 550Wx2300H wall that can manage much more than 250W at the 40c design flow. dont want to use underfloor and floors tiled now anyway. dont want to use normal rads if possible as they tend to rust. the main flow and return 28mm's to the house are running in the ceiling void so might help with some heat into the room?
ideas?
I persuaded my installer that heat loss from the adjacent hallway plus steam when you actually take a bath/shower was sufficient (in order that we didn't have to replace an existing towel rail). In practice its true!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@adamk I'm sure I recently answered a similar question but here you go:Nordic Omega Aluminium
This is what I put in my bathroom to give me high output at low flow temperature in a small space and it had to look good.
I took a punt on it initially and it has very much exceeded my expectations. The finish absolutely shrugs off any moisture in the air, the technical design is unlike anything I've ever seen with vertical convection fins and it packs out the heat. They come in multiple sizes.
If you are not in a hurry they will produce almost any RAL colour finish that you want.
Posted by: @lucia@adamk I'm sure I recently answered a similar question but here you go:Nordic Omega Aluminium
This is what I put in my bathroom to give me high output at low flow temperature in a small space and it had to look good.
I took a punt on it initially and it has very much exceeded my expectations. The finish absolutely shrugs off any moisture in the air, the technical design is unlike anything I've ever seen with vertical convection fins and it packs out the heat. They come in multiple sizes.
If you are not in a hurry they will produce almost any RAL colour finish that you want.
what about galvanic corrosion as i have copper pipes and other steel rads.
@adamk Truthfully, I'd never heard of such things. Google (from sensible sources) says there needs to be an electrical contact with both metals. Not in my bathroom, thanks. 🙂
Seriously, Aluminium is highly rated for radiators and 100% recyclable. They're also a joy to hang because of being much lighter than steel. I'm very pleased with mine.
Posted by: @luciaGoogle (from sensible sources) says there needs to be an electrical contact with both metals. No in my bathroom, thanks. 🙂
Except that water is a conductor.
Galvanic corrosion is a well known process problem with steel narrowboats, with the conductor being the water, so I wouldn't rule it out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa What I know about radiators you could write on the back of a postage stamp. And most of that you guys taught me when I was buying a heat pump. 😁
But isn't corrosion the reason why we put inhibitor in radiators? Certainly my plumbers do. Whatever they're made of.
The radiator I linked to is a beautifully (Italian) made piece of metal with a 15 year guarantee. I'm fine with that. My last lot of rads lasted about 40 years (although to be fair, they weren't ally)
I'll save my stress for Gaza and madmen with nukes in the Whitehouse. However, if all else fails, the scrap value of Aluminium is pretty good and pretty constant. 😉
Posted by: @luciaBut isn't corrosion the reason why we put inhibitor in radiators? Certainly my plumbers do. Whatever they're made of.
Yes it is.
Steel narrowboats have zinc anodes for the same reason, but the steel still rusts, just less slowly.
I have not personally heard of galvanic corrosion being a problem in central heating systems nor have I seen warnings from radiator manufacturers about mixing materials so I'm guessing it's not actually much of a risk. It might be worth asking the question though to see what the reaction is.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I see that boats in saltwater are now being suggested to use aluminium anodes which I believe also work in fresh water, whereas zinc is passivated in fresh water. Don't some hot water tanks have an anode? Thankfully we don't use seawater in our heating systems! 😀
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
- 22 Forums
- 2,072 Topics
- 45.4 K Posts
- 39 Online
- 3,350 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 5 hours ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 8 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
Hi Bobba, thank you so much for the considered and deta...
By MelonBuffet , 8 hours ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 10 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 11 hours ago
-
RE: What’s the modern take on advised types of insulation?
The former Energy Secretary claims his 1930s house is “...
By Mars , 15 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Johnmo , 1 day ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Actually I might try just turning it off and on again…....
By benson , 2 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 3 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 4 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 4 days ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 4 days ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 4 days ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 4 days ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 5 days ago