help with new bathroom and towel radiator
having a big renovation of the house so getting a heat pump in at the same time, but ive got a problem room. weve created a new bath/util room with a dedicated plant room within it for the HW tank etc. the ceiling is insulated the floor is insulated the walls on both sides are insulated. the other 2 walls are thermal type blocks. whole room is dot and dabbed. tiny double glazed window 400x800. heat loss for the whole area is 593W for just the actual area that is the bath/util its about 492W. im struggling to find a stainless steel towel rad that will fit in the 550Wx2300H wall that can manage much more than 250W at the 40c design flow. dont want to use underfloor and floors tiled now anyway. dont want to use normal rads if possible as they tend to rust. the main flow and return 28mm's to the house are running in the ceiling void so might help with some heat into the room?
ideas?
Can you include the heat loss from the plant in the calculations, as these may help you meet the heat loss for the room? A DHW tank can lose (emit) 100W per hour, and a volumiser 50W, not to mention uninsulated pipework.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @adamkhaving a big renovation of the house so getting a heat pump in at the same time, but ive got a problem room. weve created a new bath/util room with a dedicated plant room within it for the HW tank etc. the ceiling is insulated the floor is insulated the walls on both sides are insulated. the other 2 walls are thermal type blocks. whole room is dot and dabbed. tiny double glazed window 400x800. heat loss for the whole area is 593W for just the actual area that is the bath/util its about 492W. im struggling to find a stainless steel towel rad that will fit in the 550Wx2300H wall that can manage much more than 250W at the 40c design flow. dont want to use underfloor and floors tiled now anyway. dont want to use normal rads if possible as they tend to rust. the main flow and return 28mm's to the house are running in the ceiling void so might help with some heat into the room?
ideas?
I persuaded my installer that heat loss from the adjacent hallway plus steam when you actually take a bath/shower was sufficient (in order that we didn't have to replace an existing towel rail). In practice its true!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@adamk I'm sure I recently answered a similar question but here you go:Nordic Omega Aluminium
This is what I put in my bathroom to give me high output at low flow temperature in a small space and it had to look good.
I took a punt on it initially and it has very much exceeded my expectations. The finish absolutely shrugs off any moisture in the air, the technical design is unlike anything I've ever seen with vertical convection fins and it packs out the heat. They come in multiple sizes.
If you are not in a hurry they will produce almost any RAL colour finish that you want.
Posted by: @lucia@adamk I'm sure I recently answered a similar question but here you go:Nordic Omega Aluminium
This is what I put in my bathroom to give me high output at low flow temperature in a small space and it had to look good.
I took a punt on it initially and it has very much exceeded my expectations. The finish absolutely shrugs off any moisture in the air, the technical design is unlike anything I've ever seen with vertical convection fins and it packs out the heat. They come in multiple sizes.
If you are not in a hurry they will produce almost any RAL colour finish that you want.
what about galvanic corrosion as i have copper pipes and other steel rads.
@adamk Truthfully, I'd never heard of such things. Google (from sensible sources) says there needs to be an electrical contact with both metals. Not in my bathroom, thanks. 🙂
Seriously, Aluminium is highly rated for radiators and 100% recyclable. They're also a joy to hang because of being much lighter than steel. I'm very pleased with mine.
Posted by: @luciaGoogle (from sensible sources) says there needs to be an electrical contact with both metals. No in my bathroom, thanks. 🙂
Except that water is a conductor.
Galvanic corrosion is a well known process problem with steel narrowboats, with the conductor being the water, so I wouldn't rule it out.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa What I know about radiators you could write on the back of a postage stamp. And most of that you guys taught me when I was buying a heat pump. 😁
But isn't corrosion the reason why we put inhibitor in radiators? Certainly my plumbers do. Whatever they're made of.
The radiator I linked to is a beautifully (Italian) made piece of metal with a 15 year guarantee. I'm fine with that. My last lot of rads lasted about 40 years (although to be fair, they weren't ally)
I'll save my stress for Gaza and madmen with nukes in the Whitehouse. However, if all else fails, the scrap value of Aluminium is pretty good and pretty constant. 😉
Posted by: @luciaBut isn't corrosion the reason why we put inhibitor in radiators? Certainly my plumbers do. Whatever they're made of.
Yes it is.
Steel narrowboats have zinc anodes for the same reason, but the steel still rusts, just less slowly.
I have not personally heard of galvanic corrosion being a problem in central heating systems nor have I seen warnings from radiator manufacturers about mixing materials so I'm guessing it's not actually much of a risk. It might be worth asking the question though to see what the reaction is.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I see that boats in saltwater are now being suggested to use aluminium anodes which I believe also work in fresh water, whereas zinc is passivated in fresh water. Don't some hot water tanks have an anode? Thankfully we don't use seawater in our heating systems! 😀
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
- 26 Forums
- 2,275 Topics
- 50.9 K Posts
- 83 Online
- 5,936 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
It has it's uses and there is no way I could have set t...
By benson , 8 hours ago
-
Samsung Gen6 and Havenwise ........
I sourced the Wi-Fi unit (City Plumbing - £122 with 15%...
By Lenny , 8 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Definitely. 8C DT is higher than the default design DT...
By JamesPa , 10 hours ago
-
@jamespa Thanks again for your reassurance. Rob
By Ubert767 , 15 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
Thanks for the suggestion, but farmhouse is grade 2 lis...
By paultheheating , 17 hours ago
-
RE: My DIY Heat Pump installation
This is very kind. However software is not really my ...
By Polar bear , 22 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 1 day ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 1 day ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 2 days ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 2 days ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 2 days ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 2 days ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 3 days ago