Convert Pt1000 to NTC 20 kΩ?
Posted by: @derek-mWhat is the problem with the old controller?
It works fine but the integration with the rest of the system is rather clumsy. For solar back off, a relay in the SKSC2 drives a contactor which adds a resistor that makes the the thermal store appear to the system controller to be hotter than it really is. Also the RESOL DL2 data logger attached to the SKSC2 has died. Both the SKSC2 and RESOL DL2 were installed around 15 years ago.
My current thoughts are to replace my existing Viessmann Vitodens 200-W (type WB2C) with the latest version (type B2HF). The existing uses KM Bus and the latest version uses PlusBus so the wall mounted mixer extension will need to change. It seems like a good time to also change the solar controller to achieve better integration. I'm considering a Vitotrol 300-E as well. Might also replace the solar pump (how long do they last?). The upgrade should be straightforward, apart from the solar collector sensor ...
Posted by: @djhPosted by: @john-connettThe Pt1000 Resistance Table is straightforward. NTC Thermistors, Resistance/Temperature Conversion is more complex. I know it should measure 20 kΩ at 25°C but I'm not sure which of the 17 curves to apply?
Using the curve in the Viessmann guide you can see that the resistance at 140°C is about 0.5. So Rt/R25 is 0.025. You can then look at your 17 curves and see what the best match is. You could just estimate an approximate equation to match the Viessmann curve instead of trying to emulate an actual device. Or ask Viessmann what device it is?
Good suggestion. I am in the process of doing something similar to see which of the 15 (1-14, 17) Vishay curves is a good fit (It will also be interesting to see how the Ohmigo NTC 20 kΩ table compares). A table from Viessmann would have been more convenient for the comparison than the log/linear graph. However, solar thermal doesn't need as high precision as some other processes.
There are also some Vishay Tools that might be useful.
I asked OHMIGO® what curve they used for their NTC 20 kΩ table and received a very swift and useful reply:
There are small variations between suppliers and control manufacturers - most of the NTC values were created from 3rd party suppliers like Produal... the differences in ohms and even so in 'C are small.
Ohmonwifi allows you to set your own table between 'C and ohm. There is an excel spreadsheet on ohmonwifi
A reply from Vishay:
your inquiry: "Are you aware of a device or method of converting the resistance output from a Pt1000 sensor to the equivalent resistance output of an NTC 20 kΩ sensor? Background. The existing solar thermal system in my house has a Pt1000 sensor in a solar thermal collection on the roof. I am considering replacing the solar controller with a Viessmann model which uses an NTC 20 kΩ sensor. The Pt1000 sensor on the roof is difficult to access so I am investigating if it will be possible to reuse it with something to convert its resistance to the NTC 20 kΩ equivalent. My background is in systems software so this is well outside my comfort zone! Vishay's answer: if those circuits are out of your comfort zone, I suggest you do not start to modify them and take contact with the suppliers of those systems and ask them for advice. Converting RTD sensors (Pt1000) signals to be read as an NTC is not advisable.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 66 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 5 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer pleased you found it!
By JamesPa , 6 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 7 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 10 hours ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 11 hours ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 24 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 24 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 1 day ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 2 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 2 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 4 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago