Buzzing noise from UFH manifold
Our heat pump was installed in November 21 and was connected to our existing UFH system. All has been working well, but in the last week or two I’ve noticed a loud buzzing noise coming from the UFH manifold when the kitchen is calling for heat.
it’s a strange noise, it reminds me of an old dot matrix printer printing. I’ve uploaded a clip so you can hear what I mean:
https://youtube.com/shorts/F5N6KFYcJw8?feature=share
does anyone have any ideas what is causing the noise, and what I should do to stop it? As far as I can tell, the heating is still working as normal
i’ve discovered that turning the flow rate valve on the kitchen supply does temporarily stop the noise, but when I put it back to the original position the noise starts again after a short while.
Wow! ASHPs need to deliver more flow than conventional fired boiler heating systems, as they operate a much lower delta T supply and return temperature. For many retrofits, including wet rad and UFH, that usually means the existing piping system ends up with higher velocities than before. Velocities above certain speeds will start to generate audible noise. It's not normally practical to increase the piping sizes for retrofits, so you may have to adjust some flow rates to stop noisy valves and pipework where the flow is higher.
That makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
Maybe a bit of wear and tear? Bleed the system of air, it's not something you want in the system. I have one TRV that quietly 'sings' when it modulates down, and it's in our bedroom!!
Posted by: @novemberromeoThat makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
You have partially answer the question yourself, in that it has been working fine for 14 months without making any noise, so I don't think that the actual pipework may be at fault.
Is the noise coming from the flow regulation valve or the valve associated with the solenoid valve?
I am not that familiar with UFH systems, but it sounds like it could be some debris inside the valve or some part of the valve internals is working loose.
Is it still under warranty?
- 22 Forums
- 2,038 Topics
- 44.4 K Posts
- 21 Online
- 3,252 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
It is taken from the website MEL Pump App
By Patch , 4 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Not the first time I've heard this... it sounds like th...
By Mars , 4 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 13 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree with @mars. My install was not dissimilar. ...
By JamesPa , 13 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 13 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 1 day ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 3 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 3 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 3 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago