Buzzing noise from UFH manifold
Our heat pump was installed in November 21 and was connected to our existing UFH system. All has been working well, but in the last week or two I’ve noticed a loud buzzing noise coming from the UFH manifold when the kitchen is calling for heat.
it’s a strange noise, it reminds me of an old dot matrix printer printing. I’ve uploaded a clip so you can hear what I mean:
https://youtube.com/shorts/F5N6KFYcJw8?feature=share
does anyone have any ideas what is causing the noise, and what I should do to stop it? As far as I can tell, the heating is still working as normal
i’ve discovered that turning the flow rate valve on the kitchen supply does temporarily stop the noise, but when I put it back to the original position the noise starts again after a short while.
Wow! ASHPs need to deliver more flow than conventional fired boiler heating systems, as they operate a much lower delta T supply and return temperature. For many retrofits, including wet rad and UFH, that usually means the existing piping system ends up with higher velocities than before. Velocities above certain speeds will start to generate audible noise. It's not normally practical to increase the piping sizes for retrofits, so you may have to adjust some flow rates to stop noisy valves and pipework where the flow is higher.
That makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
Maybe a bit of wear and tear? Bleed the system of air, it's not something you want in the system. I have one TRV that quietly 'sings' when it modulates down, and it's in our bedroom!!
Posted by: @novemberromeoThat makes sense, but I don't see why it would only start making a noise now - 14 months after installing the system. Up until now it's been running fine without any noise. I was wondering whether it could be the sound of air in the system, or something like that? Maybe that is a non-issue for these systems? We have no radiators, UFH throughout.
You have partially answer the question yourself, in that it has been working fine for 14 months without making any noise, so I don't think that the actual pipework may be at fault.
Is the noise coming from the flow regulation valve or the valve associated with the solenoid valve?
I am not that familiar with UFH systems, but it sounds like it could be some debris inside the valve or some part of the valve internals is working loose.
Is it still under warranty?
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 393 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 26 minutes ago
-
New Daikin 11kW Altherma 3M install - is it working as it should?
I had the system installed by Octopus in October last y...
By Synthbuilder , 37 minutes ago
-
RE: Rate the quality of your heat pump design and installation
🤣 what exactly did he dismiss and why?
By Mars , 56 minutes ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@jamespa Hi James - thanks so much! That sounds like ut...
By johnbroome , 1 hour ago
-
RE: Heat pump not reaching flow temperature
@jamespa system design was for 40 degrees FT at -2 degr...
By DaveC , 1 hour ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 2 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
@iotum, this is a really good question and you’re right...
By Mars , 2 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 3 hours ago
-
Please help with the settings ecodan
I have a 160 square meter house, first floor 6 radiator...
By nose1972 , 3 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 3 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 4 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 4 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@ashp-bobba Yeah I'll give it a go, will check filter...
By Anon67 , 4 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Perhaps the names at the end of the docume...
By Toodles , 4 hours ago
-
RE: Heatpunk Floor plan issues
@jamiejones85 A2A they will design on dynamic heat loss...
By ASHP-BOBBA , 5 hours ago
-
RE: Fan unit Making terrible noise HELP!!
can you post a video looking inside, at and through the...
By ASHP-BOBBA , 5 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 23 hours ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 23 hours ago