Communicating with Huawei Inverter
Does anyone by any chance have any experience of pulling data from a Huawei inverter? I know it can be done but Im struggling where to start. I use Home Assistant for monitoring most of my other systems and found this link to integrate with it once I have established comms
https://github.com/wlcrs/huawei_solar
Thanks in advance
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@transparent Not really, but im a reasonable programmer with experience of python so im sure I could pick it up. The articles Ive read seem to suggest that they are two approaches, via modbus or via wifi. I think the wifi is preferred as being more stable but i cant see a network associated with my inverter, however that might be because its using a Powerline adapter to communicate with the Huawei server so I imagine the SSID might have been disabled.
Ive also mused about interrogating my Samsung ASHP with modbus and even ran a twin cable when I installed it just in case, however I have full monitoring on it anyway so unless I could control it via modbus there probably isnt much point.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
OK. So Modbus is the language.
RS485 or WiFi or USB is the connection medium you use for communication.
RS485 is a serial protocol which runs over a pair of wires, A and B
On a workbench I can use loose wires, but when installing devices I use a twisted-pair cable.
It can run to more than a kilometer across an entire industrial plant.
There may also be an earth wire connection.
It isn't mandatory. Sometimes a device manufacturer suggests it gets used for safety reasons.
It depends what devices you're connecting together, and whether the RS485 connections are opto-isolated.
There is one Master device, which is usually a computer.
Slave devices can be a meter, relays, signal acquisition modules or entire inverters.
Each 'slave' device must have a unique ID from 0 to 254.
That is set either by using pins/jumpers/switches or by sending it a Modbus command.
You also define the communications speed (baud rate).
It is sometimes the case that a particular slave device may only use a narrow range of IDs, such as 0-31.
It can also be the case that a device doesn't allow you to change its preset baud rate.
However, RS485 is very tolerant of that.
You can actually set the baud rate at the Master end, talk to one device, then change the speed again and talk to the rest of the modules!
There is no defined connector for using Modbus.
Each manufacturer makes up their own mind and then tells you what the pins do in the manual.
Modbus is a standard international protocol...
... which many (Far East) manufacturers ignore!
Instead they use a similar sub-set of commands which they list in their manuals or online.
Sometimes the implementation is very detailed and specific,
whilst others are pretty crude approximations.
I have Modbus devices with only one Read command.
They simply deliver back to you the status of all their internal registers...
... which you then sort out in your own software.
How's that for starters?
Save energy... recycle electrons!
@transparent So far so good, so the twin wires I ran to my Samsung ASHP would be the RS485 comms medium.
So going from the advice below:
I would be better trying to access the modbus port on my inverter via wifi than directly via a direct RS485 connection?
This is where Im hitting a brick wall as I cant see a wifi connection to the inverter
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I really don't like the sound of linking to anything made by Huawei using a WiFi connection!
Even if it isn't frittering away time trying 'call back to base' in China, Huawei doesn't handle errors well.
I had a Huawei WiFi router which would clock up at least 10% of the WiFi data packets as aborted/corrupted.
You will achieve a much more reliable connection using Modbus over RS485!
That means you can stop banging your head against that brick wall, trying to find the IP address which may be hiding behind a NetMask.
If there are physical constraints on you running an actual wire, then please say.
But in my house I try to run all 'smart' devices using real cable.
It's much more resilient, and continues to operate if WiFi crashes.
Save energy... recycle electrons!
@transparent My inverter is outside so Im a bit worried about weather resistant connections but otherwise I could run a cable. This is the link to the post that was putting me off trying this. What do you think?
https://skyboo.net/2022/02/huawei-sun2000-why-using-a-usb-dongle-for-monitoring-is-not-a-good-idea/
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@transparent and here is the dongle outside which connects directly to my network via a poowerline adapter
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
That article doesn't say anything negative about using a direct hardwired RS485 connection to the inverter @bontwoody.
The author listed RS485 as an option, but then only tried two different approaches to implement data collection using WiFi.
It was the option where WiFi was connected to the inverter's USB port which was producing lots of data errors.
Given that you already have a live mains socket supplying power to the external dongle, I can't see how Modbus over RS485 would be any less 'weather resistant'!
What is the physical connector which is offered by the Huawei inverter?
The manual I've looked at online suggests that it's an 8-pin plug with rubber seals:
That looks pretty weather resistant to me!
The smaller is the twisted pair cable you elect to use, the smaller will be the hole you need to drill through the outer wall of the house.
I have a choice of RS485 cables which I've tried, from an expensive one that's less than 3mm diameter, up to a CAT5E ethernet cable with 4 twisted pairs.
I'd drill from the outside at a slight upwards angle. That allows any ingress of water to flow back out.
And I'd use a rigid plastic liner, through which I'd thread the cable.
Save energy... recycle electrons!
@transparent so that looks like the one second from the right? It already has two cables running through it which I have no idea what they do 🙂
I mistakenly thought the connection would be through the dongle (3rd from the right)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Looking at the Huawei connections diagram, that 8-pin connector appears to support three channels of RS485.
Without delving into the full manual, I don't know how 'separate' they are.
You'll need to check if each RS485 port has independent device IDs or whether they all use the same one.
Those two cables need tracing to see where they go to.
Your storage battery probably accounts for one of them.
Didn't your installer provide you with a schematic showing all the devices and their connections?
For safety reasons you should have one which identifies how to isolate each piece of equipment in case of a failure.
Save energy... recycle electrons!
@transparent I cant trace the cables as they go behind the supporting board and I would have to take off the whole thing. I will have a look at what was left by the installer or failing that ask him as he is good at responding to questions.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 52 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 24 seconds ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 minutes ago
-
RE: Setback savings - fact or fiction?
@sunandair I don't want to get embroiled in an argument...
By JamesPa , 12 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think most heat pumps have this mode but I cant see h...
By JamesPa , 34 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago