Plastic heat exchangers are usually used inside MVHR units. For an air:air heatexchanger, there's not that much heat transfer needed across that plastic barrier (as the air conductivity is poor) so thin plastic is ok. Along the heat exchanger material we want low thermal conductivity, from the hot to cold end - so for this reason, plastic is preferred over metal. Piccy of I think what's in our MVHR core.
It does sound as though your unit is in permanent bypass then, so the heat exchanger core isn't being used. Some flaps open up inside the MVHR box, bypassing the core entirely. I suggest that you get a copy of the installation and user manuals, perhaps they can help. Certainly our own Vent Axia Sentinel Kinetic can be easily told not to use summer bypass ever, irrespective of temperature sensors - it's a user adjustment not installer on ours.
What unit do you have ?
Posted by: @roblFor an air:air heatexchanger, there's not that much heat transfer needed across that plastic barrier (as the air conductivity is poor) so thin plastic is ok.
Along the heat exchanger material we want low thermal conductivity, from the hot to cold end
Can I ask what is the purpose of a heat exchanger?
@dandee A heat exchanger is used to transfer (in this instance anyway) warmth from the air that is about to be exhausted from the house (stale air) and that energy is used to heat the colder air being introduced to the house as fresh air from outside before it is distributed in the property. Basically a surface conducts the heat from the exhaust air and applies it to the incoming fresh air. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Posted by: @fazelCan I ask what is the purpose of a heat exchanger?
That question is a great leveller. 🙂
It shows the rest of us how we quickly descend into the technical depths!
In general terms a heat exchanger transfers heat between two fluids (liquids or gasses), whilst keeping those fluids separate.
The radiator of a car is a simple heat-exchanger.
Heat from the engine is passed into cooling water.
That water is pumped through the radiator, which has thin metal fins to transfer the heat into a stream of air.
The water and the air don't come into direct contact.
Within a household ventilation system (MVHR) there is a heat exchanger with a much larger surface area.
Hot, humid, sticky air is sucked out of shower/bath-rooms and kitchens.
As it passes through the heat exchanger, the heat is passed to fresh air being drawn in from outside the home.
The separation between the two streams of air means that the cooking smells from the kitchen, and the humid atmosphere from a shower cannot pass into the fresh air.
Save energy... recycle electrons!
Posted by: @fazelPosted by: @roblFor an air:air heatexchanger, there's not that much heat transfer needed across that plastic barrier (as the air conductivity is poor) so thin plastic is ok.
Along the heat exchanger material we want low thermal conductivity, from the hot to cold end
Can I ask what is the purpose of a heat exchanger?
Ohh boi, it was a rhetorical question, see the bold highlighted statements about the heat exchanger.
Placing the quoted phrases in a bold font was too subtle for me @dandee
I'd need at least one smilie to grab my attention. 🙂
As a member of a Community Energy group, I'm not daunted by receiving very basic questions from members of the public (or politicians!).
Save energy... recycle electrons!
The heat exchanger material conductivity is actually a compromise. Through the material, the thin way, we want high conductivity. Along the material there is a parasitic loss mechanism, for which we want low conductivity. Plastic is a better compromise of these two competing requirements than Aluminium is for an Air:Air heat exchanger - as the air boundary layer has an effective conductivity which is quite low there's little point using Aluminium or Copper as it won't improve performance noticeably, while the parasitic losses would shoot up. For a water:water heat exchanger plastic would be a poor choice, and a metal would generally be chosen.
Discussion on a forum is actually a compromise. Through this medium we actually want high transmissivity of information. Along the discussion there is a inherent loss-mechanism, through which we experience periods of low communication...
... which is why @robl is still posting coherent technical descriptions of the physics behind the design of heat exchangers, 25-hours after @dandee told us it was a "rhetorical question". 🤣
But hey... it's Friday!
and I've just enjoyed reading an erudite explanation of parasitic losses. 😉
Save energy... recycle electrons!
Posted by: @roblThe heat exchanger material conductivity is actually a compromise. Through the material, the thin way, we want high conductivity. Along the material there is a parasitic loss mechanism, for which we want low conductivity. Plastic is a better compromise of these two competing requirements than Aluminium is for an Air:Air heat exchanger - as the air boundary layer has an effective conductivity which is quite low there's little point using Aluminium or Copper as it won't improve performance noticeably, while the parasitic losses would shoot up. For a water:water heat exchanger plastic would be a poor choice, and a metal would generally be chosen.
Sorry I'm struggling to understand this. I'll try to play back what I've got from you: We want to conduct air from the outgoing (warm) side to the incoming (cold) side. For this, we need a thin material that has high conductivity in the perpendicular direction, to allow transfer across the interface. However, because the air passage is quite long, we don't want the material itself to be leeching heat away from the warm air and transporting it laterally along the length of the material: we want it transfering perpendicularly across the interface only. So plastic is better for this.
However, I still don't feel like I really "grok" the explanation. Nor can I explain why we want plastic for air:air but metal for water:water.
If you don't want to explain it again (which is totally understandable!) do you have any suggestions for where I can look this up?
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl You have already noted that for efficient counter-current heat transfer, you want to avoid heat transfer within the fluid streams. In each fluid, there is a laminar boundary layer which constitutes the major resistance to heat transfer to the interface. There is then the heat transfer perpendicular through the exchanger surface as well as that within the plane of the exchanger surface. The exchanger plate thickness is minimised (and length of exchanger maximised) to maximise flow across plate rather than along it. Flux through plate is proportional to delta-T across plate surface while flux within plate is proportional to temperature gradient along plate.
However, the boundary layer in air poses at least an order of magnitude more resistance than water and heat flux through an air boundary layer is going to be correspondingly lower. At this lower heat flux, the delta-T across the plate will be also correspondingly reduced but the gradient along plate will not (I still want to shift that amount of heat in that distance). The lateral flow of heat within the plate will therefore start to dominate, particularly if the plate has a high conductivity. I am therefore willing to use a lower conductivity plate material (which will result in a higher delta-T) to shift the balance back towards transfer across plate.
It was just yesterday that James posted
Posted by: @jamespipeHello! I'm not a tech-savvy person. I'd like the moderators and other members to dumb down the complex subjects to my level. 😀
Have we achieved that yet, James? 😉
Save energy... recycle electrons!
@ronin92 thanks a lot, that cleared it up for me!
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
- 25 Forums
- 1,438 Topics
- 30.2 K Posts
- 20 Online
- 1,224 Members
Join Us!
Latest Posts
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@david999 I asked a few installers to look at your ques...
By Mars , 8 hours ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 8 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@ivanopinion where are you up to and have you made any ...
By Mars , 8 hours ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 9 hours ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 9 hours ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 13 hours ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 16 hours ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 18 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
...except that's not how probabilities work. The chanc...
By Majordennisbloodnok , 18 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
Hi, Bit of an update. I bought a decibel meter and moni...
By Lokisam , 18 hours ago
-
RE: Incorrect Billing of Customers with a Smart Meter
I have provided them with a link to this discussion and...
By KoRWraith , 20 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
As I mentioned, there are going to be some follow-up ar...
By Majordennisbloodnok , 20 hours ago
-
RE: Tell us about your Solar (PV) setup
Now, I know that this may be a little simplistic and pe...
By Toodles , 1 day ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I find increasingly staggering that the MCS rules don't...
By JamesPa , 2 days ago
-
-
RE: Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Mevl, I won't be able to answer all your question...
By HCas , 2 days ago
-
I have been watching, with interest, the rebuild and re...
By iantelescope , 2 days ago
-
RE: Making best use of Agile with a battery and ASHP
On the subject of automating battery charging schedules...
By jamesw , 2 days ago
-
Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regardin...
By Transparent , 3 days ago
-
RE: Home energy storage & battery register
Hanchu ESS - Home-ESS-LV9.4K (9.4kWh)
By IRMartini , 4 days ago
Heat Pump Humour
Latest Topics
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 3 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 4 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 6 days ago
-
Home energy storage & battery register
By Mars 6 days ago
-
Meter Readings - What are theses meters telling me?
By Potatoman 1 week ago
-
Have Octopus Energy discovered a way to Narnia?
By Davesoa 1 week ago
-
Making best use of Agile with a battery and ASHP
By jamesw 1 week ago
Members Online
No online members at the moment