Posted by: @editor@derek-m, you’ve read through a lot manuals and looked at weather compensation graphs from different manufacturers. Are the heat curves usually quite similar?
Hi Mars,
The required heat curve is mainly dependent upon the heat loss of the property, and the type and size of the heat emitters. It is basically trying to match the heat energy supply, to the heat energy demand or heat loss, at varying outdoor air temperatures, and thereby maintaining a reasonably constant indoor temperature.
I would suspect that most properties in the UK would fall in the 0.8 to 1.2 range, in that for each 1C change in outdoor air temperature, the WFT needs to be increased or decreased by somewhere in the region of 0.8C to 1.2C for your particular home. A good starting point would probably be to set the curve to a WFT of 25C at 20C ambient and 50C WFT at -5C ambient. That gives a slope of 1, 1C change in WFT for each 1C change in outdoor temperature.
Auto adaptation or modulation control has now been incorporated in some systems, to add to, or subtract from, the weather compensation curve, if the indoor temperature deviates from the desired setpoint. But these only work correctly if the system is correctly installed, configured and optimised.
I have not researched Homely in detail, but I do believe that it also utilises weather forecasts, and Time Of Use (TOU) tariffs, to help minimise costs, but not necessarily use, since it could be encouraging the heat pump to run at times when it is not as efficient.
Whilst I am a firm believer in utilising modern technology to help minimise our energy consumption, I am not yet convinced that adding additional complexity to replace a capability that is already installed within the system is the way forward. A further concern would be what happens to your heating system if you lose your internet connection?
@derek-m, that’s a terrific explanation. Thank you. We’ve put ours up to 1.8, and that’s been very comfortable throughout the property. Not cold. Not hot. I’ll drop it to 1.2 tomorrow and see the difference.
At 1.8, our flow temperature has been between 32-37C.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@derek-m, that’s a terrific explanation. Thank you. We’ve put ours up to 1.8, and that’s been very comfortable throughout the property. Not cold. Not hot. I’ll drop it to 1.2 tomorrow and see the difference.
At 1.8, our flow temperature has been between 32-37C.
Hi Mars, what controller is this, where in the house is it, and what other controls are there on the heat pump?
Professional installer
@alec-morrow, this is precisely where our weather compensation issues stem from. The installers never activated weather compensation for us when the pump was put in, so we ran our ASHP for years at set point temperatures (40 or 45C depending on how cold it was). The more we learned, we realised weather compensation was essential from an efficiency perspective so we contacted the installers and asked them why they hadn't activated the weather compensation – part of the issue was the lazy install.
They slapped the main controller for the heat pump next to the hot water cylinder in our "heating cupboard". At any given point in time it's over 27C in that cupboard when the heating is on. So not ideal.
In addition to the main controller, we have a smart Salus thermostat to switch on the radiator circuit and wired in Heatmiser thermostats to switch on the UFH circuit. Both are usually set to 23C, as we know that with out set flow temperature of 40 or 45C, rooms will typically get to around 21C which is what we like. This also prevents the heat pump from cycling as we never come to temperature for rads or UFH in winter.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
It sounds like you have found a sweet spot
the numbers on a heat curve are broadly* the same across all manufacturers
think this:
Start point would be 20c outside 20c inside flow temp 20c
for every drop of one degree outside the flow temp rises 1c at a curve of 1.00
at a curve of 0.5, 0.5c
at a curve of 1.8c flow temp rises at 1.8c
Etc
* anti cycling measures mean you may not always be following the curve, and some curves are gently bent to over come thermal inertia in the system and house
no hard and fast rule
Professional installer
@alec-morrow, it's a sweet-ish point, but probably still not as efficient as it should be. But that's something we'll have to live with.
I've dropped it to 1.2 today, just to see the difference over 24 hours.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
We decided to let our colder rooms be colder (they need insulating) rather than battle to heat them.
Our curve is now 1.0 so our flow has been about 25-29 last week. The main rooms are 19c which is perfect for us.
previously we probably ran the flow +10c hitter to just get two rooms up to temp. So they are closed off this winter then deep retrofit planned for spring!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Hi Mars,
Because your system has a range of fixed weather compensation curves it is not possible to fine tune the system to match your home's heat loss characteristics, by adjusting the slope with the end parameters. It may therefore be necessary to select different curves for different periods throughout the year.
I would suggest that you initially set your system for weather compensation and select curve 1. Increase any thermostats 1C or 2C above the desired indoor temperature, and monitor the operation of your system over several days, noting indoor temperature variations. If you find that you are not achieving the desired indoor temperature then select the next higher curve. Repeat the above until you achieve reasonably stable control.
I would be interested to see the results.
Posted by: @derek-mA further concern would be what happens to your heating system if you lose your internet connection?
+1 to this. It is very often ignored by salespeople. A related question is: what happens to the heating system if the additional controller fails?
As you know, I'm happy having an external controller tweaking the Mitsubishi one's curve based on other factors (including weather and electricity price), but if it fails for any reason, the heat pump's own controller is always in a state which wouldn't get uncomfortable quickly if left to run. The house could get a bit nippy the morning after a failure, but there's never a risk of ice on the windows or people roasting hot in their beds! I'm a bit concerned that these on/off controllers might leave the heating off if it fails.
if internet connections fail the system runs to the transmitted parameters.. internet failures are rarely excessively long.
And on the interface/room controller adjustments can be made…
Im always amazed by how people in the U.k. would rather find fault with what’s on offer rather than try and understand how things actually work.
Professional installer
@derek-m, that's the conclusion I've come to. It looks like 1.5 works for this time of year (8-15C ambient temperature). When we start to drop below 8C, that's when we'll switch to set points.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@grahamh has just posted this article on weather compensation and the Lizzie curve. It's very interesting, and we're finding that the 36-37C mark at 10-15C ambient is comfortable for us.
https://renewableheatinghub.co.uk/weather-compensation-the-lizzie-curve
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 14 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 9 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 12 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 17 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor @sandy I tried contacting them via Whatsapp b...
By brad , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 5 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
Members Online
No online members at the moment