What is the best strategy for operating a very oversized heat pump?
As the title really. There are at least three live threads currently where its obvious that a part of the problem is a heat pump oversized by a factor of 2 or more, and I would guess that a fairly significant proportion of the threads have this somewhere at their centre. As we get into the shoulder season, the 'problem' will rear its head more frequently.
So whats the best strategy and why? Im assuming that the heat pump is operated on weather compensation obviously
1. Operate on WC and leave it open loop (no external controls). Trust the heat pump controller do its job
2. Operate on WC and batch heat by timed operation, accepting the variation in IAT. Adjust the number of on/off cycles according to the thermal time constant of the house
3. Operate on WC and modulate on and off using a thermostat
4. Something else
All are in fact cycling, so all will suffer the thermodynamic/COP penalty of cycling, perhaps to a greater or lesser extent depending on the resulting flow temperatures.
What's the best strategy and why? Any answers?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Something else... that works for some people...
LG has "Quiet/silent mode" that is normally intended where noise is an issue (say at night or proximity to neighbours etc). When using that mode the compressors operate at lower rate than normally called by WC.
Some people use very effectively for oversized heat pumps to reduce cycling etc. It means operating at less than optimal efficiency for size of pump but if oversized that may suit.
I guess many other heat pumps have a similar option. Maybe called something else.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Currently viewing this topic 1 user ( Mars ) and 1 guest.
Recently viewed by users: Majordennisbloodnok 21 minutes ago, Tim441 47 minutes ago, Gary 38 minutes ago.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 78 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 55 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 1 hour ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago