Vaillant Noise Reduction effect
Curious if anyone has experimented incorrectly with the noise reduction feature, in terms of kw consumed
Does it use less kw consumption or does it balance itself out as the same?
Weird I know but am trying to keep my consumption numbers down whilst also having a comfortable home temp.
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
Posted by: @jeegneshCurious if anyone has experimented incorrectly with the noise reduction feature, in terms of kw consumed
Does it use less kw consumption or does it balance itself out as the same?
Weird I know but am trying to keep my consumption numbers down whilst also having a comfortable home temp.
I think the fundamentals are this:
NR clamps performance at a particular level. So most of the time it will make no difference. When its cold enough that it does make a difference then yes it will reduce the energy consumption, but at the expense of the house cooling. If NR is timed then the heat pump will have to work harder when the NR restrictions are removed, which may well cost more (its like a setback). The easiest way to reduce energy consumption at the expense of the house cooling is to turn down the WC curve (and thus room temperature) a bit.
That said there may be some 'second order' effects, particularly with DHW. Depending on the algorithms used which vary from manufacturer to manufacturer, NR might result in a less aggressive warm up cycle for DHW, which may well cost less at the expense of the space heating being off for longer and the reheat time being longer. Some heat pumps have selectable DHW modes, which essentially moderate the aggression of the rehear, and NR may well achieve something similar to the 'eco' mode or whatever the manufacturer chooses to call it.
Best way to achieve lowest consumption (in most cases) is to operate with no external controls, at lowest WC consistent with keeping the house warm, and no buffer tank, LLH or PHE separating heat pump and emitters. From that starting point tweaks may save a few percent, but rarely a lot unless the situation is one of the 'exceptions' (there always are exceptions!). If you have a ToU tarrif lowest cost may be at a different operating point to this of course.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
If I did a HW boost out of hours would it still run at eco, thats the only issue I see as it takes twice as long to heat up the tank.
I don't know TBH but would guess so.
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 91 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: BUS Grant, removal of all other heat sources
Thank all for the reply. Our gas fireplace it’s fairly ...
By Rikiarn , 5 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
Glad you're finding the information useful; I try to ke...
By Majordennisbloodnok , 56 minutes ago
-
@bart Stinks of corruption.
By Brendon Uys , 1 hour ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 13 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 17 hours ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 2 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 2 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 3 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 4 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 4 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 5 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 5 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 5 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 5 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 6 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 6 days ago