Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
Posted by: @samiebon1Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
You had it installed only last week? I would suggest that you need to do nothing and get the installer back pronto!
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@samiebon1 Isn’t it a sad situation when we feel we must be ‘armed’ with an argument and / or a prepared report to hand over to the installer on their return when they have failed to carry out a good install? Perhaps the good installer would not have carried out a botched job in the first place but, wouldn’t it refreshing if the installer returned and said “Oh I am sorry we made such a mess of this job, we will put it right immediately and I am so sorry to have caused you this inconvenience in the first place!”? —— Yes, I live in cloud cuckoo land I know! 😉 Regrets, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @samiebon1Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
Something is wrong with the plumbing for sure. Have the downstairs rads been bled? Are they on a separate primary or do they share a primary with the upstairs?
Unless your house is very tall 1.2 bar should suffice
Re the DHW what tank do you have and how much hot water do you use. Also what do you mean by 'up to temperature' 5kW is actually quite small if you use a lot of DHW. So if, for example, you are trying to heat 300l from cold (10) to 50, its going to take 3 hours
As @toodles says, at this stage its definitely something your installer should fix but I'm like you and prefer to be a step ahead!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa As far as I can tell they have been bled (water comes out when I bleed them). Theyre on the same primary as upstairs - 22mm copper running along upstairs, then down. Could anything be done with the 'remaining feed head' setting or is that a non starter?
Its a 150L 'UK Cylinders' heat pump tank. Its got a 3 hour window to heat in from ~36 to 48 deg so shouldn't take that long.
@samiebon1 Sounds as though the output from the heatpump is being throttled back in some way. If the system was sized appropriately, then all the radiators should be supplied with sufficient heat to bring them to temperature readily. There may be a blockage / restriction in the flow before the pipework descends to the ground floor radiators. Possibly an air lock; have you information on the consumption and how long the heat pump is running and idling? It is worth checking up on these points. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @samiebon1As far as I can tell they have been bled (water comes out when I bleed them). Theyre on the same primary as upstairs - 22mm copper running along upstairs, then down. Could anything be done with the 'remaining feed head' setting or is that a non starter?
OK so downstairs is 'after' upstairs. You may have to throttle down the LSVs upstairs, increase the pump head if thats an option, and open up (if you can) the LSVs downstairs. As @toodles says there could be an air lock, Vaillant has a 'purge' function in the installer menu which my installer said was supposed to deal with this (presumably by whacking the water pump up to max).
Posted by: @samiebon1Its a 150L 'UK Cylinders' heat pump tank. Its got a 3 hour window to heat in from ~36 to 48 deg so shouldn't take that long.
No it shouldn't, nowhere near!
Here is my 200l tank reheating today from/to about the same temperature. 22mm diameter feeds teeing off the 28mm primaries from the heat pump. I have a 7kW Vaillant. Something definitely wrong with yours, can you tell what temp the pipes are to and at the DHW tank and what diameter are they? I suppose its not possible that the installer has fitted a normal 3 way valve instead of a diverter valve (you would know as your heating would be on simultaneously with your DHW)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaI suppose its not possible that the installer has fitted a normal 3 way valve instead of a diverter valve (you would know as your heating would be on simultaneously with your DHW).
That happened with my installation. Whoever had been sent to the plumbing suppliers to buy various parts got the wrong type of valve. Once the system was running I noticed that one of the upstairs radiators was getting warm when the DHW was being heated. That was convection flow as the circulating pump wasn't running.
I think the pipe work and 3 way valve is ok from what I can see/read up. I had wondered if it's the settings - I have weather adaptation on so at the moment it's ~40deg flow, and my DHW offset is 15k (was 10k). Would this 55deg flow around the cylinder be enough to get up to target 48deg water temp?
The installer has arranged to come Monday so at least it's pencilled in!
Posted by: @samiebon1I think the pipe work and 3 way valve is ok from what I can see/read up. I had wondered if it's the settings - I have weather adaptation on so at the moment it's ~40deg flow, and my DHW offset is 15k (was 10k). Would this 55deg flow around the cylinder be enough to get up to target 48deg water temp?
The installer has arranged to come Monday so at least it's pencilled in!
DHW flow temp is completely separate to space heating flow temp. The offset is added to the target DHW temp to get the FT for DHW. 15K should be ample in principle although the cylinder supplied has a relatively small area coil (1.6 sq m) compared to 3 sq m often recommended. That said so does the Vaillant 150l cylinder! Feels to me like something is wrong, suggest you check the pipe temps near the DHW cylinder if you can!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Vaillant AroTherm Plus 7kW
8 months ago
-
Vaillant arotherm plus heat pump frost protection
1 year ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 474 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 3 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 1 hour ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 1 hour ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 7 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 14 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 14 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 17 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 18 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 20 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago