Vaillant arotherm plus heat pump frost protection
At those times on the 6/7th Frost protection kicked in. The two flow temperatures are the starting and ending for the frost protection period. The duration was around 15minutes. Yes showing frost protection on the controller.
I was expecting it to only kick in when the outside temperature reached 4oC and then elevate the flow from 6 to 12oC.
258-DHW; apologies 258 is the heat pump cycle number and DHW for heating the hot water.
When i moved the outdoor sensor indoors , the number of frost protection cycles reduced. The heating came on as per the programme.
Im sorry but I really don't understand from what you have said how you are running your heat pump (for example how can WC work when the outdoor sensor is indoors, and that being the case how did the heating 'come on' as per the programme'? ). Its also going to be difficult to work out things based on what happened over 2 months ago and with the outdoor sensor indoors.
Can I suggest you
1. relocate your outdoor sensor outdoors
2. take screenshots of the settings governing the heating schedule, room influence mode and weather compensation
3. when the problem next occurs record:
what the heat pump should have been doing according to the program you had set up and why you think this
the indoor and outdoor and flow temperatures on the sensocomfort
the time of day and date.
With a fresh example and more data on how you are running your heat pump maybe it will make sense, currently I am sorry but it doesn't, at least not to me.
I apologise I cant be more helpful at present however its difficult to tell what is going on with the various changes to configuration and the moving of the outdoor sensor, particularly as the latter is so absolutely fundamental to the control of the unit all of the time not just for frost protection.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Much appreciated for your help and thoughts. I will keep a diary. Thank you again
It occurs to me, have you got a timed heating schedule and if so what is it. Can you tell me why the indoor temperature was so low in the records in the diary. Something isn't making sense about the whole setup.
Just to emphasize, the outdoor sensor isn't primarily for frost protection, it's part of the basic weather compensation control loop of the system. It really has to be outside.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Vaillant AroTherm Plus 7kW
3 months ago
-
Vaillant - Downstairs radiators not getting warm
8 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
10 months ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
10 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
11 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 70 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Yes, one outside in a sheltered place (mine was in a co...
By cathodeRay , 18 minutes ago
-
Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
We’re pleased to announce that Havenwise are now joinin...
By Mars , 27 minutes ago
-
RE: COP is not the only measure of efficiency
I am a little sceptical of this, not least because, in ...
By jamespetts , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@ashp-bobba Well done for stepping in where most would ...
By JamesPa , 3 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have automated this decision. I have a heat pump with...
By jamespetts , 11 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 13 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 13 hours ago
-
RE: Buffers, hot water and cooling
I agree it seems like a lot of work particularly as its...
By JamesPa , 14 hours ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 17 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 19 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 22 hours ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 22 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 23 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 2 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 2 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 2 days ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 3 days ago