Slow to heat room
Our Vaillant ASHP + UFH system takes forever to heat the house. Currently we run it from 0700 to 2200, with the thermostat set to 20 deg. Over the last few days it takes 8-9 hours to go from 17 deg to the required 20 deg. The floor heats up to about 23-24 deg, and the ASHP spends most of its time off. Flow temp runs about 25-30 most of the time. At least it’s not using too much electricity, but my house is cold.
Any ideas for how to improve this? I guess I could run the system 24/7, or raise the flow temp (how?), or maybe something else?
Run it all day, lower the flow temp. Use less power and you'll get a constant heat all the time. You're letting it cool down and then it needs to get up to temp again.
Thanks for the quick reply. I'm going to try running it 24/7 for a few days and then compare the temperature and energy use. I guess I'm wondering why the ASHP is barely ticking over, with minimal flow temp, when the house is cold?
@squonk do you have a heat curve on your system? Ideally you want it just ticking over, but maybe your heat curve needs tweaking for this time of year? I assume it's fine in the winter?
@batalto That’s something I’ve been wondering about. The Vaillant setup instructions says Heat Curve: Site Specific, it defaults to 1.00 so I haven’t changed it. There is also a setting for Adaptive Heat Curve, Vaillant says this should be Off, so that’s what I’ve done.
@squonk yeah you are going to want to change those, 100% you'll be on the wrong setting if it's on the defaults. I don't have your unit, but some people on here do. Try checking the role call to see who might be able to advise
Posted by: @squonkOur Vaillant ASHP + UFH system takes forever to heat the house. Currently we run it from 0700 to 2200, with the thermostat set to 20 deg. Over the last few days it takes 8-9 hours to go from 17 deg to the required 20 deg. The floor heats up to about 23-24 deg, and the ASHP spends most of its time off. Flow temp runs about 25-30 most of the time. At least it’s not using too much electricity, but my house is cold.
Any ideas for how to improve this? I guess I could run the system 24/7, or raise the flow temp (how?), or maybe something else?
If you're using a third party thermostat with the ASHP's weather compensation, then the ASHP will only run when the room temp is below the thermostat target and the flow temp is below the weather compensation flow temp target corresponding to the outside temp. So when the WC flow temp target is reached the ASHP will stop heating even if the thermostat is still calling for heat. It will only start again when the WC flow temp drops below its target.
If this is what's happening then as a trial I would increase the weather compensation curve so that the target room is reached. The thermostat will then stop calling for heat and the ASHP will switch off. With a bit of tweaking you can come up with a weather comp curve that keeps your house at the right temperature whatever it is outside.
In winter I have my thermostats set to 30 deg and I let the weather compensation control the house temperature.
Posted by: @kev-m
If you're using a third party thermostat with the ASHP's weather compensation, then the ASHP will only run when the room temp is below the thermostat target and the flow temp is below the weather compensation flow temp target corresponding to the outside temp. So when the WC flow temp target is reached the ASHP will stop heating even if the thermostat is still calling for heat. It will only start again when the WC flow temp drops below its target.
If this is what's happening then as a trial I would increase the weather compensation curve so that the target room is reached. The thermostat will then stop calling for heat and the ASHP will switch off. With a bit of tweaking you can come up with a weather comp curve that keeps your house at the right temperature whatever it is outside.
In winter I have my thermostats set to 30 deg and I let the weather compensation control the house temperature.
The humble room stat, yet again showing how inappropriate it is for a modern heating system that uses compensating controls. It would be better for most people if the room stat was just replaced with an on/off switch 🤣
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@squonk, ASHPs are designed to run 24/7 to get the most of out of the system in terms of efficiencies and comfort. To give you an idea, it’ll take our ASHP at least 24 hours to get our entire house to 21C when we turn it on for the first time in winter. It then just needs to run, doing its thing.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @squonk@batalto That’s something I’ve been wondering about. The Vaillant setup instructions says Heat Curve: Site Specific, it defaults to 1.00 so I haven’t changed it. There is also a setting for Adaptive Heat Curve, Vaillant says this should be Off, so that’s what I’ve done.
Installers don’t like to enable weather compensation because it’s a trial and error system which leads to multiple call outs, so they just set the system to one flow temperature.
My advice is for you to experiment with the heat curves to get it running optimally for your house and your personal comfort levels.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@witchcraft, have you conquered the weather compensation on your unit?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor There doesn’t seem to be any shaping to the curve, it mainly seems to control the relationship between inside and outside temperatures as far as I can see. If that is correct then presumably it’s a case of reducing it a step at a time and seeing what happens? Ie the lower the curve the more efficient the system is, so the ideal is to take it down to the point where the house doesn’t stay warm and then crank it up a little. Doesn’t seem very scientific, but maybe I’ve been overthinking the problem.
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 275 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@kevh It's something I'm trialling at the moment - I've...
By AndrewJ , 57 minutes ago
-
RE: Electricity price predictions
Ben Watts posted on LinkedIn that he had updated this w...
By Judith , 5 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Small update, Emailed and Spoke to Midea UK and they ...
By Burtis , 5 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash Octopus does charge for the admin. The process al...
By Batpred , 5 hours ago
-
RE: External pipework insulation
@transparent HI all The products you mention are ver...
By David Smith , 5 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Issues still under investigation by Solis... Fogstar ...
By Batpred , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I agree, the consumer is not being properly represented...
By Batpred , 5 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@weoleyric, apologies for the delay in response. Give...
By Majordennisbloodnok , 7 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 22 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 23 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 1 day ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 2 days ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 2 days ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 2 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago