@drei in your original post, you said:

Posted by: @drei

I'm not guessing, I’ve had an independent assessment from a Heat Geek Elite engineer at the cost of £800, thermal imaging, flow readings, everything documented.

Did the Heat Geek Elite engineer give you a design within the £800 fee, or did he just tell you everything that was wrong and how badly wrong it was? 

My impression is that there are 2-3 key problems:

1.  The buffer tank is reducing flow temperature to the radiators, so that they never get above 40C.

2.  The radiators are inadequately sized, so even at 50C they would not be big enough.

3.  The water flow rate might be insufficient to push the water around the radiators fast enough.

Is that correct?  

Quote 1 seems to be addressing only part of the problem.  If the buffer is plumbed incorrectly (in-flow from heat pump at the top, outflow to radiators at the bottom, return from radiators at the top and return to heat pump at the bottom) then correcting that would certainly help.  But removing the buffer entirely might correct it a lot more.

Quote 2 seems to be much closer to what you need.  However, I don't understand why you wouldn't upgrade all the radiators that need upgrading.  The approach I took was to install big new radiators in the rooms that needed the most heating power.  Then, I cascaded the radiators that I had freed up into rooms needing less heating power.  Cascading existing radiators down the chain would save you buying so many new radiators, but obviously, they would have to fit in the available space. 

 


Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation


   