Secondary circulation pump settings
I have a secondary circulation pump on the other side of my Low Loss Header from my heat pump. I realise there is a lot to discuss about the problems around an LLH but for now I am interested in the setting of the pumps and therefore how they might be interacting.
The pump in question is a Grundfos UPM3 AUTO 25-70 130 zzz, I've included a picture below which shows the setting of the pump. It is not speed controlled by the heat pump and appears to be on all the time except when the heat pump is doing DHW.
Given the pump inside the heat pump is variable speed I can't see how having a fixed speed pump on a high setting will do anything other than cause a lot of mixing in the LLH and so might help partially explain the low COP values I get (currently 1.8 - 2.4).
The heat pump is a 16kW Midea monobloc. From the manuals for similar pumps there seem to be setting options for Proportional Pressure, Constant Pressure, and Constant Curve but I don't know which of these would work best in my setup (diagram below).
Any thoughts greatly appreciated.
16kW Midea Monobloc R32 Heat Pump (Heating & DHW)
4kW Solar PV (No battery storage yet)
CPC 12 INOX Solar Thermal (DHW)
Posted by: @alan-mGiven the pump inside the heat pump is variable speed I can't see how having a fixed speed pump on a high setting will do anything other than cause a lot of mixing in the LLH and so might help partially explain the low COP values I get (currently 1.8 - 2.4).
Your concern about mixing flow and return temperatures within the LLH is an issue for efficiency. And this is very likely to be more extreme if flow rates are in any way different either side of the low loss header. The mixing of the hotter LWT with the RWT means that the HP is having to work harder to produce the correct deltaT only for it to be mixed and cooled again before the water gets to the emitters.
if you have some means of measuring pipe temps entering and leaving the LLH you will know straight away if you have a significant heat mixing/loss problem.
However if you have a heat pump that has an internal circulation pump built in then this may be more complicated to do anything about it especially if it is a variable speed pump and you’re secondary pump is manually controlled and especially if operating at a fixed full speed setting.
Our situation is different to yours in that our Ecodan has an external Primary circulation pump which is now set to a constant pressure on the slowest speed which gives us a flow rate of 13 litres per minute. (Well within manufacturers minimum required flow rate) the hp then modulates to produce the deltaT of about 5 to 7c. Again this might be different to how your Midea HP regulates it’s heat output.
We have then adjusted our secondary pump to the same pump speed and checked flow rates again to try and match the flows through both circuits. This has meant that the temperature loss through the header has been measured to be only 1c. Not ideal but it’s much better than it was.
Im not sure how you might do something similar if you have a variable pump speed from an internal pump.... unless you can get a second output cable from controller to try to match the pump speeds but then you would need a compatible pump.
The other option, as I think you were hinting at, would be to explore the possibility of removing the low loss header but only if your system can operate as a single circuit.
i hope this helps clarify what can be done and perhaps someone who knows Midia might have an easier fix solution.
Our COP figures were significantly improved from 1.59 to a promising 3.3 to 3.7 depending on outside ambients. We still have the LLH fitted at the moment.
- 25 Forums
- 1,444 Topics
- 30.2 K Posts
- 35 Online
- 1,227 Members
Join Us!
Latest Posts
-
RE: Effect of buffer tank or volumiser on heat pump system
Many thanks Derek. That is what I will suggest and hope...
By DavidAlgarve , 5 mins ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
This photo shows a bi-directional RCBO by Proteus at Re...
By Transparent , 38 mins ago
-
@matenateson Our PV installation took place in July/Aug...
By Toodles , 49 mins ago
-
RE: Placement of Samsung R290 ASHP
Propane (R290) sinks, under a window is allowed so far ...
By JamesPa , 1 hour ago
-
Solar panels – is there anything I can do with them?
@transparent that’s true navitron no longer exists and ...
By David999 , 4 hours ago
-
Settings for NIBE F2040 & SMO 20
I have a NIBE F2040 with an SMO 20 controller. It was ...
By sc2987 , 4 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 21 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 22 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 24 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 24 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 2 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 2 days ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 3 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 4 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 4 days ago
Heat Pump Humour
Latest Topics
-
Placement of Samsung R290 ASHP
By Jancold 2 hours ago
-
Settings for NIBE F2040 & SMO 20
By sc2987 4 hours ago
-
Solar panels – is there anything I can do with them?
By David999 20 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 7 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 7 days ago