Samsung HTQuiet configuration for the 6th generation controller
hi all,
I have been playing with the configurations over the past weeks. Using this material:
2. https://midsummerwholesale.co.uk/pdfs/samsung-sunamp-quick-start-rev-2.pdf
The installer indicates that he set the Samsung LCD controller as the thermostat. I managed to organize all the water law stuff, etc. It is getting warm in the house now. Not many problems there. The cold days I had a COP of 3 on average, now approaching 4. So that seems to be more or less "in control".
Without an additional external thermostat, #2091 and #2092 should be zero = not used (according to the manual), and #2093 should be put to any of these values (default = 4):
0 Not use
1 Use signal only on/off
2 Use (signal on/off) or WL interlink off (water pump 1)
3 Use (signal on/off) or WL interlink off (water pump 2)
4 Use (signal on/off) or WL interlink off (water pump 3)
These values seem to behave similarly to the ones described in the manual on page 28. The standard temperature is set to "indoor". The Samsung LCD controller gives the right indoor temperature in the room (double-checked with some other devices in the same room).
The issue: the controller triggers based on the ambient temperature: if the room is getting below 20C, it starts the heat pump to heat the radiators following the water law (WC). However, it keeps on doing this and does not seem to "stop" the heat pump once it reaches the required temperature... The above values try to reduce hysteresis, but, also, option 1 does not trigger an "off". I first thought it had something to do with the difference that needs to be larger than a threshold value (Indoor Zone option -> Temperature unit -> 0.1/0.5/1, but that seems incorrect, more for setting the temperature).
The inside temperature sometimes goes up to 21C. It does, however, stop sometimes for whatever reason, I can not get my hands on it.
My reasoning now is that the "Use (signal on/off) or WL interlink off" does not trigger the signal off. But it stops because of the "WL interlink off"... I have no idea what the WL interlink is. My best guess now is that it has to do with #4052, the target deltaT, as usually, in the course of the afternoon, with warmer temperatures, the heat pump is triggered to stop. My eye also fell to #4061 for "zone control", no idea what this is...
Does anybody know what the WL interlink logic is doing and how I control this? Anybody any clue why the "signal on/off" only triggers on and no 'off"?
thanks for any help or pointer...
tom
-
LG Therma, Controller settings help needed
11 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
2 years ago
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 110 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
Thanks for all the help/comments. I completely agree w...
By JamesPa , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree and that’s why I don’t believe a lot o...
By SimonF , 6 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I doubt that matters, ToU tariffs are for the benefit o...
By JamesPa , 7 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 10 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 12 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 14 hours ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 14 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Before I answer your specific questions just one more t...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 1 day ago
-
RE: Running from backup generaor in powercut?
Definitely and professionals sometimes miss it. I had...
By Batpred , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 1 day ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 1 day ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 1 day ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 1 day ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 1 day ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 2 days ago