Samsung HTQuiet configuration for the 6th generation controller
hi all,
I have been playing with the configurations over the past weeks. Using this material:
2. https://midsummerwholesale.co.uk/pdfs/samsung-sunamp-quick-start-rev-2.pdf
The installer indicates that he set the Samsung LCD controller as the thermostat. I managed to organize all the water law stuff, etc. It is getting warm in the house now. Not many problems there. The cold days I had a COP of 3 on average, now approaching 4. So that seems to be more or less "in control".
Without an additional external thermostat, #2091 and #2092 should be zero = not used (according to the manual), and #2093 should be put to any of these values (default = 4):
0 Not use
1 Use signal only on/off
2 Use (signal on/off) or WL interlink off (water pump 1)
3 Use (signal on/off) or WL interlink off (water pump 2)
4 Use (signal on/off) or WL interlink off (water pump 3)
These values seem to behave similarly to the ones described in the manual on page 28. The standard temperature is set to "indoor". The Samsung LCD controller gives the right indoor temperature in the room (double-checked with some other devices in the same room).
The issue: the controller triggers based on the ambient temperature: if the room is getting below 20C, it starts the heat pump to heat the radiators following the water law (WC). However, it keeps on doing this and does not seem to "stop" the heat pump once it reaches the required temperature... The above values try to reduce hysteresis, but, also, option 1 does not trigger an "off". I first thought it had something to do with the difference that needs to be larger than a threshold value (Indoor Zone option -> Temperature unit -> 0.1/0.5/1, but that seems incorrect, more for setting the temperature).
The inside temperature sometimes goes up to 21C. It does, however, stop sometimes for whatever reason, I can not get my hands on it.
My reasoning now is that the "Use (signal on/off) or WL interlink off" does not trigger the signal off. But it stops because of the "WL interlink off"... I have no idea what the WL interlink is. My best guess now is that it has to do with #4052, the target deltaT, as usually, in the course of the afternoon, with warmer temperatures, the heat pump is triggered to stop. My eye also fell to #4061 for "zone control", no idea what this is...
Does anybody know what the WL interlink logic is doing and how I control this? Anybody any clue why the "signal on/off" only triggers on and no 'off"?
thanks for any help or pointer...
tom
- 24 Forums
- 1,420 Topics
- 29.8 K Posts
- 14 Online
- 1,205 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
I agree, new stuff can easily be intimidating, though f...
By cathodeRay , 4 hours ago
-
RE: Ecodan software update. Real or scam?
@editor thanks for that Mars. I’ve never had email cont...
By Morgan , 6 hours ago
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
@transparent You are a bright spark aren’t you?!
By Toodles , 10 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
That could be the case, depending on where the triple r...
By AllyFish , 10 hours ago
-
RE: Say hello and introduce yourself
@irmartini Oh! That’s a great shame.😳 Toodles.
By Toodles , 11 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@david999 On the subject of isolation after the battery...
By HughF , 17 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@robl I've added the screens. Li-Bms screen is accur...
By GGW , 1 day ago
-
RE: SCOP and seasonal variations
I’ve had a long chat with Aaron from Homely Technical S...
By Toodles , 1 day ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
Many thanks to everyone who has helped with advice and ...
By IRMartini , 2 days ago
-
RE: What is Wrong with our Heat Pump Installation?
With BESS the ASHP is best. Charge battery for free fro...
By AllyFish , 2 days ago
-
@hubb84 Try looking at powerflushassociation.com. They ...
By Toodles , 2 days ago
-
Central heating inhibitor with ASHPs
Have you seen the Heat Geek article and video?
By ChickenBig , 2 days ago
-
RE: Advice on potential HW Cylinder size
@jwilliams89 I would imagine that the MCS would insist ...
By bontwoody , 3 days ago
-
RE: Creating a second zone on Mitsubishi Ecodan ASHP
Had another go at this, the morning. With SW2-7 ON it ...
By BryanB , 3 days ago
-
RE: Samsung ASHP scheduling help
@morh Your post was music to my ears! I am getting a ...
By Elgreco69 , 3 days ago
-
RE: Issues with Vaillant connectivity via the MyCONNECT gateway
@drew-pa I have given up on the app - right now it is s...
By dr_dongle , 3 days ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
Hi - we have a Daikin 16kW HT ASHP installed which was ...
By Marzipan71 , 4 days ago
-
RE: Question about Ecodan's Room Autoadapt mode
@gary Thanks. I'm emboldened to give it a go!
By afarmery , 4 days ago
-
RE: My ASHP is not performing as well as I’d hoped: COP just over 2
@toodles No. But I wasn't forced there either and The K...
By Morgan , 4 days ago
-
RE: Viessmann Vitocal 250-A in the UK
We have a 10Kw Viessmann 200A it SCOP is currently 5.2,...
By MikeF , 4 days ago
Latest Topics
-
Ecodan software update. Real or scam?
By Morgan 13 hours ago
-
Noise problems with newly installed Samsung 8kW ASHP
By Lokisam 2 days ago
-
Central heating inhibitor with ASHPs
By IRMartini 3 days ago
-
Advice on potential HW Cylinder size
By JWilliams89 3 days ago
-
By Graeme 5 days ago
-
Interesting heat pumps installations
By Mars 1 week ago