Samsung HTQuiet configuration for the 6th generation controller
hi all,
I have been playing with the configurations over the past weeks. Using this material:
2. https://midsummerwholesale.co.uk/pdfs/samsung-sunamp-quick-start-rev-2.pdf
The installer indicates that he set the Samsung LCD controller as the thermostat. I managed to organize all the water law stuff, etc. It is getting warm in the house now. Not many problems there. The cold days I had a COP of 3 on average, now approaching 4. So that seems to be more or less "in control".
Without an additional external thermostat, #2091 and #2092 should be zero = not used (according to the manual), and #2093 should be put to any of these values (default = 4):
0 Not use
1 Use signal only on/off
2 Use (signal on/off) or WL interlink off (water pump 1)
3 Use (signal on/off) or WL interlink off (water pump 2)
4 Use (signal on/off) or WL interlink off (water pump 3)
These values seem to behave similarly to the ones described in the manual on page 28. The standard temperature is set to "indoor". The Samsung LCD controller gives the right indoor temperature in the room (double-checked with some other devices in the same room).
The issue: the controller triggers based on the ambient temperature: if the room is getting below 20C, it starts the heat pump to heat the radiators following the water law (WC). However, it keeps on doing this and does not seem to "stop" the heat pump once it reaches the required temperature... The above values try to reduce hysteresis, but, also, option 1 does not trigger an "off". I first thought it had something to do with the difference that needs to be larger than a threshold value (Indoor Zone option -> Temperature unit -> 0.1/0.5/1, but that seems incorrect, more for setting the temperature).
The inside temperature sometimes goes up to 21C. It does, however, stop sometimes for whatever reason, I can not get my hands on it.
My reasoning now is that the "Use (signal on/off) or WL interlink off" does not trigger the signal off. But it stops because of the "WL interlink off"... I have no idea what the WL interlink is. My best guess now is that it has to do with #4052, the target deltaT, as usually, in the course of the afternoon, with warmer temperatures, the heat pump is triggered to stop. My eye also fell to #4061 for "zone control", no idea what this is...
Does anybody know what the WL interlink logic is doing and how I control this? Anybody any clue why the "signal on/off" only triggers on and no 'off"?
thanks for any help or pointer...
tom
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 57 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@fiona I admire your optimism in regard to what your...
By JamesPa , 7 minutes ago
-
RE: Renewables & Heat Pumps in the News
The main reason we cannot rule out an attack on the Ibe...
By Transparent , 1 hour ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@jamespa And then there was the window company I had...
By davidnolan22 , 2 hours ago
-
RE: Bizarre Retro-fixes by AAC
So one of the best but simple mistakes I have ever seen...
By ASHP-BOBBA , 3 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
It a ridiculous approach, impossible to have zero disru...
By dgclimatecontrol , 3 hours ago
-
@ashp-bobba Thanks. I'll be interested to find out why ...
By bontwoody , 14 hours ago
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
The ACH can actually make a huge difference. My heat l...
By Matban , 16 hours ago
-
Can that be interrogated using Modbus? Over an RS485 ...
By Transparent , 17 hours ago
-
If you've never played (or heard of) Pirate Fluxx, then...
By Transparent , 17 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
This is going to be interesting because Samsung’s suppo...
By Mars , 20 hours ago
-
RE: Mitsubishi Ecodan F8 error
Better than an early Windows/DOS error 'Faulty keyboard...
By JamesPa , 1 day ago
-
I can now, I done an automation in Home Assist...
By DREI , 1 day ago
-
RE: Bosch CS5800i 5kW - Experience So Far
What a difference a pump makes. We don't have OpenEne...
By Steelbadger , 1 day ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I installed the 80L tank (volumizer) things got better ...
By immunity , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 2 days ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 2 days ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 2 days ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 2 days ago