Samsung HTQuiet configuration for the 6th generation controller
hi all,
I have been playing with the configurations over the past weeks. Using this material:
1.
2. https://midsummerwholesale.co.uk/pdfs/samsung-sunamp-quick-start-rev-2.pdf
The installer indicates that he set the Samsung LCD controller as the thermostat. I managed to organize all the water law stuff, etc. It is getting warm in the house now. Not many problems there. The cold days I had a COP of 3 on average, now approaching 4. So that seems to be more or less "in control".
Without an additional external thermostat, #2091 and #2092 should be zero = not used (according to the manual), and #2093 should be put to any of these values (default = 4):
0 Not use
1 Use signal only on/off
2 Use (signal on/off) or WL interlink off (water pump 1)
3 Use (signal on/off) or WL interlink off (water pump 2)
4 Use (signal on/off) or WL interlink off (water pump 3)
These values seem to behave similarly to the ones described in the manual on page 28. The standard temperature is set to "indoor". The Samsung LCD controller gives the right indoor temperature in the room (double-checked with some other devices in the same room).
The issue: the controller triggers based on the ambient temperature: if the room is getting below 20C, it starts the heat pump to heat the radiators following the water law (WC). However, it keeps on doing this and does not seem to "stop" the heat pump once it reaches the required temperature... The above values try to reduce hysteresis, but, also, option 1 does not trigger an "off". I first thought it had something to do with the difference that needs to be larger than a threshold value (Indoor Zone option -> Temperature unit -> 0.1/0.5/1, but that seems incorrect, more for setting the temperature).
The inside temperature sometimes goes up to 21C. It does, however, stop sometimes for whatever reason, I can not get my hands on it.
My reasoning now is that the "Use (signal on/off) or WL interlink off" does not trigger the signal off. But it stops because of the "WL interlink off"... I have no idea what the WL interlink is. My best guess now is that it has to do with #4052, the target deltaT, as usually, in the course of the afternoon, with warmer temperatures, the heat pump is triggered to stop. My eye also fell to #4061 for "zone control", no idea what this is...
Does anybody know what the WL interlink logic is doing and how I control this? Anybody any clue why the "signal on/off" only triggers on and no 'off"?
thanks for any help or pointer...
tom
Currently viewing this topic 1 guest.
- 22 Forums
- 2,096 Topics
- 46.1 K Posts
- 93 Online
- 3,383 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi cycling while on chilled water output
@iaack they have a finned emitter at the bottom a bit l...
By downfield , 34 minutes ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 6 hours ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 7 hours ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 1 day ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 1 day ago
-
RE: Commencing on an ASHP Installation Process
That outside pipework would concern me. Surely rigid se...
By benson , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 2 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 3 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 3 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 3 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 4 days ago