Samsung Gen6 setting I can't fathom..........

11 Posts
3 Users
0 Likes
397 Views
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

Our system seems to be operating as it should apart from one random (doesn't seem to be linked to time of day or outside temp) issue.

No more than once a day and not everyday the system will heat  "Water Outlet" to 64deg. No heat is cycled through radiators as the two remote zone thermostats are not asking for heat so the zone vales are closed. It does this with and without Zone screen "off". 

The Operation Status screen shows Comp Operation/ Water Tank and Water Pump as in use.

I have failed to find a setting that will stop this happening ............... has anyone seem similar ?

 

TIA

 

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
Quote
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

The pump came on again early this morning. 

I took more pics but I can't see any clues apart from  "Thermostat 1" being "on" in Zone status info ?

20230914 031611
20230914 031457
20230914 031819
20230914 031828
20230914 031450

 

 

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

ASHP ran on until outlet temp reached 64.

The lights on zone valve boxes above show neither were calling for heat.

20230914 032357

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote
(@mike-h)
Reputable Member Member
1106 kWhs
Joined: 2 years ago
Posts: 118
 
CDF2B716 EC91 4AF0 84EF 59FB06CD899C

@lenny The main Thing that comes to mind is that the heat pump is heating your domestic hot water tank. This is about the only time you would expect the flow temperature to reach 60° or more.

 
If you switch your screen to view domestic hot water details, Then you should see the temperature in your tank rising as the flow temperature rises. I hope this helps.

   
ReplyQuote
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

Thanks.

Heat pump does heat/maintain DHW but max temp is 55 (I wonder if it is running random disinfection cycle ? }

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote
(@mike-h)
Reputable Member Member
1106 kWhs
Joined: 2 years ago
Posts: 118
 

@lenny When you say the max temperature is 55 deg C, I presume you mean the max temperature that your DHW  is heated to. That is the default maximum. However the flow temperature from the heat pump (the water outlet temperature in your screenshot) will be at least 60 deg C to achieve the 55 deg C temperature of the domestic hot water. Otherwise, it wouldn't heat your hot water to 55 deg C.


   
ReplyQuote



(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

@mike-h 

thanks again, yes, that is probably it. I'll wait till next time and look

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote
(@mike-h)
Reputable Member Member
1106 kWhs
Joined: 2 years ago
Posts: 118
 

@lenny If you have Solar PV, it would probably save you a lot of money to install a Solar iBoost or similar device. This will heat your hot water from the electricity produced by your solar PV for free for at least half the year. My Samsung doesn't get used at this time of year. Failing that, it is also probably cheaper to schedule when your heat pump heats your hot water. There is inevitable heat loss from the tank and pipe work, so unless you need piping hot water all the time, heating it once or twice a day is more economical.


   
ReplyQuote
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

Set DHW on a schedule and this AM it came on proving that it was just as you suggested 🙂 . not a "issue I couldn't find" just me not thinking sideways enough.

Also the iBoost suggestion, I have been thinking about that 

 

Thanks

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote
(@prjohn)
Reputable Member Member
553 kWhs
Joined: 3 years ago
Posts: 124
 

I have the same pump as your self and a 4kw solar array. I would strongly advise you to get an Iboost. My iboost heats my water approx 9mths in the year. As I have nowhere else for my free energy to go I have the tanks set for 70C. I also have the HP coming on in the late afternoon so any "free" solar during the day is used to heat water, the HP is set to heat the hot water to 48c which is adequate for us as a back up to solar. The HP is only set for 1 hour which is long enough to heat to 48c and has never failed to achieve that. Limiting the schedule saves you money. 


   
ReplyQuote
(@lenny)
Trusted Member Member
388 kWhs
Joined: 12 months ago
Posts: 18
Topic starter  

thanks.........

The HP coming on via the iBoost or with the PV setting in the Gen6 controller ?

Samsung 12kw ASHP, nine 415w PV panel array, upgraded radiators and DHW water tank (+ pumps etc). Two wireless zone thermostat controllers and Samsung MWR-WW10N


   
ReplyQuote