Samsung gen 6 - how to manually turn on/off immersion (booster)
Hi all,
New to the forums - I've just had a Samsung gen6 12kW ASHP installed, and initial impressions are good - install seems good and it's running well.
One thing I can't figure out is a quick/easy way to manually (and/or schedule) the immersion to come on/off.
We are on Octopus Agile tariff, so occasionally get very cheap or free electricity slots. I've disabled the scheduled legionella cycle (we empty and reheat the tank twice daily), and try to schedule DHW reheats during cheaper periods. But I'd like to be able to manually turn on/off the immersion to take advantage of cheap/free pricing slots to manually manage heating the DHW tank to higher temps when it's cheap/free (as a cheap/free store of energy and manual legionella protection). Is there an easy way to turn on/off the immersion?
In the control panel schedule, I use Standard DHW to schedule the overnight reheat, and it reheats in around 20-25mins depending on starting/ambient temps (Max Operating Time (3025) and Delay Time (3032) both set to 60min to prevent immersion from kicking in on normal DHW reheat cycle). I understand the Power option uses the immersion - does the Power option use the immersion for the whole cycle? If so, I could use this, but not sure how to then heat above my max DHW temp setting of 50C (FSV 3021) or does 3021 limit only apply to the ASHP, not the immersion?
I'd like to understand exactly how the legionella (disinfection) cycle operates? I have a set point of 47C for DHW, with a max temp set to 50C (FSV 3021). Does the legionella programme heat to 50C using the ASHP and then use the immersion to boost this to 60C (or whatever it's set at in FSV 3044), or does the whole cycle use the immersion (booster) heater?
Thanks in advance,
OS
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist HI OS, yeah you're right using the power mode or forced mode the delay timer for the immersion heater will be neglected and will switch on straight away.
You can use the over shoot setting #3033 and increase to 4, so it will heat 4 degrees over your set temperature.
So I think you can set a very long delay for the booster heater, when running the DWH on standard mode, that way the booster will almost never turn on. Then when you want to do a manual heat up, use the power/forced mode to fire up the immersion heater straight away.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Thanks. Hopefully we may have some cheap pricing slots on Agile this weekend, so I will be able to have a play and observe how these settings behave in practice.
I have already set a long Delay Time (3032) of 60mins to prevent the immersion kicking in in normal operation, but have not tried Power or Forced mode yet to see how they behave. I'll check #3033, but I suspect it's at the default value of zero.
Not sure how I can use this to get to higher temps though (for manual legionella cycle), as the max temp is 55C, and the max overshoot is 4C, giving a combined max achievable temp of 59C?
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist My one thought is that if you’re getting 100% efficient very cheap hot water, is that still more expensive than 400% efficient heat at your standard rate?
How cheap are the cheap rates? It might not actually be worth doing because of the reduced efficiency.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker absolutely correct - I'd only manually kick in the immersion when prices turn negative, so (a) I can store energy by heating DHW as high as possible (above my normal set point), and (b) allow me to run the DHW through the immersion AND the heating simultaneously (in winter), thus capitalising on any negative pricing slots.
Under normal circumstances (i.e, if I'm paying for it), the immersion stays off as it's far more efficient to use the ASHP.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 15 Online
- 5,655 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@tim441 Thanks, PM received and appreciated, I can't ev...
By Carlo , 2 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
I am keen to see how this unfolds and changes the lands...
By ASHP-BOBBA , 4 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 7 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 7 hours ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 7 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 8 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 8 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago