I came across this video which is an interesting example of heat pump control within Home Assistant
Hi all
Recently had a Samsung AE140BXYDGG heat pump installed and have installed the modbus mim-b19n interface to link to Home Assistant. Before coming accross this thread I have been pulling my hair out as I'm new to modbus.
I have connected the modbus interface to a waveshare rs485 to ethernet adapter and have added some code from this thread into HA and I get 2 switches for hot water and heating plus the dhw temp sensor. Can anyone help with the code for the other sensors?
I see there is also a python script to modify the modbus interface. Can this be done over ip or do I need to connect by usb to my pi running HA?
Posted by: @jasoncs1Hi all
Recently had a Samsung AE140BXYDGG heat pump installed and have installed the modbus mim-b19n interface to link to Home Assistant. Before coming accross this thread I have been pulling my hair out as I'm new to modbus.
I have connected the modbus interface to a waveshare rs485 to ethernet adapter and have added some code from this thread into HA and I get 2 switches for hot water and heating plus the dhw temp sensor. Can anyone help with the code for the other sensors?
I see there is also a python script to modify the modbus interface. Can this be done over ip or do I need to connect by usb to my pi running HA?
Thanks in advance for any help 😀ÂÂ
Before trying to accomplish some form of on - off control via HA or otherwise, I would suggest that you consider the benefits of Weather Compensation (WC) control.
How technical are you? Do you understand the internal workings of a digital control system?
Â
Posted by: @derek-mBefore trying to accomplish some form of on - off control via HA or otherwise, I would suggest that you consider the benefits of Weather Compensation (WC) control.
How technical are you? Do you understand the internal workings of a digital control system?
Hi, I'm new to modbus but not far from being able to read all the available sensors. I just need help getting these other sensors into HA then HA can do the automations.
You may find the following of use.
Â
@derek-m thank youÂ
This is my current config, I'm just trying to see as many sensors as possible. It is at a holiday home so I just want to have control remotely. I am not sure what automations yet just integrate into HA before I leave..
# samsung ashp
modbus:
- name: "Samsung ASHP"
type: tcp
host: 172.16.1.115
port: 502
sensors:
- name: "DHW Temp"
slave: 1
address: 75
input_type: holding
unit_of_measurement: °C
state_class: measurement
count: 1
scale: 0.1
offset: 0
precision: 1
switches:
- name: Under Floor Heating
unique_id: samsung_gen6_14kw_heating
slave: 1
address: 52
command_on: 1
command_off: 0
verify:
input_type: holding
delay: 10
address: 52
state_on: 1
state_off: 0
- name: Hot Water
unique_id: samsung_gen6_14kw_hot_water
slave: 1
address: 72
command_on: 1
command_off: 0
verify:
input_type: holding
delay: 10
address: 72
state_on: 1
state_off: 0
One way to start would be to read each consecutive 16 bit Modbus register in turn and then try to decipher the information that is being stored. If you obtain some data by this method I may be able to help with the deciphering process.
Posted by: @steven@tomc are you adding a 120ohm resistor on the MIM-B19N between A+B terminals? I know Homely's install requires it and I see the USB adaptor you shared has a 120ohm on its A+B terminals.
How about ground, are you connecting that at both ends and if so what to?
Finally, are you using shielded/unshielded Cat5 or Beldren and what's your approx run length?
Hi @steven,
could you please say which contacts you used in the outdoor unit for the MIM-B19N
Â
is there a way to insert select switch for register 73 in ESPHome, I tried with number function and it works fine but a switch would be great.
0: Eco
1: Standard
2: Power
3: Force (for the EHS only)
Others: Ignored
@kocta This is my configuration.yaml code which is very much based on the work of others here
# Samsung Heat Pump Modbus Connection modbus: - name: "samsung" type: serial baudrate: 9600 bytesize: 8 method: rtu parity: E port: /dev/ttyUSB0 stopbits: 1 switches: - name: Heating unique_id: samsung_gen6_8kw_heating slave: 1 address: 52 command_on: 1 command_off: 0 verify: input_type: holding delay: 10 address: 52 state_on: 1 state_off: 0 - name: Hot Water unique_id: samsung_gen6_8kw_hot_water slave: 1 address: 72 command_on: 1 command_off: 0 verify: input_type: holding delay: 10 address: 72 state_on: 1 state_off: 0 sensors: - name: "Heat Pump Outdoor Temperature" scan_interval: 60 slave: 1 address: 5 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 # - name: "Heat Pump Status" # scan_interval: 60 # slave: 1 # address: 52 # data_type: int16 - name: "Heat Pump Mode" slave: 1 address: 53 data_type: int16 - name: "Heat Pump Outdoor Error Code" scan_interval: 60 slave: 1 address: 1 data_type: int16 - name: "Heat Pump Indoor Error Code" scan_interval: 60 slave: 1 address: 63 data_type: int16 - name: "Heat Pump Defrost Status" scan_interval: 60 slave: 1 address: 2 data_type: int16 - name: "Heat Pump Target Indoor Temperature" scan_interval: 60 slave: 1 address: 58 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Indoor Temperature" scan_interval: 60 slave: 1 address: 59 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 2 data_type: int16 - name: "Heat Pump Return Temperature" unique_id: ss_heat_pump_return_temperature scan_interval: 60 slave: 1 address: 65 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Flow Temperature" unique_id: ss_heat_pump_flow_temperature scan_interval: 60 slave: 1 address: 66 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Water Out Set Temperature" scan_interval: 60 slave: 1 address: 68 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Hot Water Status" slave: 1 address: 72 - name: "Heat Pump Hot Water Mode" scan_interval: 60 slave: 1 address: 73 data_type: int16 - name: "Heat Pump Hot Water Set Temperature" scan_interval: 60 slave: 1 address: 74 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Hot Water Temperature" scan_interval: 60 slave: 1 address: 75 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Flow Rate" unique_id: ss_heat_pump_flow_rate scan_interval: 60 slave: 1 address: 87 state_class: measurement scale: 0.1 precision: 1 data_type: int16 - name: "Heat Pump Discharge Temperature" scan_interval: 60 slave: 1 address: 60 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Heating Discharge Set Temperature" scan_interval: 60 slave: 1 address: 62 state_class: measurement scale: 0.1 unit_of_measurement: °C precision: 1 data_type: int16 - name: "Heat Pump Immersion Heater Mode" scan_interval: 60 slave: 1 address: 85 data_type: int16 - name: "Heat Pump 3way valve position" scan_interval: 60 slave: 1 address: 89 data_type: int16
Â
This is the script I run from an automation which is scheduled or triggered by pressing a Zigbee button I attached to the front of the DHW cylinder to boost the hot water
alias: Boost Hot Water
sequence:
- service: modbus.write_register
data:
hub: samsung
address: 72
slave: 1
value: 1
alias: Turn Hot Water On
- service: modbus.write_register
data:
hub: samsung
address: 73
slave: 1
value: 1
alias: Set Hot Water Mode to Standard
- service: modbus.write_register
data:
hub: samsung
address: 74
slave: 1
value: 500
alias: Set Hot Water Temp to 50°C
- delay:
hours: 0
minutes: 30
seconds: 0
milliseconds: 0
alias: Delay for 30 mins
- service: modbus.write_register
data:
hub: samsung
address: 72
slave: 1
value: 0
alias: Turn Hot Water Off
- service: modbus.write_register
data:
hub: samsung
address: 73
slave: 1
value: 0
alias: Set Hot Water Mode to Eco
- service: modbus.write_register
data:
hub: samsung
address: 74
slave: 1
value: 450
alias: Set Hot Water Temp to 45°C
mode: restart
icon: tc:heat-index
Posted by: @iancalderbankPosted by: @redzer_irlThe main part is "modbus.write_register" and the payload associated with that.
thank you . Big clue. thank you again. you're running these as HA commands with the modbus connected physically directly to and controlled from your HA machine? you're not using ESPHOME or ESP devices?
would you mind testing if the modbus.write_register HA command is able to succesfully change target flow temp? (register 68) ?
Â
@iancalderbank I have come back to this a number of times but always thought I was doing something wrong. My system was initially set up to use Water Law and when I try to write to register 68, nothing happens - as expected from the information here.
My problem is I cannot figure out how to change my system into non-Water Law mode. I have included a picture of my heating screen below and when I move the blue selection to "Heat" and click OK, I get the following message: "The thermostat is connected and automatically controlled" and then nothing happens. The "Water Law" text remains below the word "Set" on the left hand side and the value remains at 0.0°.
If you, or anyone else, can point my in the right direction to change the settings then I will certainly try to write to register 68 again.
Â
Â
- 26 Forums
- 2,360 Topics
- 53.5 K Posts
- 89 Online
- 6,026 Members
Join Us!
Worth Watching
Latest Posts
-
Sadly, no, @agentgeorge. The inverter will handle 5kW t...
By Majordennisbloodnok , 5 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent The readings are 0 for amps, 0 ...
By Batpred , 5 hours ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 6 hours ago
-
RE: Speedcomfort radiator fans
I watched the video to see whether they'd potentially b...
By Sheriff Fatman , 6 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@ecoste For what it's worth, this is my equivalent data...
By Sheriff Fatman , 7 hours ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 7 hours ago
-
RE: Setback savings - fact or fiction?
Will come back to the above points, but for now, I've j...
By cathodeRay , 7 hours ago
-
@jamespa I have found that it comes as a shock when we ...
By Toodles , 9 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
I suspect a good chunk of the "losses" are power consum...
By Bash , 10 hours ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Hi @mickamills . Welcome to the forum. It sounds like...
By bontwoody , 11 hours ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 11 hours ago
-
RE: External pipework insulation
@transparent I hope you are not being admonished @trans...
By Toodles , 11 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The FT levels off at either the set point OR the minimu...
By AndrewJ , 1 day ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent Thanks, this helps. Could it be that St...
By Batpred , 2 days ago
-
RE: Clivet ASHPs and weather compensation
Simon did share a lot of very helpful advice. On furthe...
By ambris , 2 days ago
-
-
RE: Advice on internal circulation pump noise
Extend the primary branch and make sure you have more t...
By ASHP-BOBBA , 2 days ago