Posted by: @boycey@toodles hi, I think you may of mis understood my post, I'm happy with my temps atm, and I'm monitoring them as the oat getting nearer 0C and will tweak as needed. My post was, am I thinking right, aiming to keep the third party stats above the obtainable room temp so they are always calling for heat, ie so the loops are all open and flow temp is just right to keep rooms at, for example 20.5c or whatever the comfortable level is for any one using this thought process. If one can get the weather comp curve just right, the ufh will continually run just the right flow temp, ie low and slow.. is this the right way to try and run my heat pump.
principles are good.
regarding DT3 this may or may not be issue.
May be issue- if flow rate is high (I believe the 5kw model has a low flow rate, less than 14 LPM.) or you have a low loss header with balance issues. Or WC curve is calling for too low a temperature for the HP to keep operating at (leading to cycling)
May not be an issue- if HP is trying to minimise output (modulate) if your WCcurve is asking for a low flow temp and the heat pump can manage to run at that low output without cycling.
three questions- 1 what’s your flow rate compared to optimum in data book? 2 what’s your total emitter heat loss when running at 25c in an ambient of 20c? 3 is the answer to Q2 equal to or higher than the minimum output of the 5kw model? If the output capability is less than the min operating output then there may be short cycling.
questions easy but answers may be bit harder.
maybe try posting an hourly operation graph off MELCloud showing flow and return temps and cycling frequency.
also try moving flow temp up one degree at a time if you want to stop cycling… if that’s a problem.
When ambients are colder cycling should get less. So any problems may be less noticeable.
Also raise your room stat a bit higher incase you’re getting room stat cycling instead of output short cycling. If your WC curve is set accurately to your heat loss temperature gains in room should be very slow.
@sunandair Hi thanks for the questions, im not sure i can answer then fully though but hes what i can say.
1. i have the MCs cert and under floor flow rates from commissioning, Design flow rate 7.2L/M (7 rooms all at 1l/m each) then Actual adds up to 9.8L/M, 2 rooms at 1.5, and 2 at over 2L/M. The cert also say flow rate 45deg and SCOP of 3.65. but i can't see any where near that when i use the consumed and delivered figures on the FTC6.
my pump was set to speed 5 originally approx 14 L/M when we first moved in, ive got it down to speed 2 now =9L/M.
2, not sure where this info is
3, nor this
so ive reduced the pump to what seems a better rate i think, should i be looking at the manifold rates and adjusting them to compliment the pump flow rates now, and bring them closer to 1 for each room?
ill see if i can get the melcloud hourly graphs
That’s great @boycey
it might help to know how warm the room was at 14:00 and what was the outdoor ambient at the same time. It looks like the cycling increases once the floor has been heated for a few hours…. As though it reaches a certain saturation temperature.
your DHW cycle shows it’s keeping a steady DT OF 5c
reverting to space heating also good
interesting that 14:00 graph shows heating after the ramp up.
I think I see return water (black line) coming back a bit too warm so the line curves upwards. forcing the flow temp (LWT) to also rise- until it reaches 30c which is presumably target flow temp so it shuts down for a while
That would suggest insufficient heat is being offloaded into the floors to allow the 30c flow temp to continue, for whatever reason.
Others may have a view as to why. But it does seem to behave differently the next hour.
I think your model heat pump has a minimum output of around 1.9 to 2.4kwh depending on outdoor temperatures.
Do you know the construction of you UF heating is there poured concrete or insulation under it? Spacing of pipes? Floor coverings… These things affect the performance of the heat emitting surface.
@sunandair hi. So if the Delta T is OK when doing DHW that's good, but not so on ufh? Could this be the flow rates on manifold need adjusting, I've reduced the pump flow, not sure what the rates are on the manifold as its behind the washing machine, I'll have to pull it out whilst the system is calling for heat. Am I correct in thinking the flow rates on the manifold could be a bit high, as per the commission doc designed at 1 l/m per room but some were set up at 2 l/m? So maybe by reducing these the delta T for heating would be better?
Oat was around 4 deg at 14:00, rooms at about 20.5 deg stats at about the same or just calling
I don't know the construction, but it's 2 years old, I assume poured concrete with insulation, LVT main living area kitchen/diner/lounge and hall, tiled baths, and carpeted bedrooms. Top floor in block, south facing front and east on one side
hi @boycey I don’t have underfloor heating so can’t comment on what adjustment to the existing setup you might make. hopefully there may be others in this forum who know more about the specifics of Under Floor heating and about flow rates through the manifolds.
My thoughts are drawn, perhaps prematurely, to the carpeted areas and whether you have underlay which might prevent heat radiating. Or whether introducing towel radiators might raise the heat loss to a better level. But this may be far too early or complex to even think about doing at this stage.
So perhaps someone who has UF Heating might offer some advice on how these graph outputs appear or may be adjusted.
-
ASHP install contract and BUS grant money
6 days ago
-
Oversized Ecodan
1 week ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
2 weeks ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 67 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Setback savings - fact or fiction?
We certainly are, and that's why I am here too. But tha...
By cathodeRay , 2 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 8 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 10 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think most heat pumps have this mode but I cant see h...
By JamesPa , 41 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago