Questions on my Hitachi Yutaki SCombi Heat Pump
I am trying to understand more about my Hitachi Yutaki SCombi Heat Pump (I am new to this and have a limited understanding). I appreciate that there are no active users of this system on this forum. So some questions.
The heat pump has a max power of 3kw input and approx. 12kw output.
Is the primary circuit the circuit that contains the refrigerant (outdoor unit to indoor unit piping)?
HPWF - m3/hr Heat pump water flow. What is this, I can see it modulates down from 2.06 m3/hr to lower numbers. I thought it was the rate of flow of refrigerant across the heat exchanger, but it says Heat pump “water flow”
HPH4 - Inverter frequency operation. The speed that the compressor runs at, and 120hz is the maximum? This is a modulating compressor?
HPTi - Heat pump inlet temperature and HPTo - Heat pump outlet temperature. Is this the temperatures across the heat exchanger on the water side of the system ?
I see the forum often uses a formular Power kW = Flow(l/m)/60 x DT x 4.2. Is there a more details explanation of how I should be using this formular to manage my system?
The system is set for a Delta T of 5 degrees. Is this 5 degrees across the heat exchanger on the refrigerant side or water side??
The heat pump produces a temperature of say 45C to the heat exchanger, which turns into a flow temperature of say 30C. Why does the water side not achieve the 45C?
Is there a minimum flow temperature that I can run, with a Delta T of 5C? If have a flow of 30C, this means my return cannot be less than 25C, is this correct?
How does this Hitachi system work. I have a set temperature, and it adjusts the compressor speed and flow rate of refrigerant to maintain the set temperature across the heat exchanger (water or refrigerant), it this how it works?
I run a fixed temperature as the Hitachi weather compensation system is very erratic (outside temperature fluctuations from the sun)
I have attached the explanation of the acronyms from the manual.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
200m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
3kw heat pump
50 litre buffer tank
3.6KW solar panels
Can I suggest you read (if you havent already) this 'starters guide' to heat pumps?
I think you may be getting things confused. Firstly dont worry about the refrigerant circuit, thats for the designers to worry about. Its the water circuit which goes through your emitters you need to concenterate on.
Posted by: @trebor12345HPWF - m3/hr Heat pump water flow. What is this, I can see it modulates down from 2.06 m3/hr to lower numbers. I thought it was the rate of flow of refrigerant across the heat exchanger, but it says Heat pump “water flow”
Yes it will be the rate of flow of water to the emitters. This water also flows across an internal heat exchanger where it absorbs energy from the refrigerant. The rate may well modulate up and down
Posted by: @trebor12345HPH4 - Inverter frequency operation. The speed that the compressor runs at, and 120hz is the maximum? This is a modulating compressor?
Yes it is the speed of the compressor and yes it is a modulating compressor. Dont know if 120Hz is the max, but it will be there or thereabouts.
Posted by: @trebor12345HPTi - Heat pump inlet temperature and HPTo - Heat pump outlet temperature. Is this the temperatures across the heat exchanger on the water side of the system ?
Yes, which should hopefully equal the temperature drop across the emitters unless your buffer is 4 port not 2 port (if so thats disappointing) or there is a long distance/lots of loss between heat pump and emitters
Posted by: @trebor12345I see the forum often uses a formular Power kW = Flow(l/m)/60 x DT x 4.2. Is there a more details explanation of how I should be using this formular to manage my system?
You dont (or shouldn't) need to. Once the water pump speed (or speed range) is set by your installer the heat pump will sort it out. In any case you cant directly control DT, its a function of flow rate and emitter output (your heat pump may modulate the water flow rate to maintain it, or it may not, different heat pump designers make different decisions about this point.
Posted by: @trebor12345The system is set for a Delta T of 5 degrees. Is this 5 degrees across the heat exchanger on the refrigerant side or water side??
Water side
Posted by: @trebor12345The heat pump produces a temperature of say 45C to the heat exchanger, which turns into a flow temperature of say 30C. Why does the water side not achieve the 45C?
Where are you getting the figure of 45C and indeed 30C from, this could be a problem but until we know what you are measuring we cant be certain.
Posted by: @trebor12345How does this Hitachi system work. I have a set temperature, and it adjusts the compressor speed and flow rate of refrigerant to maintain the set temperature across the heat exchanger (water or refrigerant), it this how it works?
The primary control loop of pretty much all heat pumps attempts to adjust two things namely
1. The compression ratio of the compressor - to match the refrigerant temperature to the desired flow temperature (defined by the WC curve or as a fixed temperature). The refrigerant temp will be controlled to a value above above the desired flow temp because heat flows from hot to cold not the other way round
2. The frequency of the compressor to match the power output of the unit to the demand from the house (which it can work out by observing the return temperature.
There are various secondary control loops but this is the basic way it works
Posted by: @trebor12345I run a fixed temperature as the Hitachi weather compensation system is very erratic (outside temperature fluctuations from the sun)
There should not be outside temperature fluctuations from the sun. The OAT sensor should be installed in the shade or if its attached to the unit protected from the sun.
What flow temperature are you running at when its cold outside?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thank you for the reply. That clarifies things. I hadn't read the starters guide, but will do now.
It's a 2 port buffer.
When zero or below, I run a flow of 32 or 33C.
Where are you getting the figure of 45C and indeed 30C from, this could be a problem but until we know what you are measuring we cant be certain. - I made the numbers up to try and understand how the system was working. I often see a refrigerant temperature of 45C and a flow of 30C with a return of 25C.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
200m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
3kw heat pump
50 litre buffer tank
3.6KW solar panels
Posted by: @trebor12345It's a 2 port buffer.
When zero or below, I run a flow of 32 or 33C
OK, thats good and low. With low flow temperatures like this there is less to be gained by operating weather compensation than if you were operating at higher FTs. if you can fix the OAT sensor so its in the shade, I still suggest you do try WC again - it really should not be in the sun! If you cant probably dont worry too much!
Posted by: @trebor12345I often see a refrigerant temperature of 45C and a flow of 30C with a return of 25C.
I honestly don't know if 15C difference between refrigerant temp and flow temp is normal, it seems excessive but it does depend on the heat exchanger. If you aren't getting excessive bills and are getting a reasonable COP 9ratio of heat out to electricity in - which somewhere it will tell you) I wouldnt worry.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,030 Topics
- 44.2 K Posts
- 29 Online
- 3,235 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 5 hours ago
-
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
I since checked the magnetic filter again and there was...
By Phoenix15 , 6 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Agree - I will finish optimising the rads before I thin...
By Tomdad , 6 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
So sorry to follow up self but this may clarify things ...
By Toodles , 8 hours ago
-
...which I assume started shortly after this post. I ac...
By rhh2348 , 9 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@robs Regarding the November operation as attached, t...
By Heatgeek , 11 hours ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 14 hours ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 1 day ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
Thank you, that helped in my understanding. I believe ...
By trebor12345 , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@old_scientist As another example of errors / differenc...
By Toodles , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Not with Eon Next. The only reson I left O...
By Andris , 3 days ago
-
Is this normal? Click of the DHW returning to space heating
This has been bugging me for a while and I just wanted ...
By Grantmethestrength , 4 days ago
-
@sandman1600 you need to measure whats going on real...
By davidnolan22 , 4 days ago
-
@brandon-r is this a project that you could assist with...
By Mars , 4 days ago
-
Has anyone installed these on their ASHP fed radiator s...
By Grantmethestrength , 5 days ago