Newbie: utterly confused with my Mitsubishi Zubadan air source heat pump running on 55C set flow temperature
@jamespa Thanks again for this info.
Just by way of an update, I’ve spoken to Mitsubishi support today and while they wouldn’t commit to anything because they’re obviously not in receipt of all the facts, he did say that a) he’s never seen a 14kWh machine on a single zone install before. And b) the flow rate is concerning. He said he’d expect 40l per hour rather than the often sub minimum 16 or 17 l per hour we’re seeing.
The R290 does sound like a good option but as you say; I doubt we’ll get the choice if they do arrange a swap.
Looking at the energy usage yesterday the COP is around 2.5 (or 2.9 if just looking at heating and not DHW).
Sadly the MelCloud charts don’t give you exact figures so there’s an element of guess work.
We seemed to see less cycling over the last 24 hours. Other than it bouncing around between 7am and 8am today it’s been fairly stable.
it was “buoyant” during warmer/sunnier hours yesterday (from 10am to 3pm) though.
Temperatures are looking warmer over the next couple of days so I’ll keep my eyes on it. My concern is that the $#!£ will really hit the fan when the weather gets warmer.
It may be unrelated but the concerns that @davidnolan22 initially raised about the low flow rate and also Mitsubishi’s reaction would suggest something’s amiss with the setup.
It does now feel like the size is overkill for this house.
We don’t have a diagram of the tank setup sadly. And I appreciate there’s a lot to try to fit into photos amidst the sea of lagging.
One thing that did occur to me is that we have motorized valves (image attached) on each manifold. When our original heating engineer was on site a few months ago he said we wouldn’t need that if we had a heat pump. He’s not a heat pump expert though.
Could that be causing an issue with performance?
Thanks for the legal references. I spent ages yesterday searching for them all but I couldn’t find the pertinent ECO4 references so this is all really useful again.
@sandman1600 just for comparison purposes and in case useful as evidence (!) here's my energy usage and flow temps for the same day and same Mitsi 14kW unit:
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
Posted by: @sandman1600One thing that did occur to me is that we have motorized valves (image attached) on each manifold. When our original heating engineer was on site a few months ago he said we wouldn’t need that if we had a heat pump. He’s not a heat pump expert though.
If they arent permanently open then yes they would cause a problem (unless they are all wired to close simultaneously when the DHW comes on - instead of a diverter valve. But I think I saw a diverter valve in the photo. What opens/closes them, room stats?
Posted by: @sandman1600Just by way of an update, I’ve spoken to Mitsubishi support today and while they wouldn’t commit to anything because they’re obviously not in receipt of all the facts, he did say that a) he’s never seen a 14kWh machine on a single zone install before. And b) the flow rate is concerning. He said he’d expect 40l per hour rather than the often sub minimum 16 or 17 l per hour we’re seeing.
14kW is a big machine, the sort of machine you put in houses that are likely to have more than one zone. However it shouldn't be a problem.
I assume you mean l/min not l/hr. 14l/min would be normal for a ~6kW machine. 40l/min for a 14kW machine. I am guessing the installers adjusted it down to get a specific deltaT across the emitters but thats only really a guess. Or alternatively something in the circuit is limiting it. But the fact the house is getting hot suggests that you dont need much more!
I note 25kWh consumed for heating, about 70kWh delivered on the 16th, COP as you say ~2.8/2.9. One day alone is a bit meaningless but nevertheless, for comparison, my figures were 23kWh consumed, 96kWh delivered (COP 4). Thats for a 7kW house.
Heating COP 2.9 is a bit better but really you should be seeing better still now its warm during the day.
Posted by: @sandman1600Temperatures are looking warmer over the next couple of days so I’ll keep my eyes on it. My concern is that the $#!£ will really hit the fan when the weather gets warmer.
Costs should get better as it gets warmer. Heat pumps get more efficient as flow temp falls or OAT rises.
The Melcloud user manual shows plots of various things over multiple days https://library.mitsubishielectric.co.uk/pdf/book/MELCloud_USER_MANUAL_UK1#page-1 It would be really helpful if you got these for the key parameters (eg energy, flow temp, outside temp, indoor temp) since it was installed, preferably, if it will let you do so, on the same scale.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
There is a private website called mel cloud. This logs into your data via the internet and gives loads more data. It will give you the compressor output live.
What I would ask mitshi engineer would be whats the COP consequence of 16-17 l/minute through the I assume a lager heat exchanger of the 14kw unit too. I ask this as with flow on the 30s generally, the COP should be higher than that.
even though the flow rate is concerning, I’m not sure id turn it up or ask for it to be, as this will deliver more energy into the house. Not sure you need that.
this there any way to increase the flow through the manifolds (twist the knob) are Some showing more flow than others? This is tricky and balancing, but if you can increase secondary side flow and output, it would help
If you want to check what your pump speeds are set to here is the video, they can be set to 1-5 for heating and DHW as others have said 17L is low for a 14kw unit the recommended is 25L/min this is based on a dT of 8 which is what all Mitsubishi heat pumps are designed to.
Posted by: @davidnolan22even though the flow rate is concerning, I’m not sure id turn it up or ask for it to be, as this will deliver more energy into the house. Not sure you need that.
I think what will actually happen is that the deltaT from flow to return will decrease. There may be a slight increase in energy to the house (because the average emitter temp will be higher as a result of lower deltaT) but not much as energy to house is principally goverened by how much the emitters emit, which in turn is goverened by emmitter temperature and room temperature. The heat pump responds to this, not the other way round.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@gary Thanks for the link to the video. Appreciate it. I'll check out what its's currently set to but I'm reluctant to change it until I get a better idea of what I'm doing.
The MELPump website looks very promising. There's a lack of data on a lot of the reports at the minute but I assume it will start logging the daily data now I've signed up.
I'm very wary of anyone adjusting the flow temperature until I know what's going on. Looking at the Polypipe design documents it breaks down the circuit flow rate for each room and it's between 0.5 to 2 in each room. I'm assuming there is a way of controlling this on the manifold but I'm not sure I'm confident with changing stuff I don't really understand.
It looks like some of them are at slightly different levels.
how many loops on that one?
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 233 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 9 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 11 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 14 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 16 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 16 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 1 day ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago