It's probably worth adding that it's unlikely that Samsung would offer a thermostat to go with their heat pump because you shouldn't be using a thermostat to control a heat pump!
It's also probably worth adding that homely wont/can't (I presume) stop the heat pump cycling when the demand is less than the minimum the heat pump can turn down to. It may however 'manage' the cycling intelligently into the longest cycle time possible without causing your house temperature to swing too much.
Ps I agree with all the recent comments by @derek-m and @toodles. You don't need a homely, you almost certainly don't need to change your thermostat. What you need to do is adjust the WC curve to do the job and get your thermostat out of the way of the control loop by turning it up above the target temperature and using it purely as a limiter. The main advantage by far of a homely is that it essentially does the WC adjustment for you, but that doesn't make it necessary
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iantelescope This is the whole point Ian, the WC makes the necessary adjustments - and does them far more kindly than any thermostat ever could. It won’t make a difference whether you set that ‘stat’ 2 degrees or 3 degrees higher than comfort temperature - the WC is keeping the house at the right temperature - regardless of the ‘stat. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@iantelescope I have homely - and think very highly of it too! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Homely advice ?
Did you , yourself, or a "Trained Installer" install your Homely?
Why are so enthusiastic about it ?
What are the pros and cons ?
My instincts , are still bi-metal strip , but , I can still understand and appreciate Weather Compensation.
Disabling a £120 Thermostat still feels like waste!
@iantelescope The ASHP installers fitted the Homely controller for me. Why the enthusiasm? Well, I required a system that I could set and forget, I wanted a system that would be as efficient as possible, I wanted a system that could be used by my wife were I ill or I kick the bucket, I wanted to be sure that whatever the weather, I could rely on the system to keep us warm - at the lowest running cost.I believe that we have achieved this with Homely and their technical support is excellent as I have confirmed each time I have contacted them.
I suspect their insistence on trained installers fitting the Homely is to ensure it is done properly. The training is not that involved; it is mainly an online training video and the company encourage fitters to ring them when carrying out their first installation and will ‘hand hold’ them through anything the fitter needs to know to ensure success.
I have the bonus of access to the installer’s ‘Connect’ app so I can check performance parameters as the whim takes me. Am I impressed? Yes! Can’t think of any negative aspects, other than it is not free!
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @iantelescopeBut, What if If I want to best use Octopus "Cosy" , what then , How?
I would just leave it to run on WC, treat the cheap periods as a bonus and the expensive one as a kicker.
Cosy is really for people with a battery, due to expensive period at tea time to 7pm.
I'm on E7 and will be leaving mine to run the whole 17 hrs of expensive time, aided by a battery.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @iantelescopeMy instincts , are still bi-metal strip , but , I can still understand and appreciate Weather Compensation.
Don't, just don't. The only sane way to run a heat pump is to use weather compensation and that's a direct consequence of the laws of thermodynamics so you aren't going to circumvent it (there is of course an exception, if you are running at a very low design flow temp, say sub 30C, then there may be a case for fixed flow temp in some circumstances). If you let a thermostat control it you will cost more, quite possibly a lot more, and be less comfortable.
Posted by: @iantelescopeDisabling a £120 Thermostat still feels like waste!
It should never have been fitted in the first place, but you need to get over that. As a temperature controller it is fundamentally unfit for purpose, as is absolutely any thermostat.
Use it as a limiter and if you need a time switch. Or remove it, replace it with a wire/reconfigure the heat pump to ignore it, and sell it, just don't use it as a temperature controller! And if you do replace it with a 'simple', even bimetal, thermostat you still need to set that 2-3 degrees above the desired temperature so it acts as a limiter not a controller.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Believe it or not ...........................I totally agree with you.
I have been using the Samsung Weather compensation offset Screen for most of the last two years.
I use, and intellectually understand, .......................but I, and quite a few others , do not like!
Sorry, .............for my senior moment !
Posted by: @iantelescopeI use, and intellectually understand, .......................but I, and quite a few others , do not like!
I guess that's where homely comes in. @toodles has summarised why he has it.
Unfortunately the Samsung heat pump controller lacks (or did lack - it may have changed since I studied their manual) auto adaption. Thus it relies on the installer or homeowner to set up WC correctly. The first is challenging to say the least unless the installer revisits during the season, which few will. The second is very unlikely with the average homeowner. Basically its a 'fail' in most of real world, which is probably why homely saw Samsung as one of several good targets. Maybe Samsung's principal market has different user/installer characteristics.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A comment by a visiting French Samsung Engineer that " he did not understand many parts of the Samsung Manual " does not inspire confidence.
No "installer " has , in my experience , inspired any confidence in their opinion of themselves, their company or in their non-existent training.
With "installers" and manufacturers staff so poorly trained , who is to be trusted?
@jamesPa many thanks for your obviously competent and experienced advice . Appreciated!
Posted by: @jamespaPosted by: @iantelescopeI use, and intellectually understand, .......................but I, and quite a few others , do not like!
I guess that's where homely comes in. @toodles has summarised why he has it.
Unfortunately the Samsung heat pump controller lacks (or did lack - it may have changed since I studied their manual) auto adaption. Thus it relies on the installer or homeowner to set up WC correctly. The first is challenging to say the least unless the installer revisits during the season, which few will. The second is very unlikely with the average homeowner. Basically its a 'fail' in most of real world, which is probably why homely saw Samsung as one of several good targets. Maybe Samsung's principal market has different user/installer characteristics.
I think that balancing the heat emitters is probably more difficult than setting the WC curve, the important aspect is not to try to rush either.
As a starting point, the warmer weather end of the WC curve could be set for a LWT of 25C at an OAT of 20C, then dependent upon the heat loss calculation data, the cold weather end could be set at something like 45C at an OAT of -5C.
The above should provide a reasonable IAT, which should then be monitored for a period of time. If the IAT is deemed to be too high, then lower the 45C value slightly and monitor again. Repeat the process over days, or even weeks, until you are happy with the results.
- 21 Forums
- 1,966 Topics
- 42.7 K Posts
- 63 Online
- 2,279 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa I haven't forgotten 🙂 But I want to t...
By BAMi , 5 minutes ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
It may be be because the controller has been changed, a...
By cathodeRay , 19 minutes ago
-
RE: Battery storage to run Heat Pump.
The problem with current tariff proposals is that they ...
By Transparent , 24 minutes ago
-
RE: Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
@allyfish thanks for replying, did you mean 2105? (I ca...
By damonc , 28 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
So far, I'm happy with moving to Eon next. Not paid any...
By Andris , 36 minutes ago
-
RE: Split system and pipe lengths for air source heat pump installation
@johnmo got it. Thanks.
By nickmorgan , 1 hour ago
-
Is that because the only people who will quote for 45C ...
By JamesPa , 2 hours ago
-
RE: Setback savings - fact or fiction?
And finally, the R version tidied up a bit and larger, ...
By cathodeRay , 5 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Thanks everyone for posting this, so much useful info t...
By Bamnio , 7 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
I have the same pump and if I am operating it correctly...
By Broadsman , 8 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@editor Will get back. Lots to try. Thanks to everyon...
By cliffhanger , 8 hours ago
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 19 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 20 hours ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 20 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 22 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 23 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 1 day ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 1 day ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 2 days ago
Latest Topics
-
Battery storage to run Heat Pump.
By Broadsman 8 hours ago
-
Heat Pump Sizing & Installation Costs
By Mars 1 day ago
-
SolarPV tables / online calculator
By MichelleC 2 days ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 2 days ago