No problem, Libre office can import and export pdf so we will work with thatPosted by: @iantelescope@johnmo
Sorry @johnmo , The Renewable Hub cannot accept many standard Linux format files.
I can usually translate them into Jpg ,Pdf et al , but often not .
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamesPa Should I talk to my Plumber , holding Off until late next week ?
The Buffer Tank , originally installed "to reduce , or stop Short Cycling " was later installed "to reduce or prevent Heat Pump fin icing ". ( Samsung-Dalliium - Engineer )
The Heat Exchanger was installed , by Telford, to "protect the Heat Pump from the user accidentally stopping water flow in the Radiator circuit".
A single water circuit would expose the Heat Pump to potential Water flow failure. (Telford -Engineer)
Posted by: @iantelescope@jamesPa Should I talk to my Plumber , holding Off until late next week ?
Yes
Posted by: @iantelescopeThe Buffer Tank , originally installed "to reduce , or stop Short Cycling " was later installed "to reduce or prevent Heat Pump fin icing ". ( Samsung-Dalliium - Engineer )
Most likely we will suggest it is retained, but replumbed as a two port volumiser in the return, for the purpose of assisting de-icing.
Posted by: @iantelescopeThe Heat Exchanger was installed , by Telford, to "protect the Heat Pump from the user accidentally stopping water flow in the Radiator circuit".
A single water circuit would expose the Heat Pump to potential Water flow failure. (Telford -Engineer)
This is muddle-headed out of date thinking. Heat pumps must be run with most of the system in circuit, controlled by the weather compensation (water law) curve not on/off thermostats or TRVs. So the user wont/cant/shouldn't do this. The heat exchanger reduces efficiency and effectiveness, in your case because of the parallel buffer tank very likely very significantly..
The people mentioned above are conversing in the background and we will have something for you in the next couple of days. Basically your plan is correct, there may be a few tweaks,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Plumber:
Many thanks for your advice , it is appreciated, I will try and stop the Plumber until late next week.
Heat Exchanger:
The visiting French Samsung Engineer and the NIC engineer described, and defended, the Heat Exchanger as a hydraulic barrier allowing heat to be transferred but not water.
The Heat exchanger apparently "allows for different water, and different flow rates on both Water circuits".
The French Engineer later describing the Heat Exchanger as a "hydraulic isolator" .
Potable Water ??
Some plate heat Exchanger manufacturers have been using Cheaper Stainless Steel on the assumption that the water is "potable"? ( Seigenthaler , Hydronic Heating systems )
What is potable Water ?
My EAC Heat exchanger was manufactured in Alamabad, India ......................without instruction manual.
Many thanks for your advice !
Many thanks derek ...............my Heat Pump output pipe water is definitely NOT fit for human consumption being Black , or dark green !
@iantelescope I attach a proposed revised system diagram and list of tasks/SoW that @derek-m, @johnmo and I suggest, with special thanks to @johnmo who did most of the diagram This assumes that you are now retaining a cylinder not converting to thermino.
Some of the tuning in the list of tasks will be best done by you over a period of time, eg of WC curve and whether to use timed (batch) heating either end of the season to reduce the inevitable cycling which will occur when the demand is low.
Please feel free to ask any questions/discuss anything in the diagram or on the list.
Hope this helps
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many thanks @johnmo , @jamesPa and @derek-m
Your help is invaluable!
Your rebuild of my Heat Pump is identical to my own thoughts with a couple of reservations.
Buffer
A buffer in series with the return , although simple on a circuit diagram, involves pipes physically performing U turns , the Buffer being currently positioned to the left of the Water Tank with the pipes currently pointing or traveling to the right.
I suggested to my Plumber that we remove the entire birds nest of pipes replacing with parallel pipework attached to the kitchen walls. Costly , time consuming , but neat and tidy !. From experience, Neat & Tidy is easier to maintain.
I would like to fit valves on either side of the Buffer with a third valve Shorting the Buffer. This to allow cleaning and reduction in the inevitable Energy losses during Summer. During Spring and autumn the Buffer would be used to reduce short cycling, during winter the buffer would be used to protect against icing .
Again, many thanks .
ian
Posted by: @iantelescopeI would like to fit valves on either side of the Buffer with a third valve Shorting the Buffer. This to allow cleaning and reduction in the inevitable Energy losses during Summer. During Spring and autumn the Buffer would be used to reduce short cycling, during winter the buffer would be used to protect against icing .
The valves will also enable you to determine if it's actually needed!
Posted by: @iantelescopeA buffer in series with the return , athough simple on a circuit diagram, involves pipes physically performing U turns , the Buffer being currently positioned to the left of the Water Tank with the pipes currently pointing or traveling to the right.
I had that on a combi in a kitchen once. With a bit of careful plumbing it was made to look quite sensible!
Posted by: @iantelescopeFrom experience, Neat & Tidy is easier to maintain.
Agreed!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I do not understand your suggestion that increasing the Thermostat demand Temperature will have any affect upon the Thermostat Pulse rate, PRF.
A typical graph of Power is shown in :
Where the Cycle time is here 10 minutes:
OR
Where the Cycle time is here 20 minutes.
Notice that the Time between Pulses is fixed by the Thermostat Cycle Time , either 10 or 20 minutes.
The Thermostat Cycle Time is set by the user from a selection of 3 or 6 or 12 cycles per hour.
The Room Temperature is transmitted by the Thermostat by varying the Run Time.
If the Room Temperature increases the Thermostat will reduce the Run Time.
If the Room Temperature reduces the Thermostat will increase the Run Time.
The changes in Run Time are shown here :
The Time between Run Pulses , the Cycle Time is constant.
Therefore, the continual ON / OFF Switching , initially , and wrongly , thought to be "Short Cycling " will NOT be altered by increasing the Thermostat Temperature.
The Excessive Motor Wear will continue independent of Room Temperature.
Apologies in advance ,I may very well be wrong !
I am assuming that the thermostat is trying to simulate proportional control by on off switching (it can't do true proportional control). The purpose of this is to avoid overshoot.
So if the actual temperature is far from the target temperature (by which I mean the temperature to which the thermostat is set, not your actual target room temperature) it will presumably switch on full time, otherwise the effect would be unnecessarily to slow down the approach to the target temperature. Only when the actual temperature gets close (within the 'proportional band') to the target temperature would I expect it to invoke cycling.
This is a known control approach when true proportional control is not available. I actually experienced this in a chlorine dosing controller for a swimming pool. The pump was capable of being on or off but the controller simulated proportional control by the same means as your thermostat appears to do. However once the actual departed from the target by a set amount it reverted to always on.
So assuming your thermostat does the same (we don't know but I can't see a logical alternative) setting the thermostat to well above the actual desired room temp will prevent the cycling.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Just add - I don't believe your cycling is anything to do your thermostat, I believe it's a red herring.
Your current flow path of water from the heat pump is 2 port valve, buffer then HEX and back to the ASHP. The issue, which I believe is going on, is the pressure drop across the HEX is higher than the buffer. So water (or most of it) just takes a short cut and bypasses through buffer straight back to the ASHP. So your return temp goes up too quickly and the heat pump just shuts down.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 96 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Thanks and apologies if I was a bit lazy...I have not p...
By Batpred , 3 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@plasfron Hi there! Yes your Mitsubishi heat pump needs...
By HCas , 6 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
The recent ZeroDisrupt discussions reminded me to take ...
By Mars , 6 hours ago
-
RE: What is the Heat Geek Guarantee?
@colinc, that’s a very fair and well-balanced comment, ...
By Mars , 6 hours ago
-
@toodles Thanks. I will assume they have made som...
By Papahuhu , 7 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Oh come on, that's a ridiculous argument by an installe...
By JamesPa , 7 hours ago
-
RE: Say hello and introduce yourself
I've seen photos of other people placing the tank in a ...
By Transparent , 8 hours ago
-
RE: PV Panels on roof in Conservation Area
@colinc Do your own due diligence re reviews etc but...
By Morgan , 8 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
So true, possibly with the exception of people you woul...
By JamesPa , 9 hours ago
-
RE: Isolating the system for a planned power cut
I hadn't realised your reason for a 100mA trip was due ...
By Transparent , 9 hours ago
-
RE: Midea ASHP – how to set weather compensation
Some things worth mentioning: (1) the Headroom Heat P...
By cathodeRay , 10 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
@9jwr9 I didn't get an answer at the time and there has...
By Pipcart , 10 hours ago
-
RE: Battery storage to run Heat Pump.
@majordennisbloodnok I’m not sure you will be able to r...
By Toodles , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
You've completely missed the point. Old, unpatched so...
By Majordennisbloodnok , 11 hours ago
-
RE: Ecodan Energy Monitoring Pack
@batpred that’s an idea yes. Will look into it
By Carpenterstation , 11 hours ago
-
-
PUHZ SW120Y & EHSC-VM2D - Buffer tank to Volumiser
Eventually I was able to find someone here in the Algar...
By DavidAlgarve , 11 hours ago
-
RE: Anyone still weathering it out with Agile?
We are still on agile and it works ok'ish to charge the...
By Batpred , 12 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah... now I can see a photo,and that changes the advice...
By Transparent , 14 hours ago