No problem, Libre office can import and export pdf so we will work with thatPosted by: @iantelescope@johnmo
Sorry @johnmo , The Renewable Hub cannot accept many standard Linux format files.
I can usually translate them into Jpg ,Pdf et al , but often not .
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamesPa Should I talk to my Plumber , holding Off until late next week ?
The Buffer Tank , originally installed "to reduce , or stop Short Cycling " was later installed "to reduce or prevent Heat Pump fin icing ". ( Samsung-Dalliium - Engineer )
The Heat Exchanger was installed , by Telford, to "protect the Heat Pump from the user accidentally stopping water flow in the Radiator circuit".
A single water circuit would expose the Heat Pump to potential Water flow failure. (Telford -Engineer)
Posted by: @iantelescope@jamesPa Should I talk to my Plumber , holding Off until late next week ?
Yes
Posted by: @iantelescopeThe Buffer Tank , originally installed "to reduce , or stop Short Cycling " was later installed "to reduce or prevent Heat Pump fin icing ". ( Samsung-Dalliium - Engineer )
Most likely we will suggest it is retained, but replumbed as a two port volumiser in the return, for the purpose of assisting de-icing.
Posted by: @iantelescopeThe Heat Exchanger was installed , by Telford, to "protect the Heat Pump from the user accidentally stopping water flow in the Radiator circuit".
A single water circuit would expose the Heat Pump to potential Water flow failure. (Telford -Engineer)
This is muddle-headed out of date thinking. Heat pumps must be run with most of the system in circuit, controlled by the weather compensation (water law) curve not on/off thermostats or TRVs. So the user wont/cant/shouldn't do this. The heat exchanger reduces efficiency and effectiveness, in your case because of the parallel buffer tank very likely very significantly..
The people mentioned above are conversing in the background and we will have something for you in the next couple of days. Basically your plan is correct, there may be a few tweaks,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Plumber:
Many thanks for your advice , it is appreciated, I will try and stop the Plumber until late next week.
Heat Exchanger:
The visiting French Samsung Engineer and the NIC engineer described, and defended, the Heat Exchanger as a hydraulic barrier allowing heat to be transferred but not water.
The Heat exchanger apparently "allows for different water, and different flow rates on both Water circuits".
The French Engineer later describing the Heat Exchanger as a "hydraulic isolator" .
Potable Water ??
Some plate heat Exchanger manufacturers have been using Cheaper Stainless Steel on the assumption that the water is "potable"? ( Seigenthaler , Hydronic Heating systems )
What is potable Water ?
My EAC Heat exchanger was manufactured in Alamabad, India ......................without instruction manual.
Many thanks for your advice !
Potable water is fit for human consumption, drinking, cooking etc.
Many thanks derek ...............my Heat Pump output pipe water is definitely NOT fit for human consumption being Black , or dark green !
@iantelescope I attach a proposed revised system diagram and list of tasks/SoW that @derek-m, @johnmo and I suggest, with special thanks to @johnmo who did most of the diagram This assumes that you are now retaining a cylinder not converting to thermino.
Some of the tuning in the list of tasks will be best done by you over a period of time, eg of WC curve and whether to use timed (batch) heating either end of the season to reduce the inevitable cycling which will occur when the demand is low.
Please feel free to ask any questions/discuss anything in the diagram or on the list.
Hope this helps
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many thanks @johnmo , @jamesPa and @derek-m
Your help is invaluable!
Your rebuild of my Heat Pump is identical to my own thoughts with a couple of reservations.
Buffer
A buffer in series with the return , although simple on a circuit diagram, involves pipes physically performing U turns , the Buffer being currently positioned to the left of the Water Tank with the pipes currently pointing or traveling to the right.
I suggested to my Plumber that we remove the entire birds nest of pipes replacing with parallel pipework attached to the kitchen walls. Costly , time consuming , but neat and tidy !. From experience, Neat & Tidy is easier to maintain.
I would like to fit valves on either side of the Buffer with a third valve Shorting the Buffer. This to allow cleaning and reduction in the inevitable Energy losses during Summer. During Spring and autumn the Buffer would be used to reduce short cycling, during winter the buffer would be used to protect against icing .
Again, many thanks .
ian
Posted by: @iantelescopeI would like to fit valves on either side of the Buffer with a third valve Shorting the Buffer. This to allow cleaning and reduction in the inevitable Energy losses during Summer. During Spring and autumn the Buffer would be used to reduce short cycling, during winter the buffer would be used to protect against icing .
The valves will also enable you to determine if it's actually needed!
Posted by: @iantelescopeA buffer in series with the return , athough simple on a circuit diagram, involves pipes physically performing U turns , the Buffer being currently positioned to the left of the Water Tank with the pipes currently pointing or traveling to the right.
I had that on a combi in a kitchen once. With a bit of careful plumbing it was made to look quite sensible!
Posted by: @iantelescopeFrom experience, Neat & Tidy is easier to maintain.
Agreed!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I do not understand your suggestion that increasing the Thermostat demand Temperature will have any affect upon the Thermostat Pulse rate, PRF.
A typical graph of Power is shown in :
Where the Cycle time is here 10 minutes:
OR
Where the Cycle time is here 20 minutes.
Notice that the Time between Pulses is fixed by the Thermostat Cycle Time , either 10 or 20 minutes.
The Thermostat Cycle Time is set by the user from a selection of 3 or 6 or 12 cycles per hour.
The Room Temperature is transmitted by the Thermostat by varying the Run Time.
If the Room Temperature increases the Thermostat will reduce the Run Time.
If the Room Temperature reduces the Thermostat will increase the Run Time.
The changes in Run Time are shown here :
The Time between Run Pulses , the Cycle Time is constant.
Therefore, the continual ON / OFF Switching , initially , and wrongly , thought to be "Short Cycling " will NOT be altered by increasing the Thermostat Temperature.
The Excessive Motor Wear will continue independent of Room Temperature.
Apologies in advance ,I may very well be wrong !
I am assuming that the thermostat is trying to simulate proportional control by on off switching (it can't do true proportional control). The purpose of this is to avoid overshoot.
So if the actual temperature is far from the target temperature (by which I mean the temperature to which the thermostat is set, not your actual target room temperature) it will presumably switch on full time, otherwise the effect would be unnecessarily to slow down the approach to the target temperature. Only when the actual temperature gets close (within the 'proportional band') to the target temperature would I expect it to invoke cycling.
This is a known control approach when true proportional control is not available. I actually experienced this in a chlorine dosing controller for a swimming pool. The pump was capable of being on or off but the controller simulated proportional control by the same means as your thermostat appears to do. However once the actual departed from the target by a set amount it reverted to always on.
So assuming your thermostat does the same (we don't know but I can't see a logical alternative) setting the thermostat to well above the actual desired room temp will prevent the cycling.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Just add - I don't believe your cycling is anything to do your thermostat, I believe it's a red herring.
Your current flow path of water from the heat pump is 2 port valve, buffer then HEX and back to the ASHP. The issue, which I believe is going on, is the pressure drop across the HEX is higher than the buffer. So water (or most of it) just takes a short cut and bypasses through buffer straight back to the ASHP. So your return temp goes up too quickly and the heat pump just shuts down.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 43 Online
- 3,354 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
510kWh of solar PV from my 4kW Hyundai panels and SMA S...
By JulianC , 7 hours ago
-
RE: Is my Samsung heat pump working too well?
Thats in itself is interesting. I have a Vaillant heat...
By JamesPa , 8 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent Not a swell season then ☹️
By Toodles , 11 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 1 day ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 1 day ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 1 day ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 2 days ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 2 days ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 3 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 3 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 4 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 4 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 5 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 5 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 5 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 5 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 6 days ago