Posted by: @iantelescopeThermino
From reports on Buildhub, good product in theory, but let down by poor product implementation and poor customer service. Return to base if this go wrong and they tend to. Expensive solution to store heat compared to water.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @iantelescopeThe proposal is that my Hot water tank be replaced with an "Thermino" Heat Battery
Heat batteries do not have the best temperature gradient to be heated efficiently by an ASHP, because the melt temperature of the fill material is around 60 degs. So heat pump runs flat giving a rubbish CoP.
All electric ones is just like heating a cylinder with the installed immersion. So why rip out a cylinder and replace with a heat battery.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Thread is a little long to sit and read it all. Does your cylinder have an immersion?
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @iantelescopeThermino ?? Advice , Experience ??
Given my two year long Heat Pump Fiasco I was very surprised to get a proposal to fit a "Thermino" Heat Battery.
The proposal is that my Hot water tank be replaced with an "Thermino" Heat Battery.
The "Thermino" , unlike my current Hot water tank is supplied with Electrical Energy from either the Off peak Mains OR a Solar panel array fitted to my roof.
The Cost of removing, replacing and simplifying my current Heat pump would be another £5.3k .
The Cost of the Roof Solar panels would vary between £7.5 k and £12k .
Does anyone know anything about Thermino ??
Invented by Joseph Black in Edinburgh in the eighteenth century this seems too good to be true!
Any advice anybody??
In answer to the question has anyone got any advice, I have and it's don't
Over a period of years you have been offered free and largely consistent advice by people with no vested interest in selling you anything, just a desire to help. Unfortunately you have not wished to follow it, which is of course your perogative.
However, given this, it's a mystery why you would even consider the 'advice' of another salesman given the track record of the salesmen you have so far encountered. However that is also your perogative.
I'm sorry if this seems harsh but you have asked for advice and this is mine.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many thanks for your quick replies.
The Proposal is to GREATLY SIMPLIFY the SAMSUNG-TELFORD by removing :
1) The unwanted, and unnecessary Heat Ex changer.
2) The unwanted and unnecessary Buffer tank.
3) The unnecessary Second motor.
4) The unnecessary third water expansion tank ,PRV, and second Magnetic clean filter.
5) Removing and replacing the 200 l Water tank , replacing with a Thermino Fed from Solar panels Or Off Peak Electricity NOT a Heat pump!
These changes would correspond to the advice, frequently, and often assertively , if not aggressively given, on this , and other sites.
Why would I consider installing a Thermino ?
Have a look at the state of my Kitchen with the current Samsung Telford Heat Pump .......
The idea of replacing the Heat Pump Hot Water supply with an supply from a Solar panel array OR from Off Peak electricity, is , at the very least aesthetically attractive.
At 76 , I lack the experience and confidence to do the work myself !
I repeat again , the idea is to remove the Large 200 liter water tank, fed from the Heat Pump, and replace with another Sustainable energy source, Solar Roof panels and or OFF Peak electricity from Octopus Cosy!
Remember, I have already paid out circa £14000 for this mess .....a further £5.3 k for the work on the Heat pump would raise the cost to circa £20000 !!
And that without the £7.5 k Solar panel costing!!
I would be exposed to a £27 K Debt for a Heat Pump worth perhaps £5k!
Posted by: @iantelescopeThe Proposal is to GREATLY SIMPLIFY the SAMSUNG-TELFORD by removing :
1) The unwanted, and unnecessary Heat Ex changer.
2) The unwanted and unnecessary Buffer tank.
3) The unnecessary Second motor.
4) The unnecessary third water expansion tank ,PRV, and second Magnetic clean filter.
5) Removing and replacing the 200 l Water tank , replacing with a Thermino Fed from Solar panels Or Off Peak Electricity NOT a Heat p[ump!
Noticed from your photos the immersion isn't in the best place to heat the contents of cylinder. But that can easily be fixed.
1. Yes
2. Yes
3. Yes
4. Yes
5. No or not quite.
Keep cylinder and reuse. Immersion not ideal location, but you can add a Willis heater (£50). This is installed between the cold water inlet and the hot water outlet (drinking water). No pumps required just a ball valve either side for maintenance.
Then if you have solar, a diverter to power first the cylinder immersion and second the Willis. If you don't have solar either charge the cylinder off peak using the Willis. Or if no off peak a smart self learning immersion thermostat.
Or if you want rid of the cylinder and want super simple. No expansion vessels or safety grip required. Basically works exactly the same as the phase change store you asked about, but uses water and a coil were your hot water passes through.
https://www.plumbnation.co.uk/harlequin-heatstream-electric-150l-direct-mains-hot-water-system-64-4938 h sized to suit your house.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Who is suggesting that you should remove your hot water cylinder and replace it with a Thermino?
If you can afford the solar PV system, then I would suggest that you also have a power diverter installed to generate hot water using the immersion heater. From Spring through to Autumn you should get the vast majority of your hot water totally free from solar PV, during Winter this would be supplemented by the heat pump.
While your system is far from perfect, the recent improvements relating to the thermostat, and isolating the buffer tank, should give more reliable and efficient operation come the heating season.
It may also be possible to further improve efficiency by optimising the heat pump controller settings.
Many thanks Derek and John .........your questions are accurate, unassertive , and appreciated.
My neighbor has installed a, seemingly very efficient Solar panel array, resulting in an 80 % reduction in his summer Energy consumption.
On asking for quotes from local Solar installers to install a similar system , I received several offers for the installation of a similar Solar panel array.
One of these Solar installers, said that outwith the Solar panel installation "he could fix my Heat Pump and remove the monstrous 200 litre Hot water tank simultaneously removing the unnecessary Buffer tank , Second motor , Expansion tank, Heat ex-changer". He would install a "Thermino".
Your excellent idea , much appreciated by the way, of connecting the Solar array to the tank immerser was not presented.
Who to trust?
I am Not a plumber , nor am I Heating engineer , and do not have the experience, or confidence, to repair , or replace this Heat Pump.
@johnmo Again ,excellent advice . My only question ....who do I trust to do the work??
If it was me I would get a scope of work clearly understood by yourself for the plumbing side. Write it down A, B, C... then find a local plumber you know or find a recommended one from family or friends, get them to price the job.
Split the heating system away from solar - do as different jobs.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Many thanks @jamespa & @johnmo & @derek-m
I will generate a list of plumbing operations for the rebuild of my Heat Pump as you suggest @johnmo , only then getting a local plumber to perform!
I will then get the company who installed my neighbors Solar panel array to install a similar array on my own roof! Nothing like seeing a previous working example.
Finally, I will connect the Solar panel to a suitable Immerser on the Hot water tank or , as you suggest, on to an inline water heater.
Again I did not know about these inline external Water heaters many thanks.
The Heat pump should look a wee bit less awful!
Posted by: @iantelescopesuitable Immerser
You can get a decent one from Cool Energy, it can drive two immersions on a cascade, once one heated it moves to the next one.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 22 Forums
- 2,070 Topics
- 45.3 K Posts
- 27 Online
- 3,343 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat pump installation and BUS Grant timings
@johnmo Hi, looks like i might be getting the schemes...
By StuChi , 2 hours ago
-
RE: Home energy storage & battery register
I totally agree that self install is certainly going to...
By Abernyte , 3 hours ago
-
Check the detailed specs. 7kW Vaillant is actually 8kW...
By JamesPa , 4 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent ‘Protein’s extra Luv’.
By Toodles , 5 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnnyb I was on Smart, mostly because I was on Agile ...
By Arundalep , 18 hours ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 24 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@johnmo You are correct, standard Ethylene glycol used ...
By Brendon Uys , 1 day ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 1 day ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 1 day ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 2 days ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 2 days ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 2 days ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 3 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 3 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 4 days ago