@derek-m & technogeek
Question:
How do I measure Electrical Signals and integrate them with Temperature Sensors ?
Your comment that "It is unclear what your charts are measuring or designed to show." demonstrates the problem that has been apparent from the beginning.
Measurement problems:
I can easily measure, and store , water Temperatures at any given time.
I have many DS18B20 's , K type pipe Clamp Temperature sensors and a Sharky " In Water power" meter.
I also have flow meters but cannot integrate the flow measurements Signals with Temperature measurements!
In general , I have no method of measuring Electrical signals , for example Motor relays , Water flow Sensors and integrate them with the temperature sensors.
Fast Signals . eg PWM I can measure , and store in an Oscilloscope but cannot integrate these Files with the Slow Temperature Signals.
Question 1:
How do I measure Electrical Signals and integrate them with Temperature Sensors ?
Oscilloscopes have a completely different Timebase compared to Temperature Sensors.
Question 2:
How do I correlate Relays and motors with Temperature Sensors?
Warning: Only perform tests and work on your equipment for which you have been adequately trained and you are deemed competent. Follow all necessary safety procedures.
What Arduino equipment do you have?
Whether a water pump is running or not is a binary state, so could be measured by a digital input on a monitoring device. One way to infer that a water pump is operational would be to monitor the power supply to its motor, but most monitoring equipment would not be capable of accepting a 240v ac input. It would therefore be necessary to use an interposing relay, to separate the 240v ac from a probable low voltage dc signal. A relay with a 240v ac coil connected across the power supply to the water pump would be energised at the same time as the pump. The contacts of the relay could then be used to switch a low voltage dc signal to the monitoring equipment.
An alternative would be to use a flow switch, which again could be used to switch a low voltage dc signal.
The use of temperature sensors at different locations can also be used to infer that water flow is taking place.
Monitoring AC mains Motors , Relays and Actuator valves on Samsung Heat Pumps.
I have reluctantly, because of cost, decided to buy a pair of Oscilloscope Current , CT probes.
Outwith Oscilloscope use ,these can easily, and safely, be connected to another Arduino dumping data to either a PC or a SD Card.
My Pipe Water Temperature Measurements:
1: In Water Temperature Measurement:
Water Temperatures are most accurately measured using the in Water Power Meters.
The In Water Power meter accurately measures the Water Temperature.
2: K Type Clamp pipe Temperature Measurements:
Water Temperatures can be approximately measured using K type thermocouples mounted on K type pipe clamps.
The K Types Clamps being easily moved to different locations.
All Thermocouples, suffer from offsets, drift and signal noise.
The Thermocouples here measure ONLY the Temperature of the copper pipe, Not the Water within the pipe.
3: DS18B20 Digital Sensors:
Water Temperatures can be approximately measured using DS18B20 digital sensors fitted externally to the pipes.
The DS18B20 Sensors provide a fast serial Digital Temperature Measurement easily accessible from Arduino Micros.
The DS18B20 here measures ONLY the Temperature of the copper pipe, Not the Water within the pipe.
Pipe Water Flow rates:
1: In Water Power Meter:
The In Water Power meters provide a accurate measurement of Water Flow Rates using Ultrasonic in -Water Sensors.
@derek-m @technogeek @Mars
When is a Thermostat NOT a Thermostat ?
Can my "Honeywell "Home Thermostat be called a Thermostat?
Thermostat , implies a Binary ON-OFF Switch , when my Honeywell is actually a Pulse Width Modulated Signal Temperature transmitted as a "Run Time" variable pulse width on a fixed Cycle Time?
A binary state device it is NOT!
What Temperature Sensor or Thermostat Should I use ?
Given my recent discovery that my Thermostat has been the source of my " Short Cycling" what Thermostat would be an appropriate Replacement?
My Current Honeywell "Home" Thermostat is in fact a kind of Pulse Width Modulated, PWM device .
The Honeywell "Home" runs on a CONSTANT Cycle Time with each Cycle staring with a Variable Pulse Width Run Time.
Ironically, This Thermostat appears to be designed to fix cycle times thus countering the effects of variable cycling!
The primary task of a room thermostat in a heat pump system is to limit over temperature due to solar gain or human activity. A 'smart' thermostat may therefore not be appropriate for this purpose, a basic on/off type being the preferred option.
Actual IAT control should be performed by the heat pump controller.
Posted by: @iantelescopeWhat Temperature Sensor or Thermostat Should I use ?
Can you not use the Samsung wired remote controller as your thermostat? If you need to move its location, it is just a question of running a length of two core wire to the new location. My controller was moved from an outside porch to an internal room and has replaced my 3rd party thermostat very successfully. If you don't want to do that I would recommend an ESRTP4RF+ thermostat made by ESIcontrols.
Posted by: @mike-hPosted by: @iantelescopeWhat Temperature Sensor or Thermostat Should I use ?
Can you not use the Samsung wired remote controller as your thermostat? If you need to move its location, it is just a question of running a length of two core wire to the new location. My controller was moved from an outside porch to an internal room and has replaced my 3rd party thermostat very successfully. If you don't want to do that I would recommend an ESRTP4RF+ thermostat made by ESIcontrols.
It would appear that the suggested ESI Controls thermostat operates in the same manner as the present Honeywell thermostat, so may not provide any form of improvement.
A heat pump system operates better with just a basic on/off type thermostat.
Posted by: @derek-mIt would appear that the suggested ESI Controls thermostat operates in the same manner as the present Honeywell thermostat, so may not provide any form of improvement.
This was not my experience. It operated purely as an on off thermostat. I believe that with additional wiring, it does have additional functionality, which is probably what you are referring to. However with the basic wiring it is just an on off thermostat.
Posted by: @mike-hPosted by: @derek-mIt would appear that the suggested ESI Controls thermostat operates in the same manner as the present Honeywell thermostat, so may not provide any form of improvement.
This was not my experience. It operated purely as an on off thermostat. I believe that with additional wiring, it does have additional functionality, which is probably what you are referring to. However with the basic wiring it is just an on off thermostat.
I would suggest that you read section 1.3 What is Chronoproportional Control (TPI)?
This states that the thermostat 'TPI increase
boiler efficiency by firing the boiler at regular intervals,
adjusting firing duration with demand'.
Posted by: @derek-mI would suggest that you read section 1.3 What is Chronoproportional Control (TPI)?
This states that the thermostat 'TPI increase
boiler efficiency by firing the boiler at regular intervals,
adjusting firing duration with demand'.
Er isn't that just like any thermostat, but with a (possibly synthesised) small hysteresis. Why does having a shorter cycle time make a boiler more efficient?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @derek-mI would suggest that you read section 1.3 What is Chronoproportional Control (TPI)?
This states that the thermostat 'TPI increase
boiler efficiency by firing the boiler at regular intervals,
adjusting firing duration with demand'.
Er isn't that just like any thermostat, but with a (possibly synthesised) small hysteresis. Why does having a shorter cycle time make a boiler more efficient?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @derek-mI would suggest that you read section 1.3 What is Chronoproportional Control (TPI)?
This states that the thermostat 'TPI increase
boiler efficiency by firing the boiler at regular intervals,
adjusting firing duration with demand'.Er isn't that just like any thermostat, but with a (possibly synthesised) small hysteresis. Why does having a shorter cycle time make a boiler more efficient?
You may be correct James. I suppose it depends what is meant by 'firing the boiler at regular intervals', is this every 20 minutes, but varying the on period during that 20 minutes?
I have just noticed further down that section 'This thermostat has the option of standard setting or TPI' so it would appear that it can be used in basic on/off mode. Mea Culpa. 🙄
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 178 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@kevh with the Cosy 6 I know it definitely goes to arou...
By HarrisonC , 6 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay yes I am familiar with SQL. Interesting num...
By RobS , 7 hours ago
-
Parsnip, Bacon & Coconut Milk Soup
First let me say, I am only a cook because I am human a...
By Toodles , 7 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@weoleyric Oh Dear, I don’t think I am going to be of m...
By Toodles , 8 hours ago
-
RE: Electricity price predictions
Ben Watts posted on LinkedIn that he had updated this w...
By Judith , 13 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Small update, Emailed and Spoke to Midea UK and they ...
By Burtis , 13 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash Octopus does charge for the admin. The process al...
By Batpred , 13 hours ago
-
RE: External pipework insulation
@transparent HI all The products you mention are ver...
By David Smith , 13 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Issues still under investigation by Solis... Fogstar ...
By Batpred , 14 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I agree, the consumer is not being properly represented...
By Batpred , 14 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 1 day ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 1 day ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 1 day ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 2 days ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 2 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 3 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 3 days ago