@editor Hi Mars, he is a sole trader who has installed a system at a neighbours property including my own. As he is a sole trader I will forward details to him and if he wants to promote his business on this site (via yourself) then he can take it further 🙂
All I need now is the price of electricity to come down and things will be peachy! 🤣 🤣
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
" A heat Pump OR an Oscillator ?"
" Four Pipe Buffer Tanks OR Volumisers"
My Heat Pump continues to Oscillate or "Short Cycle " :
Taking the advice from Samsung, DECC , Kensa and the MCS to fit a "50 litre Buffer Tank " :
My "Installer " fitted a 50 Litre Buffer Tank in October 2022.
The 50 Litre Buffer tank was fitted with a Valve to experimentally limit Energy Consumption .
When selected the Buffer makes a very limited change to the oscillations.
I have now found that the 4 pipe Buffer Tank water Temperature differs from the Temperature of the water in the Buffer Connecting pipe:
Clearly, the Buffer Water Temperature SHOULD be the INTEGRAL of the TEMPERATURE at the Buffer Input PORT.
It Clearly is NOT the Integral of the Water Temperature.
The Conclusion is that my Heat Pump has been fitted with a 4 pipe Buffer instead of a Volumiser!
A second conclusion is that the Volumiser SHOULD HAVE BEEN FITTED ACROSS THE OUTPUT PORTS OF THE HEAT PUMP!
My Heat Pump NEEDS a TWO PORT VOLUMISER OF 50 litre capacity fitted across the Heat Pump Output ports to Reduce these Violent Oscillations.
Given that my Oscillator Heat Pump has already cost ~£14K I have No confidence in my "installers" or the "Experts".
" Short Cycling", Thermal-Syphoning
My Heat Pump displays "Short Cycling":
The Standard Solution to "Short Cycling is the use of a Buffer Tank :
My Buffer tank appears to provide no solution to the Cycling Problem:
The graph showing the Temperature Difference between my Buffer feed pipe and the Buffer Water Temperature itself!,
with DS18B20 Temperature Sensors being used to measure Water Temperature in the Buffer Tank and the Buffer Tank feed pipe.
Notice the Buffer Water Temperature going Negative with respect to the Radiator Feed Temperature!
The Buffer appears to be dumping it's Heat Energy when the Heat Pump switches OFF
This effect , Thermal-Syphoning is shown at
https://blog.heatspring.com/2-pipe-versus-4-pipe-buffer-tank-configurations/
with the solution to "short Cycling" being the introduction of Thermal Swing Check-Valves or Spring loaded Check-Valves.
When the Heat Pump is warmer than the Buffer the Check valve is OPEN , when, however the Buffer Tank is Hotter than the Heat Pump the Valve closes.
The Thermal efficiency should be improved with the introduction of "Swing Check Valves between the buffer and the Heat Pump and Spring loaded Check valves between the Buffer and the load.
Two Port OR Four Port Tanks?
Two Port Buffer Tanks are used extensively in Europe while the USA prefers the use of Four Port Buffer Tanks.
"Black Pipe Water "?
Both TWO PORT & Four Port Buffer Tanks store Black Particulates on to the floor of the Buffer tank, requiring removal by pressure cleaning.
The Short Cycling itself tends to exacerbate the "Black Ink" Problem as shown in the BS7593:2019 .
Quite some time ago it was pointed out that because your system has a buffer tank and a plate heat exchanger, that it could not work efficiently.
Since you ignored the advice provided at the time, your system will continue to work inefficiently and short cycle until you resolve these problems. I'm afraid continually posting on the forum will not resolve these problems.
Attacking other "experts" Does NOT inspire confidence!
Heat Pump Thermal-Syphoning
My Samsung 5kW Heat Pump , now in it's second Spring Season of "Short Cycling" shows every sign of destroying itself!
With Spring Weather my Heat Pump, like many others, cannot reduce it's power below it's minimum Inverter power of 2.5 Kw, and oscillates :
My Samsung 5kw Heat Pump is inefficient with a current loss of 26% of Energy:
The NIC having STRUCK_OFF my "Installer" now says that " You are NOT GOING to like this ............but Nothing CAN be DONE!!"
The Heat Pump , fitted with a 50 Litre Buffer , continues to exhibit "Thermal-Syphoning " :
with a negative -10/-15 C Temperature Drop between the Buffer output Pipe and the Buffer Water Temperature itself!
This is Thermal -Syphoning, the dumping of energy stored within the Buffer back into the Heat Pump itself.
This Thermal -Syphoning is used by the Heat Pump during de-icing.
The Buffer was originally to be fitted by SAMSUNG-DALLIAM to fix another problem ............. DE-icing !!
Having Spent circa £14K on the Heat Pump I have neither confidence nor money!
Many "engineers" and "experts" have now inspected my Heat Pump .......but none have inspired confidence!
Many "experts" have voiced their opinions , usually completely contrary to each other!
Attacking other "experts" Does NOT inspire confidence!
@derek-m @iantelescope @editor
I am probably making a mistake wading into this but...
Sometimes in life bad things happen, its a fact.
In this case it appears that @iantelescope has a bad experience with his heat pump. As the 'victim' of bad things one has a choice. Accept it, however unfortunate, and try to do something about it (if necessary trying several things until one of them works), or forever suffer from it.
The former has the distinct advantage that you regain some level of control and hope, the latter cedes all control and hope to others (or nobody if there is nobody who cares). Obviously there are times when the former is literally impossible, such as if the bad thing is fatal, but some poor building work is unlikely to be one of those times. In this particular case I would argue that the way out (if there is a way out), is to accept it and try to do something about it.
The options involving 'the industry' stepping in, admitting responsibility, and fixing it seem (sadly) to have been exhausted. That's a pity, but appears to be a fact. Fortunately there are communities of people, who have no vested interest, yet are willing to offer advice. Furthermore, unlike many 'experts' in the industry, they are willing to explain their reasoning. This is important because it exposes their suggestions to peer review, and allows you to judge what you do believe and what you don't.
This being the case the only remaining 'do something' option appears to be to try what the community has suggested and peer-reviewed. If this is, for any reason not acceptable, then 'forever suffering from it' appears to be the inevitable result. Put simply, if you don't change something then nothing will change.
If I were in the position that @iantelescope is in, then I think I would listen to the community, on the grounds that the alternative appears to be too depressing to contemplate. I have done this many times with software that doesn't perform as one might expect it to do (I admit its a lesser problem, but the same principle).
Of course its entirely a personal choice how to proceed. However, if doing nothing is the direction of choice, then it is perhaps a bit unfair on the community who is trying to help not (a) to declare that the intent is to do nothing, so that the community knows that offering suggestions is pointless and (b) to continue raising the issue when there are many other problems that the community is trying to solve and where action might actually occur.
I acknowledge that the above is, in essence, a long winded way of saying what @derek-m said above, but perhaps it explains some of the thought processes that are going through my head in relation to this knotty problem.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I must apologise to yourself for my Scottish Scepticism.
Many thanks James, Believe me when I say I Appreciate your response .
Some of the Correspondents on this site seem intent on derision , merely generating paranoia by their Very tone..........very Twitter or "X " like !
My last confrontation with my , now former "installer " and an Engineer from the NIC finished with the "Experts" leaving with my Heat Pump completely inoperative, issuing numerous Warnings . I later successfully undid the "experts" settings.
My previous confrontation was with a French SAMSUNG Engineer who left, later producing a "secret" Report only shown to my then "installer".
The "Secret Report" was briefly shown before being spirited away by my "installer " literally when my back was turned!
Apparently you cannot have the customer understanding his Heat Pump problems!
These confrontations follow a sequence of "discoveries " where my "installer" failed to install a Flow Switch (Four times!) ,Expansion vessel , PRV , Thermostat and Buffer .........on and on. Confidence in "my Installer" , SAMSUNG-DALLIAM and NIC Completely destroyed!
Two years of this have completely destroyed any confidence in this industry ...........However, I must apologise to yourself for my Scottish Scepticism.
My final plea is for some appreciation of the statement from the NIC :
" You are NOT Going to like This ........................................But Nothing Can be Done for your Heat Pump!".
This statement follows many previous Verbal statements from the NIC that :
" If All else fails ...........the NIC will repair and Replace the Heat Pump!".
As a matter of interest have a look at the presentation in the Book :
Modern Hydronic Heating & Cooling by John Siegenthaler
This is How to teach about Heat Pumps . Loads of Diagrams Heat equations , numbers , confidence.
Posted by: @iantelescopeApparently you cannot have the customer understanding his Heat Pump problems!
That attitude isn't unique to heat pumps, many tradesmen exhibit it. The number of times I have either been told that it's 'complex' or simply given a load of BS, is too large to count.
It makes my blood boil. Internally my reaction is always the same - if you can't explain it to me, then obviously you don't actually understand it. Sometimes I will say this out loud, most often I will just tell them to go away. The people who actually understand things can explain them to any reasonably intelligent person, the rest are just chancers.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa When I had the heat pump installed and later, when a second Powerwall was added to the existing setup by the the same teams, I frequently came across comments relating to my desire to know the technical details. One said to me; ‘I’m not trying to be funny but we come across customers much younger than yourself who don’t have the technical understanding to ask the questions you have!’ I found that the leaders of the teams (both electrical and plumbing) were only too pleased to be asked about their installation work. I also spent a fair amount of time with the MD of the company discussing various aspects of the installation - he listened, he answered and where necessary made the changes I requested.
This is fine in a way but, what happens when a customer does not know enough about what is required and has little interest in doing so but wants to just ‘Leave it to the Experts’? They may be even less inclined to want to carry out any investigating to ensure their system is optimised for them. Yes a good installer should ensure that this is a satisfactory situation and the heating system will require minimal attention from the householder - it should just work … and work well.
I think that most readers of the RHH are similar to myself, and many like me will have had a good experience; there are unfortunately, others who have not. Again, if we are to believe the MCS blurb, we are all concerned unnecessarily!😉 Regards, Toodles. (Cloud Cuckoo Land costs extra Luv)
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Dropped into to a newly opened Energy Support Hub run by volunteers this morning to see what they had to offer. There was already someone in there bemoaning the performance of their heat pump. This is what they told me - as I asked.
Installed 3 years ago, replaced an old boiler that had failed - the house is not on the gas grid.
House F EPC rated, semi detached, 1920's solid brick.
Double glazed over 25 years ago 'but the curtains move when the wind blows'.
Rain comes under the front door.
Had not heard of weather compensation.
Does not know what the temperature flow is (or should be)
The rooms are all different temperatures - did not know what a TRV was or how it worked.
Was not on a heat pump tariff.
Did not have a set back temperature overnight
Had not had a commissioning handover
The company that installed it used subcontractors and no one took overall responsibility for performance
The electrician that did the wiring had never done a heat pump before.
It took 6 to 8 months for completion from day 1.
Therefore guess what? The house is cold and the running costs enormous.
Has now thought that getting a local specialist in to review the system 'might be a good thing.'
And one last thing - all done without out any grant.
Thought I'd share.
Interesting and says a lot about both the industry and the public.
Clearly this person, like many I suspect, takes little or no interest in(or doesn't understand/choose to be understand) heating systems of any kind. I suspect many are like that.
Clearly also they either take little interest in, or can't afford, insulation, or are renting so either see it as wasted money or aren't permitted to upgrade. I suspect many are in this position.
The installer didn't do a handover, but if the occupant isn't interested explaining it would be both impossible and pointless.
But as you imply there are several suspect factors in the installation.
I struggle to see how such a situation, which is likely very common, can be systematically resolved. Central heating systems are inherently quite complex and if people refuse even to understand a trv, how do you teach them to use them, particularly if there are inherent problems with the circumstances.
This isn't unique to heat pumps, the previous boiler would have suffered also but a heat pump possibly exacerbates an already poor situation.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaClearly this person, like many I suspect, takes little or no interest in(or doesn't understand/choose to be understand) heating systems of any kind. I suspect many are like that.
@jamespa sadly I have come across many a person like this and its frustrating. The same said people are also the ones who complain about the cost of living the loudest when for a small amount of invested time and money, they could improve the situation. For example, 5 years ago I renewed my loft insulation to 300mm at a material cost of £246 for a 5 bedroom house ( luckily I was able to do it myself and save even more ). Within 2 years it had paid for itself ( 3 - 4 years maybe for a contractor installation ) .
Sadly people like that complain they cannot afford it and carry on paying the extra £200 - £300 a year in energy bills, however on the next breath they are telling you they and the family are off for two weeks to Majorca for their holidays! Priorities I guess!
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 53 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 42 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 2 hours ago
-
What is the best strategy for operating a very oversized heat pump?
As the title really. There are at least three live thr...
By JamesPa , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 18 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 20 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 21 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago