@jamespa 

Hi James, nice to talk to you again.

Measuring the Temperatures of my heat exchanger ports?

I will indeed take your advice and install another pair of DS18B20 's to measure the Radiator facing ports of my Heat Pump.

Weather compensation Settings

I have extensively used the  Water law compensation.....

WL1 A

By Adding the Water Law Graph setting to the Water Law thermostat offset control on the Samsung I can , to some degree , control "Short Cycling".

With the Water -Law graph set to a pipe Water Temperature of 45 C | 47 C | 50 C when the outside temperature is -5 C | -6 C I can reduce the "short Cycling" by arranging the Heat Pump NOT to Cycle at All!

Stopping "short cycling" by stopping All cycling!.

Yes, I know it is not recommended , and is very inefficient and costly , but, stops the endless "Short Cycling".

I was asked by Telford , the tank manufacturer, to examine the pipe water only  to discover the costs of "short Cycling".

The MCS Article on Buffers and Volumisers gives the standard fix  for Short cycling as calculating and fitting a buffer tank .

Buffer sizing 11

but, gives a warning about the cost of "Short Cycling" and the potential efficiency costs of  Buffer tanks.

 

The Pipe Water was a jet black ink colour completely failing the BS7593:2019 Water quality test.

I had the pipes cleaned by a professional , at a cost of £600 only to discover that my "installer" had never cleaned, or tested, the pipe water under BS7593:2019 .

Samsung settings

I have recorded , and adjusted ,all of the 80 Controls within the Samsung, discovering that the Motor Pulse Width Modulators are faulty.

The Heat has been configured to use switch ON OFF Motor switching rather than PWM continuous control.

I have used an Arduino to supply and control BOTH PWM Motors from the Delta_T Temperatures across the Heat Exchanger primary ports.

The Temperatures are indeed increased slightly by reducing the Water flow rate using the PWM motors.

 

Again, many thanks for your advice .........it is appreciated.

 ian

 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@iantelescope

I would suggest that you have a read through the following post from page 13 onwards: https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/12kw-samsung-gen-6-short-cycling/paged/19#post-18238

The idea is to check that the short cycling is not due to incorrect controller settings before making any physical changes to the system and pipework.

This post was modified 1 year ago by Derek M

   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@iantelescope

Do you have any thermostats within your system? If so, what is the make and model.

It would be useful if you could post details of all the controllers internal parameters.


   
ReplyQuote



(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

With the Water -Law graph set to a pipe Water Temperature of 45 C | 47 C | 50 C when the outside temperature is -5 C | -6 C I can reduce the "short Cycling" by arranging the Heat Pump NOT to Cycle at All!

That's quite a high flow temp, what flow temp was the system designed for. 

Generally the starting point is to adjust WC as low as possible consistent with the house getting warm enough with trvs and thermostats fully on and the system operated 24*7.  Increasing the flow temp to reduce cycling is likely to decrease efficiency not improve it.  

My suspicion is that the flow is primarily through your low resistance buffer tank which short circuits your phe hence depriving the heating circuit of energy (which is why your system doesn't heat up as much as you need).  The recirculation alone will cause losses, exacerbated by the uninsulated pipes.  Because of this you are having to operate at a higher ft than is required by the emitters, further reducing efficiency.  Short cycling won't be helping but turning up the WC to eliminate it only leads to one-off control which isn't helping.   Together these would explain many of the symptoms you report.  

Please post the four temperatures from the phe so we can see how much damage that is doing and also the information @derek-m has asked for about the control systems.  

Most likely the right way forward is to replumb the buffer as a volumiser in the return, set all the external controls so they have effect only in extreme situations (eg solar gain) turn down the WC as far as you can, and maybe tweak the phe.  Then if necessary play with a couple of parameters other than the WC setting to control cycling.  However until we have the answers to the questions above we can't be sure.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@derek-m 

Hi Derek,

Have a look at the Samsung controls on my Heat Pump.

I have adjusted , and reset almost ALL of the settings in innumerable attempts at getting a compromise between stability, meaning reasonable Short Cycling and Efficiency , meaning reasonable Real COP. Be warned, this is NOT light reading!

The Thermostat , a Honeywell Home Thermostat was fitted some three weeks after the start of the "installation".

Again, I have adjusted , and reset the Thermostat to accommodate reasonable, and safe, living room heating conditions with cost and "Short ?Cycling".

My best "compromise" is

1) Start heat pump at 700  running until 0900 attempting, but never succeeding  to reach 21.5 C.

2) Reduce the temperature to 16C between 0900 and 1200.

3) Start heating at 1200 running until 1400.

4) Reduce room temperature to 16C between 1400 and 1700.

5) Start Heating at 1700 with an attempted  temperature of 21.5 C.

6) Reduce heating to 16 C between 000 and 0700 the following morning.

The thermostat has been programmed to mimic the Outward Settings of the Samsung Heat pump itself.

Balancing

I have attempted , without success, in balancing the living room Radiators against all the others.

I have resigned myself to only heating my living room with the Hot water Switched OFF.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa 

Hi James,

Again , many thanks for your patience.

Samsung Controls

I have attempted to "adjust" almost every Samsung control setting in my attempt at reconciling "short Cycling with COP".

 

The Buffer tank compromise

The Buffer tank, being , at my insistence , selectable  with a valve, makes very little ( 10%) difference to either the efficiency , or the stability ( absence of Short cycling ).

The Buffer tank , does , however, provide a provable protection against ice.!

During the winter I open the buffer valve to protect against frost.

Outwith Winter I have switched the Buffer tank OFF.

As an aside, I am NOT using Glycol on the outdoor water circuit , allowing the pipe water a higher Specific Heat.

 

Losses

The Heat Exchanger, the buffer tank  and the "pipework" are loosing ~ 22% of the Heat Pump generated Energy.

With the Hot water switched on the losses approach ~48%.

 

 

Adjustments

I have adjusted everything in an unsuccessful attempt at a compromise between Short Cycling  and Efficiency/Cost.

 

Measurements

After two years I now have a heat Pump covered in Sensors, but, still without explanation or progress.

 

 

ian

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@iantelescope

How many thermostats do you have and are they the type that switches on and off a set number of times each hour?

What is the temperature setting of the thermostats?


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

The Heat Exchanger, the buffer tank  and the "pipework" are loosing ~ 22% of the Heat Pump generated Energy.

I think that the recipe is fairly clear then

Insulate the pipework where you can

Remove the heat exchanger and secondary pump

Switch off the buffer tank

Turn up trvs and thermostat to max so they have no effect

Adjust WC (IE flow temp) to min poss to keep the house at the desired temp

Review the control settings

Then and only then start tweaking further

Before next winter replumb the buffer tank as an inline volumiser

 

Or

 

Leave it as it is in which case it will be as it is.

 

All subject of course to any comment @derek-m wishes to make.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@jamespa

Ian appears to have had problems for a couple of years, so rather than rush ahead I think that it is best to go through each item one step at a time. Craig1980 had similar short cycling problems that were being caused by incorrect settings within the controller, so that is one avenue to explore.

It is best not to try too many things at the same time. As Shakespeare stated "Many strokes, though with a little axe, hew down and felled the hardest timbered Oak".


   
ReplyQuote



Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

@derek-m Then dry out under a shelter for two years before using for the log fire.😊

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @derek-m

@jamespa

Ian appears to have had problems for a couple of years, so rather than rush ahead I think that it is best to go through each item one step at a time. Craig1980 had similar short cycling problems that were being caused by incorrect settings within the controller, so that is one avenue to explore.

It is best not to try too many things at the same time. As Shakespeare stated "Many strokes, though with a little axe, hew down and felled the hardest timbered Oak".

I agree with the principle, however I'm also concerned that we are starting at a place which has drifted so far from optimal that @iantelescope is at risk of chasing 'local best' and ending up in another attempt to tweak from the wrong starting point. 

But yes, doing it in a sequenced way pausing at each point and looking at results is of course sensible, so long as there is no expectation that any one change will 'fix it'. 

 

This post was modified 1 year ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa 

Hi James,

The "Designed" Flow temperatures provided by three different "installers " were:

1) MP Group , Warm flow Heat pump , first estimate  50 C

2) MP Group , Samsung 5Kw Heat Pump , second estimate , 50 C

3) MP Group , Samsung 5Kw Heat Pump , third estimate, 50 C

4) CMS Group, Midea 7.3 kW , first estimate , 55 C

5) Quarterion, Mitsubishi 8kW , estimate , 50 C

 

The NIC engineer with two other "engineers" from my "installer" attempted, unsuccessfully , in setting the flow temperature to 35 C on my Heat Pump when the flow temperature was controlled by the Water Law Thermostat resulting in Heat Pump failure.

The NIC "Engineer " then discovered that "he needed some fresh  air" disappearing into my garden leaving the pair of "engineers" from my "installer" trying , again unsuccessfully, to repair the Heat Pump. 

My "Installer" was STRUCK_OFF again after this demonstration.

 

The Primary Heat Exchanger Temperatures.

Please find the Primary Heat Exchanger Temperatures in the following graphs of the Input , output and difference Temperatures across the Heat Exchanger on 6th Feb 2024

Heat Exchanger Input Temperature 02060756
Heat Exchanger Output Temperature 02060756
Heat Exchanger Difference Temperature 02060756

The DS18B20 sensors, being high speed serial devices are plainly sensitive to noise!

 I do not have DS18B20 fitted to the PHE output ports but the Sharky Water meter is nearby giving a more accurate, if confusing picture:

Water Flow Temp

 

Water Return Temp
Water Flow  Difference Temp

The Sharky In-Water Sensors are here relatively noise insensitive.

The Temperatures are here altered by Modulating the Pulse Width Modulation motor ports on BOTH Motors.

The PWM Modulation is here controlled by the Delta_T across the Primary ports of the Heat Exchanger.

 

 

ian

 

 


   
ReplyQuote
Page 24 / 79



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security