Mitsubishi Ecodan stuck on immersion symbol
They could be defrosts but unlikely at that Frequency.
do you have the MELCloud app that can show the flow and retune temps for those times?
There is an hourly chart that is useful
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
I have UFH on ground floor and rads on 1st floor. 2 Zones have been setup, ground floor and 1st floor. There are also individual thermostats for UFH in each room.
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 888 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
Is the distance between those new farms and where the e...
By Batpred , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa hopefully after the rad balancing it will perf...
By AdamK , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
@mosibi yes I am interested in potentally evolving my s...
By benson , 3 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
@davidnolan22 Hi, ok first of all it very hard to truly...
By ASHP-BOBBA , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Installers coming tomorrow. One has messaged messaging ...
By Crimson , 5 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 5 hours ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 8 hours ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 10 hours ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 12 hours ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 14 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 15 hours ago
-
RE: My DIY Heat Pump installation
@pollar-bear Top job, I installed my own too and even t...
By bontwoody , 16 hours ago
-
RE: Who has a V2G EV installation
Not sure how you got that information, @batpred. As of ...
By Majordennisbloodnok , 17 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 1 day ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 2 days ago
-
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 2 days ago