Mitsubishi Ecodan stuck on immersion symbol
They could be defrosts but unlikely at that Frequency.
do you have the MELCloud app that can show the flow and retune temps for those times?
There is an hourly chart that is useful
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
I have UFH on ground floor and rads on 1st floor. 2 Zones have been setup, ground floor and 1st floor. There are also individual thermostats for UFH in each room.
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 264 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Thanks and apologies if I was a bit lazy...I have not p...
By Batpred , 4 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@plasfron Hi there! Yes your Mitsubishi heat pump needs...
By HCas , 6 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
The recent ZeroDisrupt discussions reminded me to take ...
By Mars , 6 hours ago
-
RE: What is the Heat Geek Guarantee?
@colinc, that’s a very fair and well-balanced comment, ...
By Mars , 7 hours ago
-
@toodles Thanks. I will assume they have made som...
By Papahuhu , 7 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Oh come on, that's a ridiculous argument by an installe...
By JamesPa , 8 hours ago
-
RE: Say hello and introduce yourself
I've seen photos of other people placing the tank in a ...
By Transparent , 9 hours ago
-
RE: PV Panels on roof in Conservation Area
@colinc Do your own due diligence re reviews etc but...
By Morgan , 9 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
So true, possibly with the exception of people you woul...
By JamesPa , 10 hours ago
-
RE: Isolating the system for a planned power cut
I hadn't realised your reason for a 100mA trip was due ...
By Transparent , 10 hours ago
-
RE: Midea ASHP – how to set weather compensation
Some things worth mentioning: (1) the Headroom Heat P...
By cathodeRay , 10 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
@9jwr9 I didn't get an answer at the time and there has...
By Pipcart , 11 hours ago
-
RE: Battery storage to run Heat Pump.
@majordennisbloodnok I’m not sure you will be able to r...
By Toodles , 11 hours ago
-
RE: Renewables & Heat Pumps in the News
You've completely missed the point. Old, unpatched so...
By Majordennisbloodnok , 12 hours ago
-
RE: Ecodan Energy Monitoring Pack
@batpred that’s an idea yes. Will look into it
By Carpenterstation , 12 hours ago
-
-
PUHZ SW120Y & EHSC-VM2D - Buffer tank to Volumiser
Eventually I was able to find someone here in the Algar...
By DavidAlgarve , 12 hours ago
-
RE: Anyone still weathering it out with Agile?
We are still on agile and it works ok'ish to charge the...
By Batpred , 12 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah... now I can see a photo,and that changes the advice...
By Transparent , 15 hours ago