Mitsubishi Ecodan stuck on immersion symbol
They could be defrosts but unlikely at that Frequency.
do you have the MELCloud app that can show the flow and retune temps for those times?
There is an hourly chart that is useful
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
I have UFH on ground floor and rads on 1st floor. 2 Zones have been setup, ground floor and 1st floor. There are also individual thermostats for UFH in each room.
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 34 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
Verified, trusted & experienced installers
Nationwide coverage expanding
Special offers available
Latest Posts
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 10 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 16 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I think that QR code is to download the app SmartHome o...
By cathodeRay , 22 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 2 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 2 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 3 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 4 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 4 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 5 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 5 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 5 days ago