@parmstar sorry to hear about your problems. What is your heat pump model number, the calculated heat loss of your home and the design flow temp?
I just want to get an idea if this is something we can solve on the forum or if you need to pursue a fight with your installer which as you've noted might be difficult.
@parmstar so on the temperature front it's clear they just didn't design as you asked. Your actual heat losses could be over 10% higher than that with the temps you want, so that might explain the problems getting to the right temperature recently.
There's definitely more to look into though. The £750 of electricity you used, is that all from the heat pump or overall? If that's just the heat pump then that is shockingly poor efficiency, so bad that I almost can't believe it's that.
Do you have data for how the heat pump itself is doing? There's a service called Melcloud that you might have been given access to that should give you some charts and figures, or if not your controller might give you info about energy usage, heat energy delivered, on time etc.
Any idea what design temperature they went for? That’ll help us determine if the rads are the correct size for the rooms and will help us choose what size heat pump should have been installed.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@oswiu thanks for getting back to me. There is no way of monitoring energy usage for just the heat pump as they installed the wrong model of control unit - this is a separate issue that I have raised with them. The figure quoted is for total electric which is stoll
way way more than my standard bill
@hugh the first column of the table is the design temp
@parmstar that’s the room temperature. I need to know what flow temperature they designed for. This is the temperature of the water that flows round the radiators and makes a massive difference to the cost and performance.
For example, an 11kW ecodan will deliver 11kW at -3, but only when heating water to 35 degrees. That’s fine for running UFH at a proper pipe spacing, but no good for retrofit onto existing radiators.
Ask it to deliver 55 degree water and it will struggle to deliver 7kW (probably)…
Tl;dr - your heat emitters are too small
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@oswiu 6.56kW continuous house usage for 14 days straight, at the backstop rate…
3kW into the heat pump and a 3kW backup immersion running too?
Or the ecodan running at a cop of under 2 because it’s uplifting to 50 degrees when it’s -5 outside?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf the immersion heater is connected to an iboost so isn’t linked with the melcloud
also forgot to mention the ASHP is facing a fence and is probably recirculating cold air which isn’t helping
Posted by: @parmstar@hughf the immersion heater is connected to an iboost so isn’t linked with the melcloud
also forgot to mention the ASHP is facing a fence and is probably recirculating cold air which isn’t helping
-- Attachment is not available --
Therein is the likely issue with the majority of your performance issues. The siting is not ideal as the cold expelled air has insufficient space to escape. The ASHP is therefore having to draw in it's own expelled cold air and working it's nuts off to reheat that air. Not at all well situated and unlikely to work efficiently.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@morgan no other place to site it unfortunately - the installer never made me aware of any of this and claimed it would be fine as it’s within clearances. It’s also within 1m of the property boundary which is a no no!
Wow the positioning of that heat pump is shocking. It's barely got any room behind it, it has almost no room around it, it's well closer than 1m to the property boundary and it's made an ice rink!
OP you might have luck getting the installer to move it by proving they've installed it contrary to the instructions in the manual. If they're registered with Mitsubishi, then I imagine Mitsubishi won't be happy with them... You're better off with a very well lagged longer pipe run in my opinion.
On the flow temp, 50C is quite high and so not the most efficient, but it's not the worst. Make sure you have weather compensation set up for when it gets a bit warmer.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 22 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
Powerwall 3 or Myenergi or something else?
Bit of background, 4 bed house 7.35kw heat loss, gas di...
By AdamK , 9 hours ago
-
RE: Does anyone have experience of a smart water meter?
Thanks, @technogeek. So far as I can make out, whilst...
By Majordennisbloodnok , 12 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 14 hours ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 14 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 2 days ago
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 2 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 2 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 3 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 5 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 5 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 6 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 6 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 7 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago