Looking for reference sites and installer recommendations
Posted by: @iancalderbankthere are no other heat sources
Don't forget people are heat sources. If you had a number of house guests, you had a number of mobile radiators/convectors... Estimates vary as to how hot we are (sic) but a commonly quoted figure is we are rated at 100W so if you had ten people in the house that's the same as a 1kW heater.
I agree, empirical evidence is always better than theoretical predictions. I also agree with @kev-m, even manufacturers' engineering data can be optimistic. The way to spot whether defrost cycles have been factored in is to plot the output against ambient temp, and look for a dip in output around 5 to 0 degrees ambient. If there is one, that is probably the defrost cycle effect showing up, meaning their effects have been included. Here's a quick plot for my 14kW (ha ha very funny) Midea heat pump at 50 degree LWT. It's not perfect, because of course with weather comp you don't have a constant LWT, but you can see a dip around 5 degrees either side of zero ambient, meaning defrost effects probably have been included:
Here's another way of looking at the data, from a chart I did a while back. It's a bit harder to get your head round, as it plots output against LWT for various ambients, but the clue to defrosts is in the gap between the drab olive 5 degree line and the mid blue zero line. That gap is the effect of defrost cycles kicking in:
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @jswhite@derek-m
I've been trying to think of a solution to this. Apparently the inner wall and outer stone is not suitable for cavity insulation. I was wondering if I could line the inner wall (and ceiling) with kingspan or equivalent straight onto the current plaster and then finish off with something a little more attractive. Half the room is already well insulated but the other half might benefit. We would lose width on a 3.3metre wide room but could probably live with that if it made a difference.
I'm not an expert when it comes to insulation, so I would suggest that you talk to a suitable company. Though more expensive, external wall insulation would probably be better, since the walls then form part of the thermal mass.
@jswhite you can buy insulated plaster with vapour barrier built in. However its best to install a vapour barrier if you want to insulate a wall like yours - it'll prevent condensation and will allow you to insulate the room on the inside.
https://www.fastbuildsupplies.co.uk/knowledge-hub/does-project-need-vapour-barrier/
Somehow I managed to screw up the x-axis in the second chart in the post above - here is the chart with the correct x-axis labels (can't edit the previous post):
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @jswhiteI was wondering if I could line the inner wall (and ceiling) with kingspan or equivalent straight onto the current plaster and then finish off with something a little more attractive
I hate to be that person, but please do consider the vapour-openness of your walls. Sealing in the moisture with kingspan or a vapour barrier or even gypsum plaster could lead to issues down the line. There are insulating lime plasters (made more insulating with cork, glass bead or hemp), but are intrusive, time-consuming and expensive to install.
Posted by: @chickenbigPosted by: @jswhiteI was wondering if I could line the inner wall (and ceiling) with kingspan or equivalent straight onto the current plaster and then finish off with something a little more attractive
I hate to be that person, but please do consider the vapour-openness of your walls. Sealing in the moisture with kingspan or a vapour barrier or even gypsum plaster could lead to issues down the line. There are insulating lime plasters (made more insulating with cork, glass bead or hemp), but are intrusive, time-consuming and expensive to install.
If problems were to occur in the future, could MVHR help to resolve them?
Posted by: @derek-mIf problems were to occur in the future, could MVHR help to resolve them?
For the moisture inside the house? I suppose so. https://www.greenbuildingstore.co.uk/information-hub/internal-wall-insulation/ seems relevant!
I'm annoyed I didn't install MVHR when I had the chance. Retrofitting would be expensive and annoying.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 14 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@damon thank you for posting. Would you care to tell ...
By JamesPa , 3 hours ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 5 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 9 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 13 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 16 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 17 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 1 day ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 4 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 4 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 5 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago