LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
Hi Tim
On my system Auto mode is near the bottom of the list of about 12 options in Installer mode: ThinQ isn't needed. My system is about 9 months old and the number on the controller is 3.06.3a
@orest thanks.
Seems to me that my older controller & software is the difference and the way I can adjust settings is more clunky and less visual. So be it! Would be nice if instructions referred to software levels etc.
If I can get weather compensation working as hoped I'll be happy. Early signs are encouraging but I suspect I need to monitor... and tweak.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
(First post)
<Main+Boost heater ON> or <Boost heater only ON>
I have a 12kW LG monobloc installed late last year in a large 1990s bungalow with no UFH and the radiators inherited from a gas boiler. After an expensive first couple of months, I managed to find and decipher the installer manual sufficiently to adjust my weather compensation, reduce the flow temperature, and increase the run time, very much in line with the ideas above. Since then, space heating has been reasonably efficient and we don't freeze. My ASHP energy use over the winter (including the immersion) is as follows (kWh)
Nov 469
Dec 857 !
Jan 700
Feb 534
Mar 491
Apr 234
As we go into May, with the CH more or less switched off, and running at about 4-5 kWh / day I'm focussing more on DHW. In particular I'd like to be able to use the heat pump to heat the tank at specific times of day, driven by my tariff and the likely availability of solar power. I haven't found any way so far to set a schedule (apart for the weekly legionella flashing) , and would welcome advice on this.
In addition, I agree with most of the settings above, but I don't understand why you have set the "Heater priority" to <Boost heater only ON>. I haven't tested yet, but feels like that would use the immersion heater rather than the ASHP for all DHW heating? If not that, then what does this setting do exactly - I'm certainly not clear from the manual or the YouTube video.
@glynh isn't this what you are asking?
DHW Boost Mode: The hot water should be set 50°C This is sufficient for normal hot water usage. Should you require
more hot water at a particular time (lots of showers etc.) you can ‘BOOST’ the temperature of the hot water temporarily.
This is done by holding the ‘Back’ button for 3 seconds while the hot water bubble is centralised on the screen.
When Boost mode is activated a lightning symbol will appear beside the shower head.
The immersion heater will then be used to get the tank to 60°C, once this is achieved
the unit will automatically return to normal operation
Thank you, useful to know but not what I was after!
The functionality you mention is accessed through the user menu on the thermostat. I'm asking about a specific setting (called "Heater priority") in the LG installer menu which (I think) governs the way in which the unit uses the heat pump and the immersion heater together in everyday operation. Some people on the thread have recommended setting this a certain way, and I'd like to understand their reasoning.
@fazel ahhhh! have to say I did not know that! thanks for explaining - i don't think I've seen it in any manual
@glynh I had set boost function to "ON" as it seemed recommended - but did not know what it did or how to use it!!
I run my hot water at just 43 deg - which seems fine as we have a large tank and just 2 of us in the house... its fine for bath even as we still have to add a bit of cold. And raise it up to 50 deg if we have guests.
That boost function should be a useful option as well
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Thanks both.
We run ours at 49 normally, as all our HW pipe runs are long. What I would like to do though, is to set different demand temperatures at different times of day in order to utilise my tariff and solar generation more efficiently. I cant see any obvious way to automate that atm.
Posted by: @glynhMy ASHP energy use over the winter (including the immersion) is as follows (kWh)
Nov 469
Dec 857 !
Jan 700
Feb 534
Mar 491
Apr 234
@glynh In case it makes you feel any better I think my usage is more than double yours!
I've only recently started keeping detailed records. Previously not on weather compensation and during much of last year we used a hot tub 😱 🤬
But this year hot tub will only be on in summer months when warmer and good solar production.
Total usage of elec last year was around 13000kwh. Hoping to get under 10000 this year
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Sadly my figures were just the power for the ASHP. We also have a hot tub, an AAHP in a different part of the house, PIH car and an Everhot range cooker so all in all we are very heavy users. To compensate, I now have a reasonable solar PV array, a battery, and I've just bought a share of Ripple Energy's latest cooperative to cover some more of our consumption. Much of this is new, as we moved into a new home last year which featured a 30 YO oil boiler at one end of the house, and electric rads at the other.
Like you, I'm now gathering as much detailed data as I can so that I can eliminate waste wherever possible. The hot tub is an interesting one though, as we actually use it most on cold, dark clear nights in winter. You can get a bespoke ASHP for hot tubs, but I think first of all I need to improve insulation as far as I can, maybe by building another box around the cabinet.
@fazel I've tried to use boost as you describe. I can get it to come on by pressing back button & get lightning symbol.
However it has stayed on for relatively short period. I think in my case the "Boost" only gets DHW back up to the set temp (in my case just 43deg) and not 60deg.
Not sure if there are other settings I need to review.
I will try a further test by setting the required temp higher and see if Boost then forces an immersion heat to get there faster than if left to ashp
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@glynh I'm also taking ashp usage readings now but guess we will not get any meaningful comparisons for some time - probably into next year.
Our hot tub is just a lay z spa so extra inefficient! Partly wanted to try that to help decide whether to invest in permanent "proper" one. Leaning against that based on our usage and more importantly the running cost.
This summer I will add extra ''ThermaWrap" insulation in the cover and use once night temps don't fall so much and we have more solar power. Perhaps mid June to end Aug. I don't think I can add meaningful insulation around outside as it's only temporary.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 My experience with Lay Z Spa is quite positive, in that it’s practical to set it up and use it frequently for a short period, then empty it and put it away for a few months. Not so true with the permanent one. That said, we’ve had a permanent spa for a long time. It has become a normal part of life, and it would be hard to let in go.
The good news is, I have solved my DHW scheduling problem. There was no problem: the exact functionality I wanted (different DHW temps or DHW off at different times of day) is easily available. I was looking for ways of doing this in the Installer menu but (as you probably knew? ) it was hiding in plain sight in the user settings menu. I needed this to allow me to use more cheap rate power using the new Octopus Flux tariff which I am trying for the summer. Now all in place.
-
What happens when the outside temperature exceeds the upper WC point?
23 hours ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
Servicing LG Therma V
8 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
1 year ago
- 22 Forums
- 2,043 Topics
- 44.5 K Posts
- 15 Online
- 3,264 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help me understand my Mitsubishi Ecodan system
Mitsubishi have a setting called summer mode for this. ...
By RobS , 7 hours ago
-
RE: Ecodan Legionella cycle - immersion heater problem
Thanks for letting us know @clockworks I admire your ...
By Transparent , 9 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@potatoman I believe I do, yes. I must admit, I'm not 1...
By weoleyric , 16 hours ago
-
@fillib what a wonderful result, both for you personall...
By Judith , 19 hours ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 21 hours ago
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor not via the WC curve but as @old_scientist ment...
By bontwoody , 23 hours ago
-
RE: MHHS and Heat Pump compatibility
@toodles to be clear I don't know if there will be a re...
By Scalextrix , 1 day ago
-
I did not know this concept, although others might. I...
By Morgan , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk it's probably filtering different providers in t...
By Mars , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
I should probably add to my comments above that, whilst...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Lots of reading and questioning which the background ma...
By JamesPa , 2 days ago
-
RE: The Great British Heat Pump Quiz
Not sure how that happened 🤣 I suspect that it ...
By Mars , 3 days ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch I think @ashp-bobba gave you some great pointers...
By SUNandAIR , 3 days ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 4 days ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 5 days ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 5 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 5 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 6 days ago