LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
I found a useful video on setting up controller for AI. Need to watch several times & use stop start!
https://m.facebook.com/RenewableBuildingSolutions/videos/400881121092193/?_rdr
Key changes on my case:
1. As explained above I'm using water only sensor for now and will use room thermostats for internal air control
2. Heater priority
Was Main & Boost on
Changed to Boost only on (as also suggested by @derek-m)
3. DHW time setting
Was 90 - 0 - 90
Changed to 30 - 30 - 30
4. Pump setting in heating
Was on 2 off 1
Changed to Continue
5. Pump capacity
Was 75
Now 85 (video suggests 100 but that seemed to make the system noisy in the house)
Am using AI mode
One important(?) difference from video was at the end of video it says go to functions and change "Water function setting" to Auto. On my screen there is no such option! any ideas?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
A very useful official video on controller settings
Somewhat frustrating as it jumps around in different order to settings so needs stop start! But helpful...
Most noticeable change in change to Auto/AI on this first day is that the flow temp from the unit is sub 30deg and was 27deg when last checked! However its important to note the outside temp is around 13 deg so the ASHP is not having to work hard to maintain 21 deg in main living areas.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
Ahhhhh
"Water function setting" Only appeared if I change Select Temperature Sensor to Air + Water
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
Posted by: @tim441Ahhhhh
"Water function setting" Only appeared if I change Select Temperature Sensor to Air + Water
This is one of the annoying aspects of the LG system, since it is not clearly explained in the manual. Particularly since if my understanding is correct, the Air + Water mode can only work successfully if the air temperature measuring sensor is located in the heated room area and not in the airing cupboard.
Did you find out how to display the 'Seasonal Auto Temperature' settings?
In hindsight we could've easily put our controller somewhere where the air temperature would have been meaningful. If only installer advice was better! I'm going to try it even if in bathroom - will turn towel rail down so that the temp is nearer to house temp. But if it seems to create false readings and lower temps in rest of house I will revert to water sensor only.
Not yet! Still looking for Seasonal Auto Temperature' settings.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
This is mine. To get into installer mode you probably know that you press the up arrow for a couple of secs in menu mode and then enter the code that's at the bottom of the screen. LG is tricky but it's been working fine for 9 months and I'm being paid to heat the house 😊
Posted by: @orestThis is mine. To get into installer mode you probably know that you press the up arrow for a couple of secs in menu mode and then enter the code that's at the bottom of the screen. LG is tricky but it's been working fine for 9 months and I'm being paid to heat the house 😊
Thank you for the information, much appreciated.
Posted by: @tim441In hindsight we could've easily put our controller somewhere where the air temperature would have been meaningful. If only installer advice was better! I'm going to try it even if in bathroom - will turn towel rail down so that the temp is nearer to house temp. But if it seems to create false readings and lower temps in rest of house I will revert to water sensor only.
Not yet! Still looking for Seasonal Auto Temperature' settings.
It would appear that you need to be in installer mode, as I suspected.
@orest @derek-m I still can't see it in installer mode. I can see everything else.
Just wondering if it's a more recent controller hardware and/or software? Or needs smart control system called called ThinQ?
Fwiw... my system was installed Aug 2020 and is controller software 3.05.5a
I'm thinking this is the old version equivalent...After "Screed Drying setting" there are 3 settings (not in pdf) that I guess may be relevant.. currently set as following:
Outdoor Temp for Auto Mode
-6 Min 17 Max
Indoor Air Temp for Auto Mode
16 Min 21 Max
LWT for Auto Mode
20 Min 45 Max
Changed the above settings following other suggestions. Not yet sure I've got optimum?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
Posted by: @tim441@orest @derek-m I still can't see it in installer mode. I can see everything else.
Just wondering if it's a more recent controller hardware and/or software? Or needs smart control system called called ThinQ?
Fwiw... my system was installed Aug 2020 and is controller software 3.05.5a
If the particular capability is shown in the manual supplied with your system, then it should be available. Maybe an e-mail to LG Technical Help would answer the question.
I find the LG manuals quite incomprehensible and I have dealt with more complex industrial systems for many years. It is quite atrocious to have instructions within the manual that are either not normally accessible, or do not exist in the installed software.
The more I see of LG's equipment and capabilities, the more it convinces me never to buy one.
@derek-m Hi Tim
On my system Auto mode is near the bottom of the list of about 12 options in Installer mode: ThinQ isn't needed. My system is about 9 months old and the number on the controller is 3.06.3a
@derek-m I think you're right.. I will email my installer & LG.
in fairness I'm generally happy with the ASHP ... its just the dreadful instructions & lack of early advice from the installers. They installed (I think) a good system, at fair cost.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
-
Servicing LG Therma V
4 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
10 months ago
-
Flow temperature up and down like a yo-yo
1 year ago
-
Daikin EDLA14D3V3 COP is now below 1
2 years ago
-
Flow temperature & weather compensation. Impact on efficiency
2 years ago
- 21 Forums
- 1,747 Topics
- 37.4 K Posts
- 59 Online
- 2,036 Members
Join Us!
Latest Posts
-
RE: Samsung E911 intermittent issue
@netdonkey The model number for your Samsung indicates ...
By ASHP-BOBBA , 30 minutes ago
-
RE: The UK’s Heating Nightmare: Why Many Systems Fail Homeowners
I don't know enough about how commercial BESS sites mak...
By Transparent , 2 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@dunlorn Good shout that buddy will give it a go at ...
By Burtis , 13 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@odd_lion I still have two copies of Bodge Buster left ...
By Mars , 22 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@bromide Thanks for the advice, doing it once but prope...
By ChandyKris , 23 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles 13.5kWh here, but no ASHP. 27kWh would be ampl...
By IanMK13 , 1 day ago
-
RE: What is a considered a decent weather curve?
Thanks Gary, I'll do that with the Drayton balancing ke...
By Crimson , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've created a separate thread to discuss WC settings a...
By Crimson , 1 day ago
-
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Thanks I will try that and look at results
By A E Deans , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
No such luck yet - installers are saying their quoted 3...
By dinhp , 2 days ago
-
RE: Excessive performance/system issues with GSHP
@johnr Thanks - the Buffer tank is in the integral gara...
By didjerama_uk , 2 days ago
-
RE: Do thick walls make for warm houses?
@robl Thanks, thats interesting 🙂
By bontwoody , 2 days ago
-
RE: Mitsubishi EcoDan ASHP Settings not saving.
@fez96 Who’d of thought.? 👍
By Westkent , 2 days ago
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 3 days ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 4 days ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 4 days ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 4 days ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 4 days ago
Latest Topics
-
Samsung E911 intermittent issue
By NetDonkey 14 hours ago
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 4 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 5 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 7 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 1 week ago
-
By R0y124 1 week ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 1 week ago